Causes of Transformer Explosion in 152 Hectares University Campus

Click For Summary

Discussion Overview

The discussion revolves around the causes of transformer explosions experienced at a university campus, focusing on both primary and secondary side factors. Participants explore various potential causes, including operational conditions, equipment age, and external influences.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant inquires about causes of transformer explosions beyond overloading, specifically looking for factors related to the primary side.
  • Another participant discusses the degradation of insulation and oil fill over time, suggesting that leakage currents can lead to short circuits and explosions if not properly managed.
  • A different contributor emphasizes the importance of monitoring oil conditions and suggests checking the neutral current on the WYE side, noting the potential impact of third harmonic currents on transformer overload.
  • Concerns are raised about changes in load characteristics, the age of the transformers, and environmental factors such as lightning strikes, which could contribute to the failures.
  • One participant mentions that high harmonic content could also be a factor, particularly in relation to nearby industrial operations like arc furnaces.

Areas of Agreement / Disagreement

Participants express multiple competing views regarding the causes of the transformer explosions, with no consensus reached on a singular cause. Various factors are proposed, but the discussion remains unresolved.

Contextual Notes

Participants highlight the need for further investigation into the transformers' age, load changes, and environmental conditions, indicating that these factors may influence the reliability and safety of the equipment.

Who May Find This Useful

Electrical engineers, maintenance personnel, and safety professionals involved in transformer operation and maintenance may find this discussion relevant.

young e.
Messages
64
Reaction score
0
hi pf folks..

currently i am the electrical engineer incharge in a 152 hectares university campus in our place. commonly our transformer are rated 7620/240 volts, 1p with capacity of 25 KVA, 50 KVA and 100 KVA.. for our three phase loads we used to bank 3- 1p transformer
wye delta...all in all we have a total of 8 transformer substation in our campus.. now few months past we experienced succesive transformer explosion in our campus in different substations, we check the secondary line there's no fault in it,,, being a neophyte in this field of practice (electrical engg.) now my question is:

1. aside from overloading, what are the other causes of transformer explosions?

2. i suspect that the succesive explosion came from the primary side since we had already made an investigation in all of our loads and secondary lines, and we found that everything is all right, now what are the factors affecting transformer explosion with regards to the primary side..

tnx in advance!

:smile: young engineer
 
Engineering news on Phys.org
Just some background information since it's not my speciality.
There is always some leakage current between the winding layers. Over time, and especially with high internal temperature, both the insulation and oil fill degrade and become slightly conductive. This of course increases the leakage currents a little. Eventually the insulation becomes carbonized and rather conductive, then you are on the way to a run-away short circuit and explosion if there ar not any fuses in the primary circuit.

To monitor the internal conditions, a chemical analysis of the oil is periodically done to check for breakdown by-products.

Others here, perhaps @jim hardy or @anorlunda, may have more details.

Cheers,
Tom
 
  • Like
Likes   Reactions: Asymptotic
Monitoring oil is a must.

Are primaries 4 wire connected? In other words, is there a neutral wire?
If so,
Measure the neutral current on WYE side.

Why do i say that ?
It is possible to overload a (4 wire WYE)-DELTA connected transformer with third harmonic current by powering it from a much larger source that has just a few % third harmonic content in its voltage .

Look up "Zero Sequence Current".

old jim
 
  • Like
Likes   Reactions: Asymptotic
Given that they have been providing trouble-free service until just recently.

1. Has the nature of their loads changed?
Has anything unusual (an earthquake, etc.) happened?

2. How old are the transformers?
Date of manufacture will be on their nameplates. If they were all installed at about the same time, and are closing in on expected service life that could explain the rash of failures.

3. Is your area particularly prone to lightning strikes?
Metal oxide, and/or spark gap arresters are popular for transformer/switchgear protection. MO arresters can fail shorted (which is hard to ignore - loud explosion, and likely to take out the primary fuse), but they may also fail open, which isn't easily detectable (special tests are required), and afterward, provides no lightning and surge protection.

A good course of action is look into transformer and switchgear testing services in your area, and have a reputable firm assess your equipment.
 
Others mentioned oil. That is the first place to look.

High harmonic content can also cause transformer explosions. Especially if you had several in the same area during the same period, I would check harmonics.

An arc furnace in a steel recycling plant can be a big source of harmonics.
 
  • Like
Likes   Reactions: jim hardy

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
Replies
1
Views
2K
  • · Replies 10 ·
Replies
10
Views
5K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 16 ·
Replies
16
Views
4K
  • · Replies 17 ·
Replies
17
Views
13K
  • · Replies 12 ·
Replies
12
Views
2K
  • · Replies 12 ·
Replies
12
Views
12K
  • · Replies 10 ·
Replies
10
Views
3K
Replies
9
Views
4K