Finding enthalpy for refrigerant-134a off the saturation curve

3 replies · 2K views · last reply
yecko
Gold Member
Messages
275
Reaction score
15
Homework Statement
How to get h2?
(see pic)
Relevant Equations
isentropic
dH = dQ + Vdp = Tds + Vdp
H = U + pV
Handwritten-style T-s diagram of a vapor-compression refrigeration cycle with pressure levels 0.8 MPa and 0.14 MPa, states 1 through 4 and 4s, and labels for heat in, heat out and work in.


h and s can be obtained from "Saturated refrigerant-134a—Pressure table"

however, how to get h2? it is not on the curve, and neither p or dV is given in the question. Thank you
 
Ity says P 0.8 MPa on the curve ! You have s,p and can look up T in table A-13
 
Table of superheated refrigerant-134a properties (Table A-13, concluded) listing temperature, specific volume, internal energy, enthalpy and entropy at 0.50, 0.60, 0.70, 0.80, 0.90 and 1.00 MPa; the 0.80 MPa rows at 50 and 60 °C are highlighted.


This is table A13, which at P=0.8MPa, s=0.94456, h should be somewhere between 286.71 and 296.82.
However, from the solution, h= 275.39kJ, am I looking at the table in a correct way?
 
Yes you are. Turns out the phys props have changed slightly.
I have an older edition (2002) of cengel and there it matches better.
40273.660.9374
50284.390.9711

https://www.egr.msu.edu/classes/me417/somerton/R134a Tables.pdf

I googled "and operates on an ideal vapor-compression refrigeration cyle between 0.14 and 0.8 MPa" and did indeed find other results too.
 
Last edited:
  • Like
Likes   Reactions: yecko