Can Westinghouse 3-loop PWRs Survive a Total Blackout?

  • Thread starter Thread starter rmattila
  • Start date Start date
Click For Summary

Discussion Overview

The discussion centers on the survivability of Westinghouse 3-loop pressurized water reactors (PWRs) during a total blackout, particularly in the context of the North Anna incident. Participants explore the water volume of the secondary side of steam generators and the implications for maintaining operations without external power.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • Some participants inquire about the water volume of the secondary side of Westinghouse 3-loop PWR steam generators to estimate blackout survivability.
  • There is a mention of the North Anna incident, where the plant lost off-site power and both units shut down, prompting interest in how long the plants could survive by boiling off water from the steam generators.
  • One participant notes that PWR steam generators can boil dry in minutes if feedwater flow is lost, emphasizing the urgency of the situation during a blackout.
  • Another participant suggests that if the steam generators are similar to those at Ringhals 4, the secondary side inventory could provide sufficient water for approximately 1.5 hours after a scram, contingent on the accuracy of their figures.
  • It is mentioned that North Anna has a steam-powered pump and a station blackout diesel, which may mitigate the risks associated with a total electrical power failure.

Areas of Agreement / Disagreement

Participants express varying levels of concern regarding the survivability of the reactors during a blackout, with some suggesting that auxiliary systems may alleviate potential issues, while others focus on the critical nature of feedwater flow loss. No consensus is reached on the exact implications or effectiveness of the auxiliary systems.

Contextual Notes

Participants rely on specific figures and assumptions regarding water volumes and operational capabilities, which may vary based on reactor design and conditions. The discussion does not resolve the uncertainties surrounding the exact survivability duration during a blackout.

rmattila
Messages
244
Reaction score
1
Would anybody happen to have at hand the water volume of the secondary side of Westinghouse 3 loop PWR steam generators?

Regarding the loss of external grid incident at North Anna, it would be nice to have a rough estimate of how long the plants could survive a total blackout by boiling off water from the SG:s.
 
Engineering news on Phys.org
rmattila said:
Would anybody happen to have at hand the water volume of the secondary side of Westinghouse 3 loop PWR steam generators?

Regarding the loss of external grid incident at North Anna, it would be nice to have a rough estimate of how long the plants could survive a total blackout by boiling off water from the SG:s.
Earthquake was about 8-9 miles from the plant, although some info indicates 1 mile. They lost off-site power and the EDGs started up. Both units shutdown.

I'm sure they'll have an interesting Event Report out soon.
 
rmattila said:
Would anybody happen to have at hand the water volume of the secondary side of Westinghouse 3 loop PWR steam generators?

Regarding the loss of external grid incident at North Anna, it would be nice to have a rough estimate of how long the plants could survive a total blackout by boiling off water from the SG:s.

With a loss of feedwater flow, PWR steam generators boil dry in minutes.

North Anna has a terry turbine (steam-powered pump) to provide feedwater flow in the case of loss of total electrical power failure, as well as a station blackout diesel (in addition to the regular backup diesels).
 
If the steam generators are similar to Ringhals 4, which is a 935 MWe Westinghouse 3-loop PWR, their secondary side inventory would appear to be some 40 m3 or 30 t per SG, which would 1 hour after scram be enough for approximately 1.5 h, if I got the figures correct.

However, the existence of a steam driven auxiliary pump and an SBO diesel make the situation appear quite non-problematic.
 
Last edited: