Thanks zoki85 for your reply.
Time fault is reduced to 80ms. What I don't understant that when fault applied on Bus loacted at the extremity of the cable or on the beginning we have no problem even if time fault increase to 250ms.So I can Conclud that I have no parameter problem on generators...
Hi All
I have done transient stability simulations on isolated electrical network using ETAP 7.5 software.
Problem: On buses Faults generators return to stable stade
But on cable faults, rotor angle is diverged so the system is not stable.
To be noted that we have 2 SOLAR generators of 5MW...