Recent content by jburgess56

  1. J

    Why Do Railroad Tracks Experience Voltage and Current from Nearby Power Lines?

    We use capacitor banks for our impedance matching and we have a power factor of .98 lagging to 1.00 unity between the 3 phases of 12 KV. Hard to get much closer...
  2. J

    Why Do Railroad Tracks Experience Voltage and Current from Nearby Power Lines?

    I am measuring across the isolated section of track with a fluke 187 volt meter. I am using a jumper across the isolated section and using a clamp on amp probe to check current flow. The voltage and amps are on both tracks and only in the isolated section of the signal area. Checking to ground...
  3. J

    Why Do Railroad Tracks Experience Voltage and Current from Nearby Power Lines?

    I have a parallel 69KV and 12KV line that runs parallel to a railroad track. Also, this system has a static on top for the system neutral. We are getting 20 plus volts and 4 amps on each track in an isolated section of track. We have deenergized the 12 kv and the volts and amps went away. The...