THERMO Spoken Here! ~ J. Pohl ©
TOC ~ 244

Instant Hot Water

Sketch of an electric demand water heater: supply water at 15°C enters a heater with an electrical supply and temperature control, and leaves through a shower head at 3.5 GPM and 44°C.

The sketch shows a wall-mounted, electric-powered water heater that operated "on demand." There is no hot water tank. When the temperature control is switched, the device delivers water as shown in the promotional sketch.

Calculate the least electrical power required?
♦  We exclude the electrical resistance coils from the system. From that perspective, this is a "heat interaction" device. Rate wise changes of kinetic and potential energy are small in comparison to the heating power. (The flow can be approximated and the smallness of these changes confirmed). The device comes to steady operation promptly. We take the system to be the water.

Of the system equations, the energy equation is the longest. It is a check-list of energy changes and causes. So we write it and put the "X"" over what is zero and the "/" through what is assumed small and is being neglected. For this consideration, the energy equation reduces as follows:

Equation (1): d/dt Σ[U + (KE + PE)_c.m.]_sys (struck out) = −d/dt ∫p_B dV (struck out) + ṁ_in (h + ke + pe)_in − ṁ_out (h + ke + pe)_out (ke and pe struck out) + ΣẆ_shaft (struck out) + Ẇ_friction − ΣẆ_ext (struck out) + ΣQ̇
(1) 1

The energy equation reduces to a single stream flow with heat.

Equation (2): 0 = ṁ_in (h_in − h_out) + Q̇
(2) 2

The mass rate of flow can be represented as a density time a volume rate.

Equation (3): 0 = ρV̇ [c (T_in − T_out)] + Q̇
(3) 3

Now the numbers are entered and care is taken to assure units are correct.

Equation (4): 0 = 1000 (kg/m³)(3.5 gal/min / 60 s/min)(ft³/7.5 gal)(m/3.28 ft)³[(4.2 kJ/kg)(15 − 44)°C] + Q̇
(4) 4

We avoided algebra as always. The reduced equation, then our result are:

Equation (5): 0 = −26.8 kJ/s + Q̇, or Q̇ = 26.8 kW
(5) 5

The above calculation did not determine the electric power required of the heating device. The heat rate calculated is the energy required by the flow of 2.5 gall/min of water to change from 15°C to 44°C. A different (and important) system must be analyzed to determine the electric power requirements and the design aspects by which that electric power becomes the above "heat rate" to the water.