Addressing Intermittent Over Current Faults in Dual UPS System

  • Thread starter Thread starter jtweedie@atdesk.com
  • Start date Start date
  • Tags Tags
    Static Switches
Click For Summary
SUMMARY

The discussion centers on addressing intermittent over current faults in a dual UPS system involving UPSA and UPSB, each handling approximately 15KW loads. When STSA transfers from source1 on UPSA to source2 on UPSB, the inverter of UPSB faults due to over current. This indicates that UPSB is not adequately sized to handle the combined loads of both UPS systems. The conclusion is that both UPS systems must be rated to supply the total load of A and B to prevent these faults.

PREREQUISITES
  • Understanding of UPS systems and their configurations
  • Knowledge of static transfer switches (STS) and their operation
  • Familiarity with load balancing in electrical systems
  • Basic concepts of electrical fault analysis
NEXT STEPS
  • Research sizing requirements for UPS systems to handle combined loads
  • Learn about static transfer switch configurations and their impact on UPS performance
  • Investigate methods for load balancing across multiple UPS units
  • Explore fault analysis techniques specific to inverter systems
USEFUL FOR

Electrical engineers, UPS system designers, and technicians involved in power management and redundancy solutions will benefit from this discussion.

jtweedie@atdesk.com
Messages
4
Reaction score
0
I have two UPSs, UPSA & UPSB, and two static transfer switches, STSA & STSB. UPSA feeds Source1 on STSA (preferred) and Source1 on STSB. UPSB feeds Source2 on STSA and Source2 on STSB (preferred). Each UPS has approxiamately a balanced 15KW load. Each UPS has 4 downstream transformers.

Question: IF i fail source1 on UPSA, STSA will will transfer from source1 to source2. BUT UPSB's inverter will fault on over current. The same thing will happen if i fail the preferred source of UPSB. This problem is also intermittent on both UPSs

There is more info but i would like to see what questions are generated so i will hold off. This is the core problem.

Any ideas
 
Engineering news on Phys.org
jtweedie@atdesk.com said:
Question: IF i fail source1 on UPSA, STSA will will transfer from source1 to source2. BUT UPSB's inverter will fault on over current.
This seems to make no sense. If B will trip on over current, then B is not adequately sized to carry both loads. No switching arrangement will cure that. You must have two UPS systems, each rated to supply A+B loads.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
5K
  • · Replies 5 ·
Replies
5
Views
4K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 1 ·
Replies
1
Views
7K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 33 ·
2
Replies
33
Views
7K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K