Causes of Transformer Explosion in 152 Hectares University Campus

In summary, the young engineer suspects that the transformer explosions were caused by the primary side, as they had already done an investigation and found no faults. The high harmonic content of the voltage source may have caused the explosions.
  • #1
young e.
64
0
hi pf folks..

currently i am the electrical engineer incharge in a 152 hectares university campus in our place. commonly our transformer are rated 7620/240 volts, 1p with capacity of 25 KVA, 50 KVA and 100 KVA.. for our three phase loads we used to bank 3- 1p transformer
wye delta...all in all we have a total of 8 transformer substation in our campus.. now few months past we experienced succesive transformer explosion in our campus in different substations, we check the secondary line there's no fault in it,,, being a neophyte in this field of practice (electrical engg.) now my question is:

1. aside from overloading, what are the other causes of transformer explosions?

2. i suspect that the succesive explosion came from the primary side since we had already made an investigation in all of our loads and secondary lines, and we found that everything is all right, now what are the factors affecting transformer explosion with regards to the primary side..

tnx in advance!

:smile: young engineer
 
Engineering news on Phys.org
  • #2
Just some background information since it's not my speciality.
There is always some leakage current between the winding layers. Over time, and especially with high internal temperature, both the insulation and oil fill degrade and become slightly conductive. This of course increases the leakage currents a little. Eventually the insulation becomes carbonized and rather conductive, then you are on the way to a run-away short circuit and explosion if there ar not any fuses in the primary circuit.

To monitor the internal conditions, a chemical analysis of the oil is periodically done to check for breakdown by-products.

Others here, perhaps @jim hardy or @anorlunda, may have more details.

Cheers,
Tom
 
  • Like
Likes Asymptotic
  • #3
Monitoring oil is a must.

Are primaries 4 wire connected? In other words, is there a neutral wire?
If so,
Measure the neutral current on WYE side.

Why do i say that ?
It is possible to overload a (4 wire WYE)-DELTA connected transformer with third harmonic current by powering it from a much larger source that has just a few % third harmonic content in its voltage .

Look up "Zero Sequence Current".

old jim
 
  • Like
Likes Asymptotic
  • #4
Given that they have been providing trouble-free service until just recently.

1. Has the nature of their loads changed?
Has anything unusual (an earthquake, etc.) happened?

2. How old are the transformers?
Date of manufacture will be on their nameplates. If they were all installed at about the same time, and are closing in on expected service life that could explain the rash of failures.

3. Is your area particularly prone to lightning strikes?
Metal oxide, and/or spark gap arresters are popular for transformer/switchgear protection. MO arresters can fail shorted (which is hard to ignore - loud explosion, and likely to take out the primary fuse), but they may also fail open, which isn't easily detectable (special tests are required), and afterward, provides no lightning and surge protection.

A good course of action is look into transformer and switchgear testing services in your area, and have a reputable firm assess your equipment.
 
  • #5
Others mentioned oil. That is the first place to look.

High harmonic content can also cause transformer explosions. Especially if you had several in the same area during the same period, I would check harmonics.

An arc furnace in a steel recycling plant can be a big source of harmonics.
 
  • Like
Likes jim hardy

1. What are the main causes of transformer explosions?

The main causes of transformer explosions in a university campus could include overloading, aging equipment, electrical faults, and inadequate maintenance. Overloading occurs when the transformer is unable to handle the amount of electricity passing through it, causing it to overheat and potentially explode. Aging equipment can also lead to weaknesses in the transformer's insulation, increasing the risk of explosion. Electrical faults, such as short circuits, can also cause explosions due to the sudden surge of electricity. Lastly, inadequate maintenance can lead to the buildup of debris or moisture in the transformer, which can also contribute to an explosion.

2. How can overloading cause a transformer explosion?

Overloading occurs when the transformer is forced to handle more electricity than it is designed to handle. This can happen due to increased demand for electricity or faulty equipment. When a transformer is overloaded, the internal temperature rises, causing the insulation to break down and the transformer to fail. This can lead to an explosion if the pressure inside the transformer becomes too great.

3. What are the signs of an aging transformer that could lead to an explosion?

Signs of an aging transformer include rust or corrosion on the outer casing, leaks or cracks in the insulation, and discoloration or charring on the transformer's components. These signs indicate that the transformer may be weakened and at a higher risk of failure. It is important to regularly inspect and maintain transformers to prevent explosions and ensure the safety of the campus.

4. How can electrical faults cause a transformer explosion?

Electrical faults, such as short circuits, can cause a sudden surge of electricity through the transformer. This surge can lead to overheating and potentially cause an explosion. It is important to have proper safety measures in place, such as fuses and circuit breakers, to prevent electrical faults from causing explosions.

5. What steps can be taken to prevent transformer explosions in a university campus?

To prevent transformer explosions, regular maintenance and inspections should be conducted to identify any potential issues. Upgrading to newer and more efficient equipment can also help prevent overloading and aging of transformers. Implementing safety measures such as fuses and circuit breakers can also help prevent electrical faults from causing explosions. It is also important to have emergency response plans in place in case of an explosion. Proper training and education for staff and students on electrical safety can also help prevent accidents and explosions.

Similar threads

  • Electrical Engineering
Replies
2
Views
1K
  • Electrical Engineering
Replies
1
Views
1K
  • Electrical Engineering
Replies
3
Views
1K
  • Electrical Engineering
Replies
16
Views
3K
  • Electrical Engineering
Replies
10
Views
4K
Replies
12
Views
1K
  • Electrical Engineering
Replies
17
Views
11K
  • Electrical Engineering
Replies
12
Views
11K
  • Nuclear Engineering
Replies
9
Views
2K
Replies
10
Views
2K
Back
Top