Japan Earthquake: Nuclear Plants at Fukushima Daiichi
The discussion revolves around the technical aspects and current status of the nuclear plants at Fukushima Daiichi following the earthquake and tsunami in Japan. Participants are seeking reliable information regarding the operational conditions, safety measures, and potential risks associated with the nuclear reactors in the aftermath of the disaster.
  • Some participants express skepticism about the reliability of media reports and emphasize the need for technical information from official sources like TEPCO and METI.
  • There are concerns regarding the reactor pressure levels, with reports suggesting that pressure may have exceeded safe limits, which some participants describe as a significant issue.
  • Questions are raised about the likelihood of a meltdown, with differing opinions on whether this is a realistic concern or media exaggeration.
  • One participant explains the role of coolant in a nuclear power plant, noting that it is essential for cooling the reactor and managing decay heat after shutdown.
  • There is discussion about the reactor's ability to be scrammed (shut down) and the implications of losing coolant, with some participants clarifying that decay heat continues to be produced even after shutdown.
  • Concerns are raised about the explosion of the containment building and its implications for safety, with speculation about the potential release of radioactive materials.
  • Participants discuss the wind direction at the time of the explosion and its potential impact on the dispersion of any radioactive materials released.
Participants do not reach a consensus on the likelihood of a meltdown or the implications of the current situation at Fukushima Daiichi. There are multiple competing views regarding the severity of the situation and the reliability of information being reported.
Participants note the limitations of available information, including the reliance on second-hand reports and the challenges in verifying the status of the reactors and containment structures. There are also unresolved questions regarding the operational status of safety systems and the exact nature of the explosion.
  • #12,961
MadderDoc said:
Gentlemen, it is such a pleasure working with you. On reviewing the video using autogain, as inspired by Spunky's wonderfully improved video, and using westfield's directives along the route, I get the timeline below of the camera position relative to landmarks of the cavity wall.
Position A is at the outside wall of the concrete shield, B is at the first notch on the wall, C is a small notch in the wall which I would think is close to as far as the plug goes, when it is fully inserted. Behind C and deeper into the void, we are inside the room that was behind the plug in its normal position. At D not far from C, the room seems to narrow in considerably, which might mean we are now inside the cylindrical part of the hatch construction, and we could potentially now be seeing the lid of the hatch at some time during the approximately 2 minute sequence which follows, until the camera finally exits.
Entry times:
A: 0:54.4
B: 0:58.4
C: 1.07.8
D: 1.09.0
Exit times
D: 3:05.3
C: 3:08.0
B: 3:19.0
A: 3:31.2
Thanks and nice orderly sequenced parsing of all that mess! I agree with what you say.
At some moments I get the feeling there may be a corner at the 'slime trail' (leaky flange) that runs the length of the trail, meaning one side of the trail angles up 90˚, but I'm not sure. But if so, that would probably be the metal of a hatch insertion into the PCV concrete. I'm already confident one side of the trail is painted metal of the hatch insertion, just not sure if it angles at 90˚ from the wall. :)
I'm now confident (due to the contrast-suppressed video that makes clear the same location during entry) that the little red and white objects are in fact on the floor in the hatch passageway near its opening. I guess we can't be sure when they got there, perhaps they fell from something during efforts to get a look into the crevice. But if they were there before the first post-tsunami inspections, they provide clear evidence that explosive forces did not blast through the crevice as such forces would surely not leave such small lightweight objects there.
To Spunky: looking at these streaking particles, there are times I get this weird impression that they move as being taken by a wind, is it only my brain doing this, is it some kind of illusion, or is there a draught at the floor in that room?
Yes, some kind of wind turbulence would explain the irregular and sometimes curved paths of the chips. I'd like to see what the camera probe looks like. I wonder how it maintained height as it extended, I presume it's on some rigid extension, but it also seems to have some range of flexibility in edging around the corners. And then the camera at its end rotates too. So it might be fairly sophisticated. Perhaps it has a small fan on it? Probably not, just thinking out loud.
To both of you: Could that yucky rusty patch be on such presumed horizontal floor inside the metal portion of the hatch?. I can't get away from Tepco's statement that the water is seen on a floor.
I think we're looking at the metal of the hatch insertion (probably not the hatch door). The paint appears to flake off that metal surface, and the concrete in that area is not painted.
  • #12,962
etudiant said:
While it is true that after the 2 H2 and the O2 molecules ( 3 molecules in all) combine, there are only 2 molecules of H2O left as a result, these residual molecules have the benefit of a good deal of energy released by the combination. There is plenty of energy to form an expanding cloud of steam from the reaction, even if the number of molecules is cut by a third.
I'm confident that we saw misty water vapor in the Unit 1 shockwave (note the sliver-moon-shaped misty cloud that shoots upward biased to the left in the first instants of the explosion), consistent with a hydrogen-oxygen synthesis reaction. But that volume of water vapor was tiny compared to the Unit-3 mushroom cloud and it vanished in fractions of a second. The Unit-1 vapor also showed no signs of being hot.
So how would you account for the volume of persistent hydrogen-oxygen-synthesis vapor necessary to form the massive Unit-3 mushroom cloud? And why would the same reaction at Unit 1 produce such a relatively tiny amount of water vapor?
  • #12,963
Having 1000kg of H2 on hand to detonate and actually burning all 1000kg in the perfect 2:1 mix with rapidly accumulating H20 are two different things. Does a 50% burn still provide sufficient energy to explain all observed damage?
  • #12,964
jim hardy said:
Thanks m'doc & etud't
<snip>
plodding along, behind as usual. It's my asperger's.
old jim
You and nearly everyone else here are way ahead of me when it comes to the real nitty gritty of chemistry.
I don't have the knowledge to do the math and this probably was covered previously as it's seems a fairly obvious thing to consider - All I know is there would be some energy potential in the heat & water of the SFP.
Would the U3 SFP be creating an appreciable amount of heat and steam at the time of the explosion and if so, can this play any meaningful part in the characteristics of the explosion?
  • #12,965
The thing in the unit 1 explosion video is the trailing edge of a rapidly decelerating shock front, made visible by atmospheric water condensation (there's a rather sharp pressure dip that "follows" the pressure spike, of course).
I miss the #3 explosion thread, boy do I.
  • #12,966
To your question: there is no way you'd get a partial H2 combustion in air.
This isn't a gasoline engine (even those have to be rather finely tuned to avoid "knocking" - the leaner the mix the worse the danger of detonation, as oxygen, not fuel, is the limiting factor).
  • #12,967
The 5th mid long term meeting was held yesterday: http://www.meti.go.jp/earthquake/nuclear/20120423_02.html
The 4th meeting (28 March 2012) : https://www.physicsforums.com/showpost.php?p=3838108&postcount=12764
The 3rd meeting (27 February 2012) has been translated into English on Tepco's website : http://www.tepco.co.jp/en/nu/fukushima-np/roadmap/conference-e.html
23 April government-Tokyo Electric mid and long term response committee, steering committee (5th meeting)
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02a.pdf Agenda
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02b.pdf Participants
Document 1
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02c.pdf Abstract of the proceedings of 4th steering committee meeting
Document 2: Plant status
Document 2-1: Plant status
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02d.pdf Plant parameters
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02e.pdf Accumulated water storage status
Document 3 Study and execution of each special plan
3-1 Cooling by closed loop water injection
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02f.pdf Schedule
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02g.pdf Report on the results of mock-up experiment for the purpose of installing alternative RPV thermometers
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02h.pdf Measurement of unit 4 spent fuel pool inclination and desalination status
3-2 Treatment of accumulated water
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02j.pdf Schedule
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02k.pdf Plan to lay polyethylene pipes at water treatment facilites
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02m.pdf Progress status of subdrain purification test
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02n.pdf Plan to reduce volumes of groundwater seeping into units 1~4 buildings by groundwater bypass
3-3 Countermeasures to reduce environmental radiations
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02p.pdf Schedule
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02q.pdf Management of debris, cut down trees, generated by the response to the accident
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02r.pdf Plan to decontaminate the whole power plant premises
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02s.pdf Results of scattered debris survey
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02t.pdf Sinking of zeolite sandbags and checking of the results
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02u.pdf Operational achievements of seawater closed loop purification system
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02v.pdf Results of evaluation of additional releases from reactor building's primary containment vessels
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02w.pdf Evaluation of yearly radiation exposure at plant premises boundary
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02x.pdf Sampling survey of fish and shellfish in the 20 km range from Fukushima Daiichi nuclear power plant
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02y.pdf Measures to improve monitoring posts' environment
3-4 Improvement of working conditions
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02z.pdf Schedule
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02aa.pdf Plan to turn Fukushima Daiichi NPP's seismic isolated building (part of it) into an area outside the radiation management area
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02bb.pdf Test run of screening and decontamination facility for vehicles at Fukushima Daiichi NPP
3-5 Countermeasures for spent fuels pools
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02cc.pdf Schedule
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02dd.pdf Debris removal work, reactor building top part, unit 3
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02ee.pdf Debris removal work, reactor building top part, unit 4
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02ff.pdf Results of unit 3 underwater survey into spent fuel pool for the purpose of debris removal
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02gg.pdf Unit 4 spent fuel pool debris map
3-6 Preparations for fuel debris removal
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02hh.pdf Schedule
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02jj.pdf Execution of onsite survey as part of "Development of remote controlled decontamination techniques inside buildings"
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02kk.pdf Onsite survey into unit 2 reactor building basement torus room
3-7 treatment and disposal of radioactive waste
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02mm.pdf Schedule
Document 4
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_02nn.pdf roadmap progress (abstract)
23 April 2012 government-Tokyo Electric mid and long term response committee, technical development progress headquarters (5th meeting) (http://www.meti.go.jp/earthquake/nuclear/20120423_01.html )
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01a.pdf Agenda
Document 1
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01b.pdf Abstract of the proceedings of 4th meeting
Document 2-1
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01c.pdf Orientation of evaluation of achievements and revisions of research and development projects (draft)
Spent fuel pool countermeasures working team
Evaluation of long term soundness of fuel assemblies removed from spent fuel pools
Document 2-2-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01d.pdf Project evaluation (draft)
Document 2-2-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01e.pdf Project achievements, etc. in fiscal 2011 (JAEA)
Machinery and equipment development etc. sub-working team
Document 2-3-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01f.pdf Project evaluation (draft)
Document 2-3-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01g.pdf Project achievements, etc. in fiscal 2011 (Toshiba, Hitachi GE, Mitsubishi Heavy Industries)
Development of techniques to determine PCV leakage points
Document 2-4-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01h.pdf Project evaluation (draft)
Document 2-4-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01j.pdf Project achievements, etc. in fiscal 2011 (Toshiba, Hitachi GE, Mitsubishi Heavy Industries)
Development of techniques to repare PCV
Document 2-5-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01k.pdf Project evaluation (draft)
Document 2-5-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01m.pdf Project achievements, etc. in fiscal 2011 (Toshiba, Hitachi GE, Mitsubishi Heavy Industries)
Development of techniques to survey inside PCV
Document 2-6-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01n.pdf Project evaluation (draft)
Document 2-6-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01p.pdf Project achievements, etc. in fiscal 2011 (Toshiba, Hitachi GE, Mitsubishi Heavy Industries)
Development of techniques to evaluate soundness of RPV/PCV
Document 2-7-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01q.pdf Project evaluation (draft)
Document 2-7-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01r.pdf Project achievements, etc. in fiscal 2011 (Toshiba, Hitachi GE, Mitsubishi Heavy Industries)
Development of techniques to manage debris criticality
Document 2-8 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01s.pdf Fiscal 2012 plan for development of techniques to manage debris criticality
Reactor inside status grasping and analysis sub-working team
Upgrading of accident progression analysis for the purpose of grasping reactor inside status (implementation of user tuning type)
Document 2-9-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01t.pdf Project evaluation (draft)
Document 2-9-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01u.pdf Project achievements, etc. in fiscal 2011 (Toshiba)
Upgrading of accident progression analysis for the purpose of grasping reactor inside status (structural model type)
Document 2-10-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01v.pdf Project evaluation (draft)
Document 2-10-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01w.pdf Project achievements, etc. in fiscal 2011 (Institute of Applied Energy)
Characterization and preparation of treatment of fuel debris sub-working team
Characterization using mock-up debris and development of debris treatment techniques
Document 2-11-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01x.pdf Project evaluation (draft)
Document 2-11-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01y.pdf Project achievements, etc. in fiscal 2011 (JAEA)
Construction of plan for material accountancy of fuel debris
Document 2-12-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01z.pdf Project evaluation (draft)
Document 2-12-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01aa.pdf Project achievements, etc. in fiscal 2011 (Tepco)
Treatment and disposal of radioactive waste working team
Development of techniques for treatment and disposal of secondary radioactive waste generated by contaminated water treatment
Document 2-13-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01bb.pdf Project evaluation (draft)
Document 2-13-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01cc.pdf Project achievements, etc. in fiscal 2011 (JAEA)
Development of techniques for treatment and disposal of radioactive waste
Document 2-14-1 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01dd.pdf Project evaluation (draft)
Document 2-14-2 http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01ee.pdf Project achievements, etc. in fiscal 2011 (JAEA)
Document 3
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01ff.pdf Results of public appeal for technical catalogue for equipments and machinery (etc.) for fuel debris removal toward decommissionning of Fukushima Daiichi NPP units 1~4
Document 4
http://www.meti.go.jp/earthquake/nuclear/pdf/120423/120423_01gg.pdf Activities of the remote control technical task force
  • #12,968
Thanks! You're probably right. A nice example of that phenomenon is seen here. Does this imply that Unit 1 was a detonation, or can this condensation happen with subsonic shockwaves?
  • #12,969
Gaaah. I really wish that thread hadn't been wiped out.
The nice condensation cloud happens during transitions from super- to sub-sonic or viceversa (google transonic shock and you'll find a few beautiful pictures). Your picture is also very educational by the way, as you can see the pressure front has moved on (the white circle on the water has a much bigger radius than the wispy white cloud).
  • #12,970
Page 3/6
2. Surveyed locations (representative)
Page 4/6
3. Survey results
Page 5/6
4. Summary
* With this survey, we could check part of the status of the fallen debris inside pool and part of the status of the fallen FHM. Also, although it is only a tiny part, we could check the fuel and at the checked location no fuel handle deformation, etc. was observed.
* With this survey, we could not check the whole fallen debris status. In the future, depending on the reactor building debris removal status, we plan to intermittently perform more surveys.
  • #12,971
Page 6/6
(Reference) Outline of Fuel Handling Machine
  • #12,973
Thanks tsutsuji!
Looks like the track guide of the FHM is located (identified as '3' on the overhead map photo above) about right where we'd expect it to be, implying that the crane was just slightly dislodged from its track and fell straight down from where it was, still largely in its original east-west orientation.
  • #12,974
Unless we will introduce assumptions of something quite out of the ordinary about the pool (e.g. a leak/sloshing/siphoning event that had drained most of its water, or re-criticality), the pool could not have been a meaningful source of steam in the context of the unit 3 explosion.
Assuming just its native state (1400 m3 water, and a decay heat of 0.54 MJ/s) the temperature of that amount of water could have increased by at most 8 oC/day. And the explosion happened less than 3 days after pool cooling stopped on March 11th. Over that period, the water in the pool would likely have become warm to the touch, but it would have been far from boiling.
  • #12,975
Some interesting stuff there.
This one deals with how to improve modelling to establish core damage etc.
http://www.tepco.co.jp/en/nu/fukushima-np/roadmap/images/m120314_02-e.pdf
It gets quite interesting from page 25 onwards because they have updated their model analysis of the 3 reactors. Here are notable changes from older versions:
Reactor 1 they have an assumption of leakage from in-core monitor guide tube, and leakage due to MS line flange damage.
Reactor 1 core melt diagrams show earlier progression to fully melted state & rev damage - now just 8.6 hours after SCRAM rather than 15 hours.
Reactor 2 they have the assumption that water in the torus room may have helped cool the S/C, which helps their simulation to produce pressure figures that are in better alignment with the measured data. Assumed D/W leakage now occurs much later, at about the time we see photo evidence of steam escaping from blowout panel.
Reactor 2 core melt & rpv damage analysis is still producing results where rev damage doesn't happen for a rather long period of time, its now even longer after the updated analysis, and more of the fuel remains in RPV.
Reactor 3 they have gotten their model to match the data better by putting in new assumptions about how HPCI was controlled by operators when it was in use. They still have a problem getting model results to match measured containment pressure during time when HPCI was in use, and they wonder whether this may be down to thermal stratification in the S/C.
Reactor 3 core & rpv damage analysis is much like reactor 2, now shows even greater lengths of time and lack of damage.
Whilst I do not rule out the possibility of substantial quantities of fuel remaining in RPV at reactors 2 & 3, I think they are well aware that their analysis in this regard is probably out of whack with reality.
  • #12,976
And this document about fuel removal difficulties has a few things that relate to recent discussions here:
http://www.tepco.co.jp/en/nu/fukushima-np/roadmap/images/m120314_01-e.pdf
Page 6 we see an example of how to fix leaks at the large equipment hatch, with diagram.
Page 17 we see a robot view up the north-east stairs of reactor 3, where there is much debris. Daylight can be seen through hole above. I attempt to relate this to recent discussion about black/hole area of reactor 3, and offer the suggestion that a stairwell in this area is involved.
  • #12,977
I had seen that diagram a number of times, but I did not realize what this was about. As it was only this diagram without a narrative and without dimensions, not being aware that there was a trouble at unit 3 and that this was badly needed, I though it was just an example, of the kinds of technologies that might be needed if you want to enter the PCV with a robot or something.
  • #12,978
Perhaps that is more like a fact than an assumption:
"From approximately 01:00 until around 02:00 on March 12, the shift team members
equipped with self-contained air breathing sets (self-air-set), small flashlights and rubber
boots went to the RCIC room on the first basement floor of the R/B of Unit 2 to inspect
the operating condition of the RCIC system. The RCIC room was flooded
and the water level was just below the upper edge of their rubber boots.
When they opened the door, water gushed out of the room and they could not go in.
"At approximately 02:10 that day (March 12th), members of the shift team with the same outfits as the previous
went to the RCIC room of the R/B at Unit 2. Though the level of water inside the room had risen,
the shift team members went inside to check the operating condition of the RCIC system.
"It was confirmed with Unit 2 at around 04:00 on March 12 that water level showed a
decrease for the condensate storage tank, the water source for the RCIC
. Accordingly,
the shift team decided to change the water source for the RCIC from the condensate
storage tank to the S/C in order to maintain the water level of the condensate storage
tank and control increase in S/C water level."
accordingly..
"From around 04:20 to around 05:00 that day, some shift team members wearing the
level C outfits and full-face masks went to the RCIC room on the first basement of the
Unit 2 R/B. The RCIC room was flooded and the depth of water was up to about the
upper edge of the rubber boots the team members were wearing
and the temperature and humidity were high. "
  • #12,979
The outline of the landing of that staircase at the fifth floor is somewhat north of the big black hole. I believe its outline can be made out from photos of the building top, but its state cannot be seen since too much debris has landed on top of it. I believe the view up to the sky has been enabled by yet another black hole in the fifth floor, east of that staircase landing, and close to the wall. This latter hole seems to have relatively clean edges, and to coincide with the position of some stationary equipment likely connected to a penetration of the 5th floor there. The equipment at the wall in that corner of the building was pushed out through the wall frames during the explosion, and could be seen hanging on to the wall outside apparently in defiance of gravity, before that platform for debris clearance came up.
  • #12,980
I speak of assumptions because this stuff is about modelling, and the assumptions they feed into the model. I do not doubt that there was water in the torus room.
  • #12,981
MadderDoc said:
Unless we will introduce assumptions of something quite out of the ordinary about the pool (e.g. a leak/sloshing/siphoning event that had drained most of its water, or re-criticality), the pool could not have been a meaningful source of steam in the context of the unit 3 explosion.<snip.
Cheers.
  • #12,982
SpunkyMonkey said:
Thanks tsutsuji!
However note that '4' , photographed in a perpendicular to direction to '3', and at some distance from it, is the lower NW end of the north face of the bridge, which on the intact machine was mounted just above, and only a meter away from the track guide. Indeed the video of '4' shows the flange through which this corner was connected to the frame piece that is/was mounted on top of the track guide (albeit the mounting flange now looks sadly beaten up, de-bolted and without its partner)
  • #12,983
Sorry, I think it was the pleonastic use of 'assumption' and 'may' in your expression that threw me off.
  • #12,984
MadderDoc said:
<snip>
U3. FL5, NE corner - large ducting right in the corner diving down into the floor & possibly the gravity defying equipment near it -
  • #12,985
The orientation marked "4" on that diagram is misleading.
In the video & still shot marked "4" we are viewing the vertical plane of the northern side of the bridge not the horizontal "top" of the bridge as the arrow tends to indicate. What we are seeing most of is the personnel "catwalk" with the driveshaft under it which is\was? bolted along the northern face of the FHM bridge proper.
In the video we only see a small glimpse of the main part of FHM bridge truss structure in the background, through the "catwalk" truss and possibly the FH Machine itself in the furthest background. It's very difficult to tell how "apart" the various sections of the whole FHM are but as Madder Doc mentioned, it's clear the heavy "end" piece shown in view "3" parted from this catwalk section in view "4".
Here is a quick diagram I made that didn't turn out that clear and features some terrible abuses of perspective & photoshop :)
Also, to be clear, it's comparing to Unit 2's FHM which is a little different but close enough for the purpose. There are just no decent images of the northern side of U3's FHM as it was.
PS - if this sort of post is getting just too off track then someone please say so - it is a bit of a messy thread at times and perhaps another thread for this sort of PCV hatch \ FHM \ Holes in floor type of discussion would be useful and make this sort of thing less disruptive to this thread? Perhaps rename & recycle the Unit 2 thread which is very quiet.
  • #12,986
Different Topic:
Unit 1 IC mystery - why did they shut down the IC on March 11th after 6 pm when they activated it barely a couple of minutes ago?
So I had this idea...
Here's a 1991 GE patent for an Isolation Condenser:
http://www.patentgenius.com/patent/5158742.html
It's noted that:
In order for the isolation condenser to be effective for maximizing heat transfer from the reactor steam to the pool water, the tubes must be relatively thin and single walled, but, they must be also strong enough to contain the relatively highpressure of the reactor steam being channeled therethrough. Since the reactor steam is channeled through the containment building and through the condenser tubes disposed outside thereof, the tubes themselves provide only a single barrier againstrelease of the reactor steam, which is radioactive. If one or more of the condenser tubes fails during operation, the reactor steam will leak into the isolation pool and be released through a conventional vent to the atmosphere, which therefore wouldrelease radiation to the atmosphere outside the containment building.
In order to reduce the risk of radioactive steam release from the condenser in the event of a failure thereof, conventional isolation valves are provided both in the conduits leading from the pressure vessel or containment building to theisolation condenser and in the conduits returning the condensed steam back to the pressure vessel. The isolation valves are normally closed valves which must be energized to open during operation so that, upon any failure of the isolation condenserwhich might release steam therefrom, the fail-safe condition will allow the valves to close upon interruption of power thereto which will stop the flow of reactor steam to the isolation condenser and, therefore, prevent any further release of radiationto the atmosphere.
Perhaps they feared that high reactor pressure would burst the IC-tubes? And that's why they shut it down...
  • #12,987
I see what you mean, it also thought it could be more instructive. But the intent of the arrow to mislead is plausibly deniable. The arrow points as best it can to an object that is not visible in the drawing.
Neat. See that is more instructive! Attached is a suggestion for modification of the markup of unit 3 added x-beams, as I think they are at that end of the bridge.(Lest it might mislead into thinking you've seen more of the length of the bridge in that video, than you actually have.)
  • #12,988
Yes, maybe. According to the most recent narrative of events, the IC was switched on, while it was observed whether steam would be emitted from the IC exhausts. (Immediate powerful steam emission from the exhaust on operation of the IC was apparently thought of as indicating correct operation) As little or no steam was observed it was thought the system was not operating properly due to low water level in the condenser, and the system was shut down out of fear that "uncooled steam may cause IC pipes to break and result in releasing contaminated radioactive steam into the atmosphere."
  • #12,989
housekeeping
I'd rather not, given the #3 explosion thread debacle. Perhaps we all could start using post titles properly instead?
  • #12,990
Page 2/12
Outline
Measures dealing with liquid waste
Concerning liquid waste, in the future we shall perform the necessary studies mentioned below, and by performing the related countermeasures, it is intended not to simply release contaminated water into the sea.
①Radical measures against groundwater seeping into reactor buildings, etc., which is responsible for water increase.
②Measures for securing the upgrading of the decontamination capacity of the water decontamination facilities and for securing the stable running of those facilities including backup equipments to be used during breakdowns.
③Further installation of onshore equipments for contaminated water management
It must be noted that without the approval of concerned ministries, releases into the sea will not be performed.
It will continue in the future
As a radical measure against groundwater seeping into buildings, we are currently working for the recovery of the subdrains, but especially around the reactor buildings, the radiation dose being high, the degree of difficulty is high.
As an auxiliary measure in support of the subdrain, the following items are proposed:
The groundwater that flows down from the mountain side is to be pumped from a point upstream from the buildings (O.P. + 35 m level), and the watercourse is changed (groundwater bypass).
■ As a consequence of the groundwater bypass, the underground water level in the surroundings of the buildings (especially on the mountain side) is lowered, and the seeping volume into building basements is regulated.
■ The pumped water is bypassed to the sea using a special channel. Also, monitoring of the water quality is performed.
Page 3/12
Concept
Present status
■Water mainly flows through the permeable layer from mountain side to seaside.
■Part of the groundwater seeps into the buildings during its way to the sea → increase of accumulated water inside buildings
In order to regulate the volume of groundwater seeping into the buildings, the subdrain system is under restoration
Proposal
■ The groundwater that flows down from the mountain side is pumped from a point upstream from the buildings, and the underground water's watercourse is changed (groundwater bypass).
As before, the subdrain system restoration work continues
Page 4/12
Feasibility status
Page 5/12
Estimated effects
Assumption used to calculate effects : groundwater flows through building side walls as a consequence of the difference between the groundwater level and the inside building water level.
50K
  • · Replies 41 ·
  • · Replies 2K ·
60
471K
21K
  • · Replies 763 ·
284K
  • · Replies 38 ·
17K
12K