why do we use the 3phase and not the 4phase or other phase supply?
please answer...
please answer...
Last edited by a moderator:
PhanthomJay said:do you mean 3 phase instead of 4 wire systems, or do you mean 3 phase instead of more than 3 live wires ? If the first, no need for the neutral if load is balanced amongst the live phase conductors as in AC transmission, although 4 wire is common at the lower distribution voltages main lines that directly supply customers. Three phase has become the norm for AC transmission, due primarily to economics. And Tesla. Some research was done awhile ago on 6 phase systems during the EMF issues of health concerns, but nothing was ever implemented of significance.
PhanthomJay said:In a three phase AC system, the voltages between wires are time wise 120 degrees apart , and same with the current. With some vector algebra, the power delivered can be shown to be equal to (root 3)(V)(I) , where V is the voltage difference between any 2 phase conductors. For a 115 kV phase -to - phase 3 phase line, carrying 1000 amps in each conductor, this is about 200 MW of power assuming unity power factor and no line losses. Now with a single phase line (2 wire system with neutral return), you only get 115 MW out of it for the same current...it's economics...and other factors already mentioned.