Japan Earthquake: Nuclear Plants at Fukushima Daiichi
The discussion revolves around the technical aspects and current status of the nuclear plants at Fukushima Daiichi following the earthquake and tsunami in Japan. Participants are seeking reliable information regarding the operational conditions, safety measures, and potential risks associated with the nuclear reactors in the aftermath of the disaster.
  • Some participants express skepticism about the reliability of media reports and emphasize the need for technical information from official sources like TEPCO and METI.
  • There are concerns regarding the reactor pressure levels, with reports suggesting that pressure may have exceeded safe limits, which some participants describe as a significant issue.
  • Questions are raised about the likelihood of a meltdown, with differing opinions on whether this is a realistic concern or media exaggeration.
  • One participant explains the role of coolant in a nuclear power plant, noting that it is essential for cooling the reactor and managing decay heat after shutdown.
  • There is discussion about the reactor's ability to be scrammed (shut down) and the implications of losing coolant, with some participants clarifying that decay heat continues to be produced even after shutdown.
  • Concerns are raised about the explosion of the containment building and its implications for safety, with speculation about the potential release of radioactive materials.
  • Participants discuss the wind direction at the time of the explosion and its potential impact on the dispersion of any radioactive materials released.
Participants do not reach a consensus on the likelihood of a meltdown or the implications of the current situation at Fukushima Daiichi. There are multiple competing views regarding the severity of the situation and the reliability of information being reported.
Participants note the limitations of available information, including the reliance on second-hand reports and the challenges in verifying the status of the reactors and containment structures. There are also unresolved questions regarding the operational status of safety systems and the exact nature of the explosion.
  • #11,251
westfield said:
Can someone clarify that? Perhaps they meant via seals, penetrations etc, not directly through the PCV wall?
Dunno what they meant, but hydrogen does indeed diffuse through just about anything you'd care to name, steel included. I doubt very much that this had any effect, though. There are myriad faster possible paths.
  • #11,252
http://www3.nhk.or.jp/news/genpatsu-fukushima/20110920/index.html Because the contaminated water level in buildings is not decreasing as quickly as the water treatment flow rate suggests, Tepco has calculated an estimate of the amount of ground water leaking every day into the buildings: from 200 to 500 tons. Tepco's thought is to keep the water level in buildings just below the ground water level. The NISA says "It is necessary that the long term contaminated water treatment plan takes into account the ground water leak rate. The amount of ground water changes with seasons, and we want to evaluate this".
  • #11,253
westfield said:
Ditto for the authors stating that TEPCO backpeddaled from the May 15th press release regarding Unit #4 Hydrogen coming from Unit 3 via SGTS. The authors state that the next day TEPCO retracted the theory because because it found closed valves would preclude that possibility. Again, I'm not implying its not true, just where is the source.
I would like to know their source too. This "retracting the next day" story reminds me another story about the unit 1 explosion analysis. On 4 June the Asahi had a story of hydrogen flowing backwards from the exhaust stack into unit 1 reactor building : http://www.asahi.com/national/update/0603/TKY201106030574.html then on the next day, on 5 June, the Asahi reported that Tepco had found that one of the concerned valves was built to close automatically if electric power is lost, so that the possibility that it was open is "extremely low" : http://www.asahi.com/special/10005/TKY201106040552.html
The hydrogen flow from unit 3 to unit 4 theory was stated in the Japanese government to IAEA report in June, and again in late August when Tepco analysed the radiations of the filters : "Result of Radioactive Dose Measurement at Unit 4 Emergency Gas Treatment System in Fukushima Daiichi Nuclear Power Station": http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_110827_02-e.pdf (27 August).
http://www.shippai.org/images/html/news559/FukuAccSummary110819Final.pdf "It is difficult to determine what happened in F4 from the above contradicting observations, but it is likely that there was some kind of dry-out and failure with the fuel". Dry-out is refuted by Tepco's September report :
tsutsuji said:
http://www.nikkei.com/news/category...39797E3E2E2E2;at=DGXZZO0195165008122009000000 This is the first time Tepco is providing the government with a report gathering details on the accident. Concerning the cores, it repeats previous statements. Concerning spent fuel pools, it says "it can be thought that the fuel was not exposed above the water level". At unit 4, pool temperature rose up to 90°C and water level decreased to 1.5 m above fuel.
http://www.asahi.com/national/update/0914/TKY201109140511.html 14 September: A Tokyo university research team has presented an analysis supporting the view that hydrogen produced in unit 4 spent fuel pool is one of the causes of the explosion. It does not demolish Tepco's theory that hydrogen flowed from unit 3 to unit 4, but it checks how much hydrogen from the pool might have contributed to the explosion. They mocked up the reactor building with an iron box, put boiling water in it and exposed it to radiations. Pushed by the steam pressure, hydrogen concentrates against the wall and exceeds explosive concentration level. Until now, Tepco has explained unit 4's explosion as resulting of hydrogen flowing backwards during the venting of unit 3.
  • #11,254
To: tsutsuji RE Your Post 11267
The link (translation) only describes general conditions, do you have a better link that describes the leakage you mention? Yours is the first I've seen to quantify the amount of leakage, which I've been thinking is "Massive" but nowhere as large as "from 200 to 500 tons"! Great Post! Thanks!
Question: Where is this leakage going, into the ground water table or almost immediately into the Pacific? I'm guessing that most is going into the Pacific!
  • #11,255
The leak is inwards (=from groundwater to the buildings), not outwards.
  • #11,256
2 Questions:
1. If the leakage is "Inward", then where is all the ocean pollution coming from?
2. I have a hard time imagining that much water flowing upward into the building from ground level, without some outside "change" in the geology of the landfill and or underlying ground,
like a new "crack" caused by the Big Quake.
BTW: That would be a real "gusher" especially since all of the "cooling water being injected, would serve to raise the water level inside the reactor containment building.
Perhaps a new crack caused by the Quake?
Thanks
  • #11,257
Latest chart info 9/20/11:
http://atmc.jp/plant/rad/
Sept 19th Reactor 1 spiked 411 Sieverts.
Sept 20th Reactor 1 currently 192 Sieverts.
This chart shows #1 RPV pressure almost constant for last six days!
http://translate.google.com/translate?hl=en&sl=&tl=en&u=http%3A%2F%2Fatmc.jp%2Fplant%2Frad%2F
  • #11,258
CaptD said:
2 Questions:
This was last discussed in the other thread at https://www.physicsforums.com/showpost.php?p=3491491&postcount=288
The water level in basements is supposed to be lower than the ground water level in nearby ground, so that the ground water seems to flow downward, not upward. If deep enough, a basement, like a well, naturally fills with water.
  • #11,259
That CAMS sensor for reactor 1 has been fluctuating wildly for many months now, so the spikes are not interesting. The other drywall CAMS sensor for reactor 1 broke completely a few months back so its even less easy to ascertain what's happening on that front.
Pressure readings have not fluctuated much for ages either, so I don't think that data deserves an exclamation mark.
  • #11,260
I would think any salt that accumulated during the seawater pumping would eventually hitch a ride on the now fresh water that is being pumped through leaving little or no salt in the reactors.
  • #11,261
joewein said:
That is not quite true: Since the RPV was vented into the S/C, the nuclear soup in there should have received a fair amount of fission products that give off decay heat. Nuclear decay, wherever it takes place in the buildings, is the only heat source around there. It's hard to say how much of the radioactive inventory is still in the core, how much is in the S/C and how much is in the flooded basements. The 4 Sv/h spot in unit 1 near where steam rises up from the S/C suggests to me that the S/C does still put out a lot of decay heat.
If the S/C temp goes up, it would suggest one of two things to me:
1) More radio-nuclides were washed out from the RPV by the added core spray water flow and that water somehow drained into the S/C at the bottom, increasing decay heat output there.
2) The added core spray resulted in more steam production (instead of conduction via the hot RPV metal), more steam condensation in the dry well and a larger flow of still hot condensate from there down into the S/C.
If that data is reliable and D/W radioactivity decreases while S/C radioactivity goes up, perhaps it means that fission products are getting flushed into the S/C, as per the first of my 2 theories.
In unit 2 the S/C is supposed to have ruptured. If radioactivity gets washed into the S/C from the RPV or D/W there's a good chance it will leak from there into the basements. In the best case it will eventually end up in the cesium sludge filters of the Areva/Kurion and SARRY plants. In the worst case it will end up in the soil or ocean.
Cheers for this response, these were the kinds of things I was wondering about.
Given that the change in temperature trends that I commented on started well before alternative spraying started at reactor 2, I have been looking for other possibilities. I note that they have sometimes had to adjust the water flow rate in recent month or so, because its fallen lower than they intended, so I suppose its possible that fluctuations in this could lead to a similar disturbance & relocation of material or changes in water/steam flows.Or perhaps some other thing else caused some kind of change around the end of August, perhaps an earthquake or some other work. I suppose I should also consider whether the nature of the water being injected has changed, e.g. is it warmer than it used to be, but in that case I would expect to see similar trends at the other reactors.
My main reason for interest in this stuff is that since reactor 2 was blamed for around 90% of the total radioactive release, it is of most interest to me. Given the likely location of the explosion there, and a report that suggested that some corium that escaped the reactor vessel could well find its way down to the basement that the suppression chamber lives in, I am interested in what's going on down there. And since I haven't seen similar temperature trends before (most rises being of the spike variety rather than a gradual climb), I thought I may as well draw attention to it.
I should probably also consider the possibility that the data we have about the suppression chamber may actually reflect changes to the conditions in the basement rather than the suppression chamber directly. e.g. If more core entered the basement, we would expect suppression chamber to be affected?
  • #11,262
Regarding the second option: IMHO it's possible to give a rough estimate about the amount of core still within the shroud through the dT/dt rate (torus capacity) and the remanent heat.
  • #11,263
Perhaps I should think more about the possibility that the water being injected is now following a path that means some of it is picking up more heat before ending up draining down into the suppression chamber, so warmer water is entering the suppression chamber, rather than being warmed more once it reaches that location?
There are very tentative signs that suppression chamber temps at reactor 3 might just have started to nudge up, but its many days too soon to make this claim seriously, and all of the rises I have been talking about are small, so I don't want to overstate my point.
Anyway as regards reactor 3 the other temperatures are surely more interesting right now, seeing what they are able to achieve with really quite high rates of water injection via the CS system at the moment. Its made quite a large difference so far, and recently they are placing even more emphasis on the pseudo-'cold shutdown' achievement that they always harp on about. So they would probably like to be able to have this flow rate on a sustained basis in order to produce numbers that look comfortably below 100 degrees C, but with the water treatment facilities as trouble-prone as they are, its likely not the easiest of balancing acts to get right.
  • #11,264
True, but it's going to be a slow process if the current pattern of water treatment doesn't change.
If the basements were drained by pumps as far as possible, there would be little salt left there. However, as long as the goal remains only not to let the basements overflow, with say 20,000 tons left sitting there and maybe 200 tons pumped out of each unit per day, as much as would be reinjected for cooling or leaking in from ground water, then it would merely be diluted by 1% per day. Since 0.99 ^ 69 = 0.5, the salt content would drop by half in a little over 2 months, or to a quarter in a little under 5 months.
I guess eventually, when the water treatment plants work well enough they will go for complete drainage of the basements, at least once, because that will make the desalination much more efficient.
For spent fuel pools they will have no choice but go for gradual dilution, because complete drainage followed by refilling is not an option.
  • #11,265
If they drain the basements, what will keep the melted fuel from catching on fire?
  • #11,266
The fuel would be mostly oxide, or hydrated oxides, which don't burn. Besides, it has not been determined that there is molten fuel outside of the pressure vessels.
  • #11,267
Not sure I understand you. If filtered, desalinated water is being pumped into the RPV, what difference does it make about basement water?? I assume salt removal from the RPV (where we assume a lot was deposited) is what is desired??
  • #11,268
Astronuc said:
At the moment, I don't see a 'real' chance of a meltdown. It is a worst case scenario, which is what licensing space is all about.
Astronuc said:
At the time of the explosion, the wind was apparently moving toward the northeast, so any vapor would be carried out to sea.
However, I understand that the building where the explosion has occurred is not associated with containment, but I have not been able to verify this.
Astronuc said:
I doubt the fuel will melt - but it might break into pieces - which will be trapped by the channels and bottom tie plate. The control rods may still be intact.
I think what I am trying to show here is that in the absence of hard data, you are naturally biased towards optimism. Not that I think it is a bad bias to have, mind you.
So, I think your remark needs qualification:
If the fuel has never reached temperatures high enough to become reduced to metal form then it
But of course, we do not have enough information to support OR definitively deny. So we speculate.
  • #11,269
If there's core on the floor (which is still a rather big if), I cannot see how it would go anywhere other than straight down, rather than flowing outwards (and upwards, I think?) to the S/C.
  • #11,270
I think there are a few people who have an erroneous mental image of where these so-called "basements" are under the reactor buildings (not talking about the turbine or other support buildings here, only the reactor buildings proper).
Once again, there are not excavated underground rooms or chambers directly underneath the RB structures enclosing the primary containment vessels. There is nothing directly under those except concrete and Earth (and possibly a layer of sand directly under the bottom of the steel shell).
The supression chamber encircles each PCV and sits in an annular excavation of sorts. Other than this circular cut-out that contains the SC and its supporting structures and equipment, there is no other "basement" to speak of.
With this in mind, it is impossible for corium that may have flowed (or dropped) out of the RPV to migrate downward and into the torus excavation. The drywell's vent pipe arrangement would not permit that to happen.
I apologize for the tone, but all this talk about corium eating its way through the lower extremities of the drywell and somehow ending up "in the basement" makes absolutely zero sense according to my understanding of the physical layout of the reactor buildings. It could go into the concrete substrate underneath the PCV, or into the Earth beyond the structural foundations of the buildings... but there is no basement direcly under the drywells.
  • #11,271
There is no requirement to keep the reactor buildings and turbine buildings submerged to be able to cool the fuel inside the reactor pressure vessel or primary containment.
The fuel can be cooled adequately as long as water can be sprayed onto it from either the feed water pipe or the core spray system in the RPV. If melted fuel has penetrated the bottom of the RPV and has dropped onto the base of the dry well, leaking water from those two injection sources should follow the same path that liquid fuel took and reach it.
About half the water in the basements of units 1-3 is standing inside the turbine hall basements. A quarter of the total is inside the reactor building basements (such as in the triangular corners of the octagonal space holding the suppression chamber). The remainder is in the trenches or the small radioactive waste treatment buildings adjacent to the reactor buildings. This http://www.tepco.co.jp/cc/press/betu11_j/images/110603a.pdf" by TEPCO has a breakdown. Since the water levels haven't dropped much since June, when this was published, the basic data should still be meaningful.
  • #11,272
I see your point. Yes, if we're talking about the salt in the RPV, it doesn't matter one bit whether the basements are drained completely or not. My point was about the larger volume of salt in the 100,000t or so of water in the basements. I am concerned about that because of metal corrosion and because of effects it may have on the concrete of the structure.
For the RPV, if water injected into the core leaks out via either the presumably damaged recirculation pump seals or through damage to the RPV bottom from melting fuel, then the salt probably has already been flushed out. Only if the RPV bottom was completely intact and the cooling water boiled off before it reached a level high enough to leak via the pumps or other pipes should there still be significant amounts of salt in the RPV.
The minimum flow of 3.8 m3 per hour (units 1 and 2 in recent months) amounts to 90 t of water a day, which could dissolve about 30 t of salt per day (assuming none of it boiled off). It's been about 180 days of fresh water cooling so far, so even if the vast majority of the cooling water had escaped as steam rather than liquid the rest should have been enough to flush out the accumulated salt.
  • #11,273
http://www.yomiuri.co.jp/science/news/20110920-OYT1T01060.htm The calculation is the following:
contaminated water at the end of may: 105,000 tons
contaminated water on 13 September: 102,000 tons
amount processed at the water treatment facility during that time: 90,000 tons
water added in the basements during that time: 90,000 + 102,000 - 105,000 = 87,000 tons
water injected into reactors (estimate) : 47,000 tons
ground water and partly rain [before the roofs were repaired ?] : 87,000-47,000 = 40,000
[PLAIN]http://www.tokyo-np.co.jp/article/feature/nucerror/list/images/PK2011092002100038_size0.jpg
light blue: the amount of contaminated water as suggested by the water treatment flow
dark blue: the actual amount present in basements
black and white arrow: possibility of ground water seeping in
source: http://www.tokyo-np.co.jp/article/feature/nucerror/list/CK2011092002100008.html?ref=rank
http://www.nikkan.co.jp/news/photograph/nkx_p20110920-2.html From October, the decontamination process will rely on SARRY as the main facility. Dedicated to the backup of SARRY and Kurion, the Areva system will be used as little as possible. Instead of diminishing the volume of water in turbine buildings' basements, it will be momentarily kept at a fixed amount. The volume injected into the reactors will be increased in order to enhance the cooling of the reactors. SARRY will be operated using both lines, which will bring the processing rate from 25 to 50 tons per hour. SARRY has a better utilization rate (92.1% during the week before 13 September) than Areva-Kurion (83.3%). SARRY was developed mainly by Toshiba, using American technology as base. With only two pumps, the number of moving parts is small. While the Kurion-Areva system is a complicated, "tricky" system, to such extent that operators misunderstood closed valves as being opened, SARRY is easy to operate. Japanese companies such as Organo and Swing (Ebara group) are involved in preparing low contaminated water treatment systems. "In any case new water treatment plans are necessary", a Tepco manager said, suggesting Tepco turns its expectations to the Japanese water treatment companies together with Toshiba and Hitachi. At present low contaminated water is stored in temporary tanks. It is possible that this water will be released into the nature after being purified. For this purpose the understanding of local communities and of the fishing industry must be obtained. "I understand very well that the water treatment companies have the technology to bring the contaminants below the detection level", the same Tepco manager said.
http://www.tepco.co.jp/nu/fukushima-np/images/handouts_110920_02-j.pdf explanations (in Japanese, not yet translated) of the 3:35 minute long video available at http://www.tepco.co.jp/en/news/110311/images/110920_1e.wmv (20 MB)
  • #11,274
On the contrary, I only mention the basement stuff because it was discussed in a proper report, rather than being completely ignorant speculation. I will now spend some time struggling to find out which report it was in, but I am sure it was mentioned in this thread at the time.
I don't blame you for your tone, considering how many times I myself have become tired with some of the wacky theories we have seen people cling to despite having few facts in their favour.
  • #11,275
Happily I was able to find the report quickly.
The Impact of BWR Mk 1 Primary Containment Failure Dynamics On Secondary Containment Integrity.
http://www.osti.gov/bridge/servlets/purl/5835351-nR29Hq/5835351.pdf
Pages 5 onwards are of interest. For example it says the following, and there are also some diagrams:
Should the liner fail near the drywell floor elevation, the most probable sites for blowdown entry into the secondary containment are the reactor building basement torus room and the second floor of the reactor building (Exhibit 2). The transport path for the blowdown is the gap between the drywell shell and the surrounding reactor building concrete, and the annular gaps surrounding the drywell vent pipes and penetra- tions. These gaps provide a 145 ft2 (13.5 m2) flow path into the torus room and a 135 ft2 (12.6 m2) flow path into the second floor of the reactor building. Since elevated drywell pressures and temperatures result in swelling of the drywell liner and a reduction in the gap between the liner and the reactor building concrete (Exhibit 3), it appears that the etfective flow path area for drywell blowdown would be limited by the actual size of the drywell shell rupture or the available space between the liner and the surrounding concrete
They admit there is considerable uncertainty, but as I understand that the 'torus room' is part of the basement, so I think you were wrong to be so dismissive of these possibilities.
  • #11,276
But the IF statement is incorrect.
The UO2 fuel is in the form of an oxide + fission products. Some fission product species become metallic inclusions because other more reactive elements tie up any free oxygen. The environment in a BWR is oxidizing, especially when the hydrogen gas escapes.
The Zircaloy cladding and channel, and stainless steel would oxidize rapidly at temperatures below metal. Therefore, if the fuel melted, it is in the form of oxides, higher order oxides, and probably more likely hydrated oxides - which do not burn. There is no IF about it.
The presence of seawater would enhance the corrosion of steel and the fuel to some extent.
Besides designing nuclear fuel and analyzing it under normal operating conditions, I also simulate it under accident, failed and degraded conditions.
I wasn't looking at evidence optimistically, I was just looking at the evidence. Any optimism was quashed with the first explosion, which indicated that they had failed to contain the accident, as was also indicated by the activity outside of containment.
  • #11,277
OK I'm going to go one better, with a report that explores the possibility of molten core penetrating the drywell.
http://www.osti.gov/bridge/servlets/purl/6250306-2XRtiq/6250306.pdf
What becomes clear when reading this document, is that the possibility they are exploring is not about the core traveling downwards from the pedestal area, but what happens if there is enough of it, at sufficient temperatures, to travel outwards, reach a steel wall and melt through it pretty quickly.
As they point out, there are a good number of factors which can prevent this theoretical scenario from happening, e.g. if the temp isn't high enough or there isn't enough of it to reach the wall, or if it travels downwards through concrete quite quickly then there won't be enough of it left higher up to reach the steel walls. But at the time this report was written many years ago, it sounds like this was a new scenario that hadn't been properly considered before, and they decided it was plausible enough to add it to the list of possible failure modes (some of the others are mentioned in the report).
  • #11,278
The paper mentions "a wide range of hypothetical core melt scenarios." It does not address plausibility or possibility. The group is charged with considering hypothetical, often worst-case, scenarios - no matter how implausible they might be. It would be like an automotive engineer crash testing a car at 200 or 300 mph, when the top speed would be 120 mph due to engine limitations and drag.
  • #11,279
I should point out that my use of the term 'wall' is rather sloppy, should read the report to get a proper sense of what it says as I have not likely done an excellent job of abbreviating it.
Also I don't want to make it sound like I am a huge believer of ideas that involve a great big quantity of molten core doing something very dramatic. They remain possibilities to me, but not ones which we have had a lot of excellent data pointing clearly in the direction of.
So I bring this stuff up now only because, if we are going to have any discussions about various theoretical possibilities that involve corium and basements, I don't want the fact that the torus room & other basement spaces are not directly underneath the reactor pressure vessel to be taken too far. Especially if we are not trying to suggest that the entire core is sitting in the basement in the form of a big blob, but rather the possibility that just some core material has found its way down there by one mechanism or another.
  • #11,280
I had missed YOUR point about the salt remaining in the basement. No doubt others here understand the basement construction better than me. So far, I think of the basement as the area around the torus and the control rod drive room.
Clearly the corrosion rate is a serious concern, particularly if it causes the torus to fail/leak (assuming it isn't ALREADY leaking). Particularly, unit 2 appears to have suffered torus damage - or at least the bellows connecting it to the drywell. Somewhere I read the weakest part, pressure wise, was those bellows. I guess we will eventually learn the exact nature of that damage.
No doubt, additional leaks and problems will arise - for years. IMHO the best anyone can do is solve them as they occur.
49K
  • · Replies 41 ·
  • · Replies 2K ·
60
459K
20K
  • · Replies 763 ·
279K
  • · Replies 38 ·
16K
12K