Jun16-12, 04:18 AM   #1
 

megger test


hi, in megger test of transformers which terminals we have to earth and why? How this test is used to check insulation?
 
PhysOrg.com
PhysOrg
engineering news on PhysOrg.com

>> Company pioneering new types of material for 3-D printer 'ink'
>> Student-built innovations to help improve and save lives
>> Researchers use light projector and single-pixel detectors to create 3-D images
Jun16-12, 04:49 AM   #2
 
Recognitions:
Science Advisor Science Advisor
Megger tests on transformers are to test the insulation of the transformer.

So you would measure between windings, and between windings and the metal core of the transformer.

Be aware that on large transformers these areas can have substantial capacitance and they can hold a possibly lethal charge for days after the test. So, it is important to discharge this capacitance by the use of a shorting bar.
 
Jun18-12, 11:17 AM   #3
 
Quote by vk6kro View Post
Megger tests on transformers are to test the insulation of the transformer.

So you would measure between windings, and between windings and the metal core of the transformer.

Be aware that on large transformers these areas can have substantial capacitance and they can hold a possibly lethal charge for days after the test. So, it is important to discharge this capacitance by the use of a shorting bar.
thnx for the reply but i want to know the exact process to check the insulation and the theory behind it?.....plz help
 
Jun18-12, 08:08 PM   #4
 
Recognitions:
Science Advisor Science Advisor

megger test


A transformer should not conduct at all between windings or from any winding to ground.

So, depending on the type on Megger, you attach the Megger to the windings you want to test the insulation between and then push a button to produce a high voltage.

If the insulation is OK then the meter will indicate that there is no conduction or that there is infinite resistance between the windings.

You release the button and wait for the voltage to be dissipated or you may have to short out the leads to make the transformer safe.

Never touch both leads of a Megger at the same time, even if you believe it is safe. They can deliver a vicious shock.

I have used hand-held meggers and they are mostly simple to use. Really old ones used to have a handle which you had to wind to get a high voltage. More recent ones just have a DC-DC converter in them which generates the high voltage.

Mostly, you get a choice of voltage to test with. This voltage might be 500 V, 1000 V or 2000 V.
It is possible to do damage with this feature if you select too high a voltage when testing components that are not rated for such a high voltage, but for testing transformers you could test on 1000 volts safely.
 
Jun19-12, 11:11 PM   #5
 
Quote by vk6kro View Post
A transformer should not conduct at all between windings or from any winding to ground.

So, depending on the type on Megger, you attach the Megger to the windings you want to test the insulation between and then push a button to produce a high voltage.

If the insulation is OK then the meter will indicate that there is no conduction or that there is infinite resistance between the windings.

You release the button and wait for the voltage to be dissipated or you may have to short out the leads to make the transformer safe.

Never touch both leads of a Megger at the same time, even if you believe it is safe. They can deliver a vicious shock.

I have used hand-held meggers and they are mostly simple to use. Really old ones used to have a handle which you had to wind to get a high voltage. More recent ones just have a DC-DC converter in them which generates the high voltage.

Mostly, you get a choice of voltage to test with. This voltage might be 500 V, 1000 V or 2000 V.
It is possible to do damage with this feature if you select too high a voltage when testing components that are not rated for such a high voltage, but for testing transformers you could test on 1000 volts safely.
thank u very much for ur xplanation.....i have only one doubt tht is which part of the transformer has to be grounded while performin the test and y?
 
Jun20-12, 05:13 AM   #6
 
Recognitions:
Science Advisor Science Advisor
You may have misunderstood this.

The frame of most transformers is grounded in normal use, so testing the transformer windings for leakage to frame involves grounding one side of the Megger.
 
Jun22-12, 03:05 AM   #7
 
Quote by vk6kro View Post
You may have misunderstood this.

The frame of most transformers is grounded in normal use, so testing the transformer windings for leakage to frame involves grounding one side of the Megger.
ok i got it thank u very much i truly appreciate ur help
 
New Reply
Thread Tools


Similar Threads for: megger test
Thread Forum Replies
Problem 51 from (GRE) math subject test: practice test book Calculus & Beyond Homework 10
A limsup inequality (showing that the root test is stronger than the ratio test) Calculus & Beyond Homework 0
Integral test, basic comparsion test, limit comparsion test Calculus & Beyond Homework 11
A primality test for Fermat numbers faster than Pépin's test ? Linear & Abstract Algebra 2