Ground Fault Isolation
We are using 120V commercial grade electronic ballasts, properly grounded, rated at 2Amps to drive two low pressure UV lamps submerged in water rated at 800mA. System requirements are to use GFI barkers with each ballast. This installation in a wastewater treatment plant, where there are motors, pumps and air compressors. GFI’s are randomly tripping at 5mA from ballast electronic current leakage up to 9.2mA. Can we resolve our nuisance GFI tripping by using 120V to 120V isolation transformers between the GFI and electronic ballast?
|
| Jun18-07, 10:27 PM | #2 |
|
|
Well maybe the isolation transformers will help. It depends on what you're trying to achieve. a) you mention the facility has motors, pumps, compressors, etc. and there's some implication that maybe the power line fluctuations / noise from these may be relevant in causing the GFI's to trip. If the GFIs trip because of EMI / noise present on the power line, then they're erroneously tripping due to noise and not a 'real' ground fault. To solve problems relating to power line coupled noise, try installing power line EMI filters and/or filtering surge suppressors and/or filtered or "online" UPS units BEFORE the GFI so that the power supply INTO the GFI is clean and stable and the GFI won't be more likely to trip due to noise present on its INPUT. b) If EMI coupled through induction to the leads on the OUTPUT of the GFI (between the GFI and its load, the ballasts) is causing enough noise so as to contribute strongly to tripping the GFI, then you'll need to minimize the circuit loop inductance and EMI noise coupled from the ballast circuit loop to the GFI's output side. This can be done by using more closely spaced wires, twisted pairs of wires, series ferrite / iron chokes which each of the individual circuit wires is separately wound around, and by installing a series EMI filter (capacitor / inductor) unit just on the outside of the GFI before the leads run out toward the ballast load(s). Using more heavily shielded metallic conduit and boxes can also help somewhat in reducing the amount of induced EMI coupled to the GFI and its associated wiring. c) if you install an isolation transformer after the GFI and before the GFI's load, so that the transformer IS the GFI's only load then you've just created a somewhat distinct partition of your circuitry. Circuit A is between the GFI's output and the isolation transformer. Circuit B is between the isolation transformer and the ballast(s). The GFI will ensure there are no ground faults between it and its load, Circuit A, the isolation transformer. If you draw a significant imbalanced current from either the hot or neutral lines attached to the GFI to ground, the GFI will trip. If the current in the hot and neutral leads of the GFI is balanced (equal within a couple milliamps), the GFI should not trip. By using a transformer between the GFI and the ballast, and by (for the sake of example) locating the isolation transformer right next to the GFI, you're almost ensuring that there WON'T be any ground faults that the GFI will 'see' since unless you do cause a ground fault in the short circuit path between the GFI and the transformer primary circuit, there will be no ground fault for the GFI to detect IN THE CIRCUIT IT IS MONITORING. Now the isolated SECONDARY winding of the isolation transformer is CIRCUIT B and consists of the secondary of the iso xfmr and the ballast(s) which load it. One could create a legitimate ground fault on CIRCUIT B, relative ONLY to the SECONDARY of the ISO XFMR and the GFCI on CIRCUIT A would not detect it since the current in CIRCUIT A is still balanced (through the ISO transformer PRIMARY) and isn't ground-faulting. There could be unbalanced current from the secondary of the ISO XFMR but that's not what the GFCI is attached to and therefore it's not monitored. Certainly in such a case you'd be reducing the nuisance tripping of the GFCI due to a legitimate ground fault in the circuit leading to the ballast(s), but in such cases of a 'true' ground fault imbalance in CIRCUIT B, the GFCI on circuit A is providing no protection / detection. So could it help solve nuisance tripping? YES. Could it help to circumvent the very protection that the GFCI is supposed to provide in the major way it's supposed to work? YES, in that your ultimate circuit would include portions of it that wouldn't be GFCI protected against real ground faults. d) However since isolation transformers usually are somewhat effective line noise filters for some kinds of high frequency spikes, surges, EMI, the mere presence of an isolation transformer in the circuit COULD help reduce EMI related GFCI tripping due to the other motors / compressors / etc. in the vicinity. For maximum EMI / line noise protection, of course you should use an isolation transformer that also incorporates EMI filtration / surge suppression / choke type circuitry. That'd help against nuisance tripping that ISN'T due to a true ground fault. |
| Jun19-07, 05:54 PM | #3 |
|
|
Are you sure that the UV lamps and wiring aren't leaking through the water? I would think this is the most likely reason for seeing a ground fault.
Have you checked with other water treatment facilities to see if they have experienced such problems? And what they have done? If you use an insolation transformer then will your GFIs still be effective? I think not. |
| Thread Closed |
| Thread Tools | |
Similar Threads for: Ground Fault Isolation
|
||||
| Thread | Forum | Replies | ||
| Ground plane isolation question | Electrical Engineering | 4 | ||
| 3 Phase System Line to Ground fault Fault current calculation | Engineering, Comp Sci, & Technology Homework | 1 | ||
| San Andreas Fault | Earth | 5 | ||
| Fox News: 9-11 Kerry's fault. | Current Events | 33 | ||
| Segmentation Fault !!! | Computing & Technology | 5 | ||