What Is the Coefficient of Performance of a Carnot Air Conditioner?

Click For Summary

Homework Help Overview

The discussion revolves around calculating the coefficient of performance (COP) of a Carnot air conditioner, given the temperatures of the hot and cold reservoirs. The original poster expresses confusion regarding the relationship between the COP and the variables involved, specifically noting the lack of certain values needed for calculation.

Discussion Character

  • Conceptual clarification, Mathematical reasoning, Assumption checking

Approaches and Questions Raised

  • The original poster attempts to use the relationship Qc/W but struggles with having two unknowns. They question what they might be overlooking in their approach. Another participant suggests a formula for COP based on temperatures, prompting further inquiry about its derivation.

Discussion Status

The discussion is ongoing, with participants exploring different equations for COP and questioning their sources. There is no explicit consensus on the correct approach, but some guidance has been offered regarding the ideal Carnot cycle.

Contextual Notes

Participants note discrepancies between their textbooks and the equations being discussed, indicating potential confusion about the definitions and relationships involved in the problem.

BlackMamba
Messages
187
Reaction score
0
Hi there,

I have what should be a simple problem, but it's driving me insane.

Here's the problem: A Carnot air conditioner maintains the temperature in a house at 290 K on a day when the temperature outside is 315 K. What is the coefficient of performance of the air conditioner?

So I know to find the coefficient it would be Qc/W. I have neither of those numbers in the problem. I do have Th and Tc and even if I do substitutions I will ALWAYS have two unknowns. At least the way I am attempting this.

My thinking was originally that I could substitute for Qc, since Oc = W + Qh but I still have two unknown variables... What am I forgetting??

Any help will be greatly appreciated.
 
Physics news on Phys.org
BlackMamba said:
Here's the problem: A Carnot air conditioner maintains the temperature in a house at 290 K on a day when the temperature outside is 315 K. What is the coefficient of performance of the air conditioner?
They expect you to determine the coefficient of performance of an ideal Carnot cycle using:

[tex]COP = \frac{T_C}{T_H-T_C}[/tex]

AM
 
Thanks for replying but how did you come to that point? In my book the equation for the coefficient of performance is Qc/W. No where in my book is your equation listed.

Thanks for your help.
 
BlackMamba said:
Thanks for replying but how did you come to that point? In my book the equation for the coefficient of performance is Qc/W. No where in my book is your equation listed.

Thanks for your help.
For the refrigerator,
[tex]Q_H = \Delta W + Q_C[/tex]
This means that the heat flowing out of the cold reservoir + work added is equal to the heat flowing into the hot reservoir.

For the reversible (ideal) Carnot cycle, [tex]\Delta S = 0[/tex] where S = Q/T
So:
[tex]Q_H/T_H - Q_C/T_C = 0[/tex]

Combining these two equations:
[tex]Q_H = Q_C(T_H/T_C) = \Delta W + Q_C[/tex]
[tex]T_H/T_C = \Delta W/Q_C + 1[/tex]
[tex]Q_C/\Delta W = 1/(T_H/T_C - 1)[/tex]

Which simply reduces to:
[tex]Q_C/\Delta W = T_C/(T_H-T_C)[/tex]

AM
 
Last edited:

Similar threads

  • · Replies 3 ·
Replies
3
Views
5K
Replies
14
Views
3K
  • · Replies 2 ·
Replies
2
Views
3K
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 4 ·
Replies
4
Views
8K
Replies
1
Views
2K
Replies
3
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K