3 phase 4 wire conductors radiated electromagnetic interference?
The power cables will be concrete encased and approx 10'-15' below some rooms that could have some sensitive digital equipment. Someone on another forum recommended running them in steel conduit and grounding the conduit that would provide some shielding.- djr3203
- Post #5
- Forum: Electrical Engineering
-
D
3 phase 4 wire conductors radiated electromagnetic interference?
Well someone has brought up the concern of EMI issues with the installation. The setup involves 8 parallel conductors for each phase both carrying approx. 345A all at a frequency of 60Hz. Someone has suggested twisting the wires to reduce EMI radiation, but I tend to think this won't have a...- djr3203
- Post #3
- Forum: Electrical Engineering
-
D
3 phase 4 wire conductors radiated electromagnetic interference?
If you have a 3 phase 4 wire distribution where the 3 phase conductors and 1 neutral is inside a pvc conduit, how would you model the force of the electromagnetic field at a certain distance away from the conduit? Assuming the loads are balanced, the currents would sum to zero on the...- djr3203
- Thread
- 3 phase Conductors Electromagnetic Interference Phase Wire
- Replies: 8
- Forum: Electrical Engineering