How is the 90-degree phase shift achieved in a Var transducer?
  • Thread starter Thread starter kanishke007
    Watt
A Var transducer achieves a 90-degree phase shift necessary for calculating reactive power (Vars) by modifying the physical arrangement of its windings, similar to a Watt transducer. This phase shift is essential for converting real power measurements into reactive power by utilizing the sine of the phase angle. Historically, electromechanical meters used eddy-current motors with specific winding configurations to produce the required torque proportional to the electric fields. Modern devices have transitioned to microprocessors and digital signal processing for improved accuracy, although older mechanical meters were often more reliable in non-linear load scenarios. The discussion highlights the evolution of metering technology and the continued relevance of older methods in certain applications.
kanishke007
A Watt transducer has line to line voltages and line currents as inputs. It calculates the Watts and outputs DC mA. The one i am working on is rated 1mA DC for 500W AC. The relationship is linear.
A Var transducer does exactly the same, but it shifts the input AC by 90degrees to get Vars.
My question is: How do we mechanically/electrically achieve the 90deg ph. shft. in the construction of the Var transducer ?
Volt-ampere reactive (var) is calculated by multiplying the rms values of the potential (volts), current (amps), and the sine of the phase angle between them.
http://en.wikipedia.org/wiki/Volt-amperes_reactive"
You are absolutely right. However, that was not my question.
The Var transducer is the same physical device as the Watt transducer. However, to make the Watt tranducer output Vars, there is a phase shift of 90degs applied to the real power hence making it cos(90-angle)=sin(angle), which gives us Vars. So, my question is, how is this phase shift applied mechanically ? is it something to do with the way the turns are wound on the coil ? or something else perhaps ?
thanks
Well, the transducer measures the phase angle and makes the calculation.
Check out Figure 3 (Application diagram for phase to phase reverse VAR connection) for their Type MWTU 11 Forward and Reverse Power Relay.
"www.electricalmanuals.net/files/RELAYS/ALSTOM/MWTU/R8127B.pdf"[/URL]
Here they use a phase sensitive bridge.
Long ago, electricity power meters (kWh, kVAh and kVArh) operated using eddy-current motors that spun a metal disk. The disk was connected via gears to a series of mechanical dials which could be visually read. The various windings for the eddy-current motors were wound such that the mechanical arrangement produced torque in the disk proportional to the product of the electric fields from the current-windings and the voltage-windings. The phase relationship was alterable during the construction via the relative physical relationship between the windings.
The days it is all done with microprocessor devices & digital signal processing methods. For the most part, this is an improvement, as the old electromechanical instruments would develop inaccuracies as the jewel bearings became worn. However, the older meters were actually more accurate in measuring power in non-linear loads.
Hi MThornton,
I bet they are still used a lot. In the '80s when I was involved with watt/var metering, these mechanical meters were used in tie-line substations (metering between two areas/companies) to account for MegaWattHours being sold and bought. The disk had a pattern of holes that allowed light to be detected, creating pulses; each representing 1 MWH.
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...