Why Does Generator Fault Current Increase When Connected to the Grid?

In summary, the conversation discusses a strange issue regarding short circuit calculations in a generator power plant. When the generator is operating alone, the short circuit fault current is 30kA, but when it is in parallel to the grid, the total fault current is 86.4kA, with 46kA coming from the generator side. The question is how this increased current is possible and if it goes through the generator windings. The equipment being used in the plant is also described. The conversation ends with a discussion about possible explanations for the increased current.
  • #1
ge.vasiliou
9
0
Hi guys,
For one more time I need your opinion in a kind of strange issue, which escapes my understanding.

Performing a single line to ground short circuit calculations (Low Voltage Side) in a simple Generator power plant using a step up to transformer, we can observe the two following facts:

1. For a stand alone generator (not parallel to the grid) single line to ground fault current (low voltage side) equals to 30kA. This value actually represents that behavior of the generator itself.
Gen+Only.jpg


2. If generator works in parallel to the existed grid, results of the short circuit fault current calculation equals to 86,4kA. This total fault current splits to 46kA coming from Generator side, and rest 40,5 kA come from grid side.
Gen+Grid.jpg


The question is:
Since generator as a source is capable to provide 30kA on it's own, how is it possible in a parallel to grid configuration to have 46 kA coming from the generator side?
It seems 16 kA have been added to the generator side. Is this fault current actually going thru generator windings?

PS1 : Please notice that the above results in both cases can be reached either by a simulation software or by hand calculations using symmetrical components analysis.

PS 2: Quick Description of equipment:
Generator is 1,9MVA , cosF 0,8, 400Volts, 50Hz, Star connected, solid grounding, Xd'' = 0,13 p.u and Xo=0,02p.u. Step Up Transformer is 2,5 MVA, 6% impedance, Delta connection at LV Side, Star Connection (solid grounding) at 20kV Side. Grid is 20 kV , 250MVAsc, star – solid ground.
 
Engineering news on Phys.org
  • #2
  • #3
No, we don't mix transient reactances. The currents appear in my sketches are short circuit current (symmetrical rms) during subtransient state of the fault, meaning actually the short circuit current for the first 0.2 - 0.5 seconds (before the whatever protective device operates). For the calculation of short circuit current - subtransient state we need Xd'' of the generator (subtransient reactance). The link you uploaded is nice, i already have this document. Thanks anyway.

I can understand why the fault level is increased when in parallel to grid:
Generator impedance are in parallel to the grid impedance resulting in a total smaller impedance meaning a bigger fault current.

What i don't know is if this extra current of 16kA which seems to come from my Generator side is actually going thru my generator windings.
 
  • #4
i never have done short circuit calculations, so won't pretend to know.

But i look forward to learning from whoever does respond !This is a single phase fault?
What is state of CB1 for your two conditions? Which side of it is the fault on?
Perhaps because of the delta connected transformer the other two phases of generator can contribute current to the faullt through the transformer windings?
In other words, CB1 connects the unfaulted phases to the fault through transformer winding.

that's just a guess.

old jim
 
  • #5
Jim,
Yes it is a single phase fault. CB1 is closed - normal operating conditions - in both sketches. Your guess doesn't apply to the second scenario that current is increased in Generator Side. This increased current is due to the existence of the grid (the only difference between my two schemes).
 

What is the "Generators Calculation Bug"?

The "Generators Calculation Bug" is a software bug that affects the calculations of generators in a system. It may result in incorrect outputs or unexpected behavior.

How does the "Generators Calculation Bug" impact scientific research?

The "Generators Calculation Bug" can significantly impact scientific research by producing inaccurate or unreliable results. This can lead to incorrect conclusions and hinder the progress of scientific understanding.

What causes the "Generators Calculation Bug"?

The "Generators Calculation Bug" can be caused by various factors, such as coding errors, incorrect input parameters, or compatibility issues with other software or hardware components.

How can the "Generators Calculation Bug" be prevented?

The "Generators Calculation Bug" can be prevented by thorough testing and debugging of the code, using standardized coding practices, and regularly updating and maintaining the software.

How can the "Generators Calculation Bug" be fixed?

The "Generators Calculation Bug" can be fixed by identifying the root cause of the bug and implementing a solution, which may involve rewriting code, updating software, or addressing compatibility issues.

Similar threads

Replies
12
Views
7K
Back
Top