Voltage drop along cable
  • Thread starter lavalin
I have a 45kW VSD drive with pf of .9 and FL amp of 75A, I have a 350m run from the MCC to the VSD itself and I'm trying to calculate what size cable I need so that I don't exceed the specified voltage drop of 3%. The line-line voltage where the motor is to be placed is 400V and the cable impedance is say .2ohms per km.
I was looking in the australian standards and their voltage formula is as follows:
Vdrop = (sqrt(3) * I(line) * Distance * Z(cable))/1000
V(% drop) = Vdrop/400
What I want to know is, why are they multiplying by sqrt(3), when you already have the line value Current. I thought sqrt(3) was only used to convert between phase/line values of current or voltage in delta/star configurations. The motor has a delta winding and I'm running 4C (3C+E) out to it.
From what I understand it should be:
Vdrop = I(line) * Distance * Z(cable)
So;
Vdrop = (75 * 350 * .2) / 1000
Vdrop = 5.25V
V(%) = (Vdrop/V) * 100
V(%) = (5.25 / 400) *100
V(%) = 1.31%
Thanks
Answers and Replies
stewartcs
It appears they are approximating the voltage drop from line-to-line of a three phase system, not line-to-neutral.
The general approximation for a line-to-neutral voltage drop is:
VD = IRcos(phi) + IXsin(phi)
where,
VD = voltage drop in one conductor, one way
I = current flowing in one conductor
R = line resistance for one conductor in ohms
X = line reactance for one conductor in ohms
phi = angle whose cosine is the load power factor
Note that I is usually assumed to be the load carrying capacity of the conductor.
The line-to-line voltage drop for a three-phase system is then found by multiplying by sqrt(3).
CS
You have given cable Z of 0.2 ohm/km which is value for 95mm2
This cable has 3ph volt drop of 0.4mV/Am
Hence VD = 0.4 *75*350/1000 = 10.5v
Volt drop usually is % of voltage at MCC which usually 415v
3% of 415V is 12.45v hence you are below this
%V = ( phase voltage drop / rated phase voltage)* 100
%V (in symetrical system) = ( sqrt (3) * phase voltage drop / sqrt (3) * rated phase voltage) * 100