    House load operation steam turbine

    immediately generator load will come to house load of say 20-30 MW from 600 MW. Turbine tends to over speed ( around 106% for 2-3 seconds thereafter 102% for around 2-3 minutes) & boiler goes on run back ( say 50% within a minute or twoo)...thereafter load further reduces in controlled manner to...
  2. A

    House load operation steam turbine

    1. Have the machine supplied by major manufacturers in the world like Siemens, MHI, Alstom, GE, Skoda, Toshiba have House load capability? Reply: yes major turbine manufacturers (OEM) machine have capability to run under house load, however each OEM specifies their maximum limitation of time to...