Exploring Transformer Connections for Step Up/Down Transformers

In summary: but these days, with the benefit of newer technology and more sophisticated monitoring, a wye stepup usually falls into the category of reliable, safe, and easy to detect faults.
  • #1
KraakeCrest
18
2
Hi
Take a look at the picture below, I am curious of what transformer connections are used at each step up/step down transformer. I am sure that there are several way of connecting them and each have their pros and cons, but what are the most usual connections?

Lets start at the consumer and work backwards:
I would assume that there is a star connection with neutral on the secondary side at the 120/240 voltage level to support single phase circuits etc. On the primary side, maybe a delta connection or star with neutral to be able to support the flow of zero sequence currents?

Green substation step-down transformer:
Not sure, but I would assume a three conductor configuration to avoid the extra cost of a 4th wire on the primary side.

Generator step up transformer:
Same here, three conductor configuration on the secondary to avoid a 4th wire. Unsure about primary side.

And are the star "neutral point" always grounded or are there exceptions?
ElectricPowerSystem.jpg
 
Engineering news on Phys.org
  • #2
KraakeCrest said:
I would assume that there is a star connection with neutral on the secondary side at the 120/240 voltage level to support single phase circuits etc.
KraakeCrest said:
And are the star "neutral point" always grounded or are there exceptions?
The Neutral is usually Earthed (in the UK) but that Earth isn't always made available to the house, in such cases a local Earth rod may have to be used. There are various earthing strategies used in the UK..

http://wiki.diyfaq.org.uk/index.php/Earthing_Types


Sorry no idea why the font size is off in this post.
 
  • Like
Likes KraakeCrest
  • #3
KraakeCrest said:
Green substation step-down transformer:
Not sure, but I would assume a three conductor configuration to avoid the extra cost of a 4th wire on the primary side.

Be aware my experience is all In US

Here it's a four wire connection with neutral earthed so that a phase to ground fault will trip its feed.
Look at the poles in your neighborhood,
around here the neutral wire is the smaller one on shorter insulators usually installed lower than the phase conductors.
In high lightning areas it's often run on top to serve as a lightning rod,
in other areas it's run below the others so that should a phase wire fall it will likely hit the neutral and trip the feeder rather than falling across a roadway energized..
Also - should an overheight truck hit a wire you'd want it to be the neutral.

KraakeCrest said:
Generator step up transformer:
Same here, three conductor configuration on the secondary to avoid a 4th wire. Unsure about primary side.
Only configuration I've seen for power plants -

Stepup secondary is wye, grounded neutral for same reason as above.

On primary side the stepup transformer is delta connected and hardwired to generator by what @anorlunda referred to as "isophase" bus.
Generator is wye wound.
Generator's neutral is earthed through a huge high power resistor whose job it is to limit fault current to a value low enough it won't cause an electrical explosion inside the generator, twenty amps or less.. In my plant that resistor was the size of a pickup truck.

old jim
 
  • Like
Likes KraakeCrest and Asymptotic
  • #4
jim hardy said:
In my plant that resistor was the size of a pickup truck.
Indeed. I just Googled for an image and found this one. (compliments of http://www.kiantajhiz.com/en/Products/211)

dimensions.jpg
 
  • Like
Likes KraakeCrest, Asymptotic and jim hardy
  • #5
To further Jim's comment... many older systems were Delta secondary, this had been preferred for reliability, as a single ground fault would not cause an outage since it would actually take 2 ground faults, typically on different phases to get the system to trip - but this was very dangerous and unreliable. Then rudimentary Ground Fault detection schemes were set up - the 3 light bulbs... often not causing a trip, but an indicator that there was a fault relying on those inconstant humans to monitor and take action..

Today - the wye secondary, has both safety and filtering benefits. Using a resistor on the neutral-grounding point connection when there is no neutral load, provides a known ground reference to the whole system. Or a known state. It is relatively easy to detect an abnormal conditions now by monitoring the current flow through the resistor. This can trigger an investigation or a system trip, all depending on the application, safety aspects, and reliability requirements. For example feeding a neighborhood the emphasis is on safety, feeding the back-up cooling of a nuke... well reliability.

So - for safety - you may be just wanting to limit the fault current, and trip almost instantly, for reliability, the system can be configured to allow a full time, continuous ground fault, setting off alarms, but not tripping off the system. Also - the Ground Fault current can be traced, sometimes allowing the location of the fault to be identified, and isolated without tripping the entire system.

Basically - there is never a one ideal solution for every situation.
 

1. What is a step up/down transformer?

A step up/down transformer is a type of electrical device used to change the voltage of an alternating current (AC) power supply. It has two or more coils of wire, called windings, that are connected by a magnetic core. This allows the transformer to either increase (step up) or decrease (step down) the voltage of the input power supply.

2. Why would I need to use a step up/down transformer?

Step up/down transformers are commonly used in many different industries and applications. They are most commonly used to convert high voltage power from power plants to lower voltages that are suitable for use in homes and businesses. They are also used to convert power from one country's electrical system to another when traveling internationally.

3. How do I choose the right transformer connections for my specific needs?

The right transformer connections will depend on the specific voltage requirements of your equipment or application. It is important to consult with a qualified electrician or engineer to determine the appropriate connections for your specific needs. Factors such as the input and output voltage, load capacity, and frequency should all be considered when selecting the transformer connections.

4. What are the different types of transformer connections?

There are several different types of transformer connections, including delta, wye, and autotransformer connections. These connections can be configured in various ways, such as step up, step down, and isolation. Each type of connection has its own benefits and is suitable for different applications.

5. Are there any safety precautions I should take when working with step up/down transformers?

Yes, it is important to follow proper safety precautions when working with electrical equipment, including step up/down transformers. This may include wearing protective gear, ensuring proper grounding, and following proper handling and maintenance procedures. It is also important to consult with a qualified electrician or engineer for any specific safety guidelines related to your specific transformer and its connections.

Similar threads

Replies
2
Views
750
Replies
3
Views
677
  • Electrical Engineering
Replies
8
Views
1K
Replies
6
Views
2K
Replies
13
Views
3K
  • Electrical Engineering
Replies
14
Views
2K
  • Electrical Engineering
Replies
6
Views
3K
  • Electrical Engineering
Replies
32
Views
2K
Replies
18
Views
4K
  • Electrical Engineering
Replies
7
Views
5K
Back
Top