Generators Calculation Bug

by ge.vasiliou
Tags: calculation, generators
Share this thread:
ge.vasiliou
#1
Apr9-12, 08:02 AM
P: 9
Hi guys,
For one more time I need your opinion in a kind of strange issue, which escapes my understanding.

Performing a single line to ground short circuit calculations (Low Voltage Side) in a simple Generator power plant using a step up to transformer, we can observe the two following facts:

1. For a stand alone generator (not parallel to the grid) single line to ground fault current (low voltage side) equals to 30kA. This value actually represents that behavior of the generator itself.


2. If generator works in parallel to the existed grid, results of the short circuit fault current calculation equals to 86,4kA. This total fault current splits to 46kA coming from Generator side, and rest 40,5 kA come from grid side.


The question is:
Since generator as a source is capable to provide 30kA on it's own, how is it possible in a parallel to grid configuration to have 46 kA coming from the generator side?
It seems 16 kA have been added to the generator side. Is this fault current actually going thru generator windings?

PS1 : Please notice that the above results in both cases can be reached either by a simulation software or by hand calculations using symmetrical components analysis.

PS 2: Quick Description of equipment:
Generator is 1,9MVA , cosF 0,8, 400Volts, 50Hz, Star connected, solid grounding, Xd'' = 0,13 p.u and Xo=0,02p.u. Step Up Transformer is 2,5 MVA, 6% impedance, Delta connection at LV Side, Star Connection (solid grounding) at 20kV Side. Grid is 20 kV , 250MVAsc, star solid ground.
Phys.Org News Partner Engineering news on Phys.org
Identifying long-distance threats: New 3D technology could improve CCTV images
Intelligent system that predicts when alarms might be triggered could greatly improve the management of industrial plant
3D printed nose wins design award
jim hardy
#2
Apr9-12, 06:44 PM
Sci Advisor
PF Gold
jim hardy's Avatar
P: 3,659
Xd'' = 0,13 p.u
are we perhaps mixing direct, transient and subtransient reactances?

I'm not a relay guy but here's a handy looking article..

http://www.google.com/url?sa=t&rct=j...aWs8d5z2vJKs_Q

it's PDF , if above doesn't work search on "Power topic #6008 | Technical information from Cummins Power Generation"

sorry i dont have an exact answer .

old jim
ge.vasiliou
#3
Apr10-12, 05:10 AM
P: 9
No, we don't mix transient reactances. The currents appear in my sketches are short circuit current (symmetrical rms) during subtransient state of the fault, meaning actually the short circuit current for the first 0.2 - 0.5 seconds (before the whatever protective device operates). For the calculation of short circuit current - subtransient state we need Xd'' of the generator (subtransient reactance). The link you uploaded is nice, i already have this document. Thanks anyway.

I can understand why the fault level is increased when in parallel to grid:
Generator impedance are in parallel to the grid impedance resulting in a total smaller impedance meaning a bigger fault current.

What i don't know is if this extra current of 16kA which seems to come from my Generator side is actually going thru my generator windings.

jim hardy
#4
Apr10-12, 09:33 AM
Sci Advisor
PF Gold
jim hardy's Avatar
P: 3,659
Generators Calculation Bug

i never have done short circuit calculations, so won't pretend to know.

But i look forward to learning from whoever does respond !


This is a single phase fault?
What is state of CB1 for your two conditions? Which side of it is the fault on?
Perhaps because of the delta connected transformer the other two phases of generator can contribute current to the faullt through the transformer windings?
In other words, CB1 connects the unfaulted phases to the fault through transformer winding.

that's just a guess.

old jim
ge.vasiliou
#5
Apr10-12, 10:50 AM
P: 9
Jim,
Yes it is a single phase fault. CB1 is closed - normal operating conditions - in both sketches. Your guess doesn't apply to the second scenario that current is increased in Generator Side. This increased current is due to the existance of the grid (the only difference between my two schemes).


Register to reply

Related Discussions
Finding a set of Generators for a group G when Generators for Kerh, Imh are known; h Linear & Abstract Algebra 1
How *exactly* do you get the generators (1/2,1/2) Quantum Physics 11
Between d.c generators and a.c generators Electrical Engineering 3
Generators of R4 Linear & Abstract Algebra 3
Learning about self-excited and separate shunt generators Electrical Engineering 2