Recent content by abhiks4u
-
A
House load operation steam turbine
immediately generator load will come to house load of say 20-30 MW from 600 MW. Turbine tends to over speed ( around 106% for 2-3 seconds thereafter 102% for around 2-3 minutes) & boiler goes on run back ( say 50% within a minute or twoo)...thereafter load further reduces in controlled manner to...- abhiks4u
- Post #14
- Forum: Mechanical Engineering
-
A
House load operation steam turbine
1. Have the machine supplied by major manufacturers in the world like Siemens, MHI, Alstom, GE, Skoda, Toshiba have House load capability? Reply: yes major turbine manufacturers (OEM) machine have capability to run under house load, however each OEM specifies their maximum limitation of time to...- abhiks4u
- Post #11
- Forum: Mechanical Engineering