Is There a Ratio Between Short Term and Continuous Current for Power Cables?
~40 mm^2 cross section mostly because the current decays so fast after 1 time constant, so this makes sense.- rontruong
- Post #10
- Forum: Electrical Engineering
-
R
Is There a Ratio Between Short Term and Continuous Current for Power Cables?
I redid calculations with real RMS values and the cable size is much much smaller! thanks for the help!- rontruong
- Post #8
- Forum: Electrical Engineering
-
R
Is There a Ratio Between Short Term and Continuous Current for Power Cables?
Okay, I think I'm going to listen to you for simplicity reasons. With the 95 mm^2 results, then a size of 4/0 AWG copper cable should be sufficient. Can you show me where you got the equation and k values from, I need it for a presentation. Thank you for your help. Actually, the purpose of...- rontruong
- Post #7
- Forum: Electrical Engineering
-
R
Is There a Ratio Between Short Term and Continuous Current for Power Cables?
Hi guys, I'm looking to find out if there is a ratio between short term and continuous current for power cables. I know that people usually generalize around 5-10 x rated ampacity, but I'm just asking around to see if there is a certain #. On McMaster Carr, the highest rated cable is for...- rontruong
- Thread
- Cables Short Term
- Replies: 14
- Forum: Electrical Engineering