Heat pump COP theoretical maximum
 
Hello everybody.

I have trouble of proving the theoretical maximum of heat pump Coefficent of Performance.
The thing I'm trying to calculate is for heat pump pumping heat from colder reservoir to the hotter reservoir:
COP=Qh/W
Qh - heat supplied to the hot reservoir(output)
W - mechanical work consumed by the pump(input)

The formulas in the wikipedia seems to be wrong and I want to derive the correct formulas from the thermodynamic laws. With current Wikipedia formula it is normal to get COP >2. Search wikipedia:Coefficent of Performance.

As I calculate the heat balance of the basic air to air heat pump, any COP values above 2 will violate the second law of the thermodynamics, and therefore make perpetual motion machine possible.

So is what is the correct formula and what is the way to prove it?

I argued a lot with my friend about that, when he wanted to buy the heat pump to heat his office. Eventually he still bought the pump because I could not provide the calculation and he decided to believe what the sales man told him (COP=3 or something). But now he do not seem very happy with the electricity bill.

Thanks in advance.

mfb Feb13-13 05:30 PM

Re: Heat pump COP theoretical maximum
 
Quote:

The formulas in the wikipedia seems to be wrong
I don't think so.

A COP>2 is possible, if the temperature difference is not too large. Looks like you have some error in your calculations.

Thermolelctric Feb14-13 03:07 AM

Re: Heat pump COP theoretical maximum
 
According to my understanding COP >2 is not possible for air to air heat pump. Based on assumption that heat from the building is lost to the same air (cold reservoir) from where it is pumped to inside the building (hot reservoir).

The COP>2 is possible for land to air pump, when the cold reservoir is hotter than the air aruond the building to where the heat is lost. But not for the air to air.

The formula COP=Thot/(Thot-Tcold) maybe it is for calculating the possible improvment over air to air pump. Thot being the earth and Tcold being the air around the building. The common miscontseption being that using Tcold = outside temp, and Thot = temp inside building. While should be Tcold =outside temp, and Thot = earth (or other heat) source temperature.

Huge amount of people are scammed with this false calculation!

Thermolelctric Feb14-13 03:18 AM

Re: Heat pump COP theoretical maximum
 
OK, let me put it that way:

Can anyone prove that COP>2 is possible, based on thermodynamic laws and other postulates?
Conditions: pumping heat from cold reservoir(Tcold) to the hot reservoir(Thot). Tcold<Thot.

DrClaude Feb14-13 04:27 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by Thermolelctric (Post 4269649)
OK, let me put it that way:

Can anyone prove that COP>2 is possible, based on thermodynamic laws and other postulates?
Conditions: pumping heat from cold reservoir(Tcold) to the hot reservoir(Thot). Tcold<Thot.

[itex]Q_h[/itex]: heat pumped into the building
[itex]Q_c[/itex]: heat taken from outside the building
[itex]W[/itex]: electrical energy used by the heat pump
[itex]T_h[/itex]: temperature inside the building
[itex]T_c[/itex]: temperature outside the building

1st law: [itex]Q_h = W + Q_c[/itex]

Therefore [tex]\mathrm{COP} = \frac{Q_h}{W} = {Q_h}{Q_h - Q_c} = \frac{1}{1 - Q_c/Q_h} > 1[/tex]

2nd law: [tex]\frac{Q_h}{T_h} \ge \frac{Q_c}{T_c}[/tex] therefore [tex]1 - \frac{T_c}{T_h} \le 1 - \frac{Q_c}{Q_h}[/tex] for which we get [tex]\mathrm{COP} \le \frac{1}{1 - T_c/T_h} = \frac{T_h}{T_h - T_c}[/tex]
There is no fundamental reason why the COP cannot be greater than 2.

Quote:

Quote by Thermolelctric (Post 4269643)
According to my understanding COP >2 is not possible for air to air heat pump. Based on assumption that heat from the building is lost to the same air (cold reservoir) from where it is pumped to inside the building (hot reservoir).

I don't see how any losses from the building come into play in the calculation of the COP of heat pump itself.

Thermolelctric Feb14-13 04:57 AM

Re: Heat pump COP theoretical maximum
 
Thanks DrClaude.
Quote:

Quote by DrClaude (Post 4269691)
[itex]Q_h[/itex]: heat pumped into the building

Therefore [tex]\mathrm{COP} = \frac{Q_h}{W} = {Q_h}{Q_h - Q_c} = \frac{1}{1 - Q_c/Q_h} > 1[/tex]

Can you explain more how you get this?

Quote:

Quote by DrClaude (Post 4269691)
[itex]Q_h[/itex]
I don't see how any losses from the building come into play in the calculation of the COP of heat pump itself.

For building heating, this is the main goal to determine most economic way to get the energy needed to maintain the temperature inside the building above the ambient. So naturally one wants to compare how much heating energy he gets using different apparatus. Correct understanding of the COP of the heat pump is needed for those calculations.

There must be error in those calculations, because when simple heat pump has a COP of over 2, it is possible to reheat the input with the energy from the output and with that increase the COP infinetly resulting in infinite COP -- the mashine that pumps heat from cold reservoir to hot reservoir without needing any additional energy to run.

DaleSpam Feb14-13 05:53 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by Thermolelctric (Post 4269711)
There must be error in those calculations, because when simple heat pump has a COP of over 2, it is possible to reheat the input with the energy from the output and with that increase the COP infinetly resulting in infinite COP -- the mashine that pumps heat from cold reservoir to hot reservoir without needing any additional energy to run.

Please show your calculations for this claim.

DrClaude Feb14-13 05:54 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by Thermolelctric (Post 4269711)
Thanks DrClaude.
Can you explain more how you get this?

Sorry, a part of the equation didn't come out right. [tex]\mathrm{COP} = \frac{Q_h}{W} = \frac{Q_h}{Q_h-Q_c} = \frac{1}{1-Q_c/Q_h} >1[/tex] I hope it is now clear.

Quote:

Quote by Thermolelctric (Post 4269711)
For building heating, this is the main goal to determine most economic way to get the energy needed to maintain the temperature inside the building above the ambient. So naturally one wants to compare how much heating energy he gets using different apparatus.

Yes, but this can be made independent of the COP of the pump, by assuming that you have a desired indoor temperature, for a given outdoor temperature. Of course, if your goal is to maintain an indoor temperature relative to the outside, it becomes more complicated. Note also that actual COPs are usually given for a standard pair of indoor and outdoor temperatures, and are mostly useful in comparing one pump with another. If you want to calculate the actual energy needed over a year, including variations of the outside temperature, you would need measured COPs as a function of inside/outside temperatures.

Quote:

Quote by Thermolelctric (Post 4269711)
There must be error in those calculations, because when simple heat pump has a COP of over 2, it is possible to reheat the input with the energy from the output and with that increase the COP infinetly resulting in infinite COP -- the mashine that pumps heat from cold reservoir to hot reservoir without needing any additional energy to run.

No error, it is just how the COP is defined. Infinite COP will only occur for [itex]T_h=T_c[/itex], in which case the pump is not doing anything, so indeed it doesn't need any energy to run! Event for finite but huge COPs, they correspond to extremely small differences in temperatures that are not realistic in real world applications. And it is just an inequality: for real heat pumps [tex]\mathrm{COP} = \eta \frac{T_h}{T_h-T_c}[/tex] with [itex]\eta < 1[/itex] and itself a function of [itex]T_h[/itex] and [itex]T_c[/itex].

Thermolelctric Feb14-13 06:07 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by DrClaude (Post 4269740)
No error, it is just how the COP is defined. Infinite COP will only occur for [itex]T_h=T_c[/itex], in which case the pump is not doing anything, so indeed it doesn't need any energy to run! Event for finite but huge COPs, they correspond to extremely small differences in temperatures that are not realistic in real world applications. And it is just an inequality: for real heat pumps [tex]\mathrm{COP} = \eta \frac{T_h}{T_h-T_c}[/tex] with [itex]\eta < 1[/itex] and itself a function of [itex]T_h[/itex] and [itex]T_c[/itex].

Thanks.
But what happens to COP when Th closes to infinity?

DaleSpam Feb14-13 06:20 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by Thermolelctric (Post 4269741)
But what happens to COP when Th closes to infinity?

The ideal COP approaches 1 as Th approaches infinity.

Thermolelctric Feb14-13 06:21 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by DaleSpam (Post 4269739)
Please show your calculations for this claim.

This is what I am working on.

We have cold reservoir, and hot reservoir. We are pumping from cold to hot.
Lets assume we have a COP=5
Mehanical work into the pump=1kW
Heat output to the hot reservoir=5kW

So now we let 2kw go back to heat the cold reservoir.
This leaves us still 3kW output to hot reservoir, this heats the hot reservoir, but we do not let the hot reservoir temperature increase, the exess heat is conducted away. So Th=const.
But added 2kW to cold reservoir will increase the cold reservoir temperature. And this increases the COP by formula COP=Th/(Th−Tc). So now we get even more output heat because of increased COP. And the cycle repeats. The COP is increased to infinity.
We have perpetum mobile!

DaleSpam Feb14-13 06:27 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by Thermolelctric (Post 4269750)
So now we let 2kw go back to heat the cold reservoir.
This leaves us still 3kW output to hot reservoir, this heats the hot reservoir, but we do not let the hot reservoir temperature increase, the exess heat is conducted away. So Th=const.
But added 2kW to cold reservoir will increase the cold reservoir temperature. And this increases the COP by formula COP=Th/(Th−Tc).

Even with the increased COP it still takes work to move the heat back up. You seem to think that the heat that leaks into the cold reservoir is somehow free to move back to the hot reservoir.

DrClaude Feb14-13 06:27 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by Thermolelctric (Post 4269741)
Thanks.
But what happens to COP when Th closes to infinity?

[itex]\mathrm{COP} \sim 1[/itex]

Consider the following hypothetical situation. An ideal (Carnot engine) heat pump installed between a hot sink at [itex]T_h[/itex] and a cold source at [itex]T_c[/itex], and functions with a constant consumption of electrical energy ([itex]W = \mathrm{const.}[/itex]). Both sources are connected such that heat can flow from hot to cold to maintain the hot source at [itex]T_h[/itex] (imagine that we have a demon that can do that so that we don't need to worry about entropy here). The temperature of the cold source will vary according to
[tex]
T_c = T_{c0} - \frac{Q_c}{C} t + \frac{Q_h}{C} t
[/tex]
where [itex]T_{c0}[/itex] is the initial temperature of the cold source and [itex]C[/itex] its heat capacity. Since [itex]Q_h = W+Q_c[/itex], we have
[tex]
T_c = T_{c0} - \frac{Q_c}{C} t + \frac{W + Q_c}{C} t = T_{c0} + \frac{W}{C} t
[/tex]
so the heat pump is basically heating up the cold source as would a perfect electrical heater. No "over unity" or other violation of the laws of TD.

Note that the initial value of the COP is of no relevance. This will work even if it is initially < 2. The value of the COP grows towards infinity during the process, but so what?

Hope this helps.

Thermolelctric Feb14-13 06:41 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by DaleSpam (Post 4269754)
Even with the increased COP it still takes work to move the heat back up. You seem to think that the heat that leaks into the cold reservoir is somehow free to move back to the hot reservoir.

This is what I'm trying to prove. That this COP formula is incorrect.

DrClaude Feb14-13 06:44 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by Thermolelctric (Post 4269763)
This is what I'm trying to prove. That this COP formula is incorrect.

But the COP formula is just
[tex]
\mathrm{COP} = \frac{\textrm{benefit}}{\textrm{cost}} = \frac{Q_h}{W}
[/tex]

Thermolelctric Feb14-13 06:48 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by DrClaude (Post 4269769)
By the COP formula is just
[tex]
\mathrm{COP} = \frac{\textrm{benefit}}{\textrm{cost}} = \frac{Q_h}{W}
[/tex]

Not that one!

DrClaude Feb14-13 06:55 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by Thermolelctric (Post 4269771)
Not that!

I derived the COP in terms of temperatures above. If you can't find any fault with the derivation, then both are equivalent.

Quote:

Quote by Thermolelctric (Post 4269750)
So now we get even more output heat because of increased COP.

Or you just need less [itex]W[/itex] for the same [itex]Q_h[/itex], which makes sense: the heat pump requires less work if the sink and the source are close to the same temperature.

Quote:

Quote by Thermolelctric (Post 4269750)
The COP is increased to infinity.
We have perpetum mobile!

No, you reach [itex]T_c = T_h[/itex] and you don't have a heat pump anymore! Or, see my previous post, you just continue heating the cold source as would a electrical heater.

Thermolelctric Feb14-13 06:55 AM

Re: Heat pump COP theoretical maximum
 
Quote:

Quote by DrClaude (Post 4269755)
[itex]\mathrm{COP} \sim 1[/itex]

Consider the following hypothetical situation. An ideal (Carnot engine) heat pump installed between a hot sink at [itex]T_h[/itex] and a cold source at [itex]T_c[/itex], and functions with a constant consumption of electrical energy ([itex]W = \mathrm{const.}[/itex]). Both sources are connected such that heat can flow from hot to cold to maintain the hot source at [itex]T_h[/itex] (imagine that we have a demon that can do that so that we don't need to worry about entropy here). The temperature of the cold source will vary according to
[tex]
T_c = T_{c0} - \frac{Q_c}{C} t + \frac{Q_h}{C} t
[/tex]
where [itex]T_{c0}[/itex] is the initial temperature of the cold source and [itex]C[/itex] its heat capacity. Since [itex]Q_h = W+Q_c[/itex], we have
[tex]
T_c = T_{c0} - \frac{Q_c}{C} t + \frac{W + Q_c}{C} t = T_{c0} + \frac{W}{C} t
[/tex]
so the heat pump is basically heating up the cold source as would a perfect electrical heater. No "over unity" or other violation of the laws of TD.

Note that the initial value of the COP is of no relevance. This will work even if it is initially < 2. The value of the COP grows towards infinity during the process, but so what?

Hope this helps.

Thanks, we are getting closer to the solution -- proving the maximum efficiency of the air to air, building heating, heat pump.