How does high voltage decrease energy loss in a wire
The discussion revolves around the relationship between voltage, current, and resistance in electrical systems, particularly focusing on how increasing voltage can lead to reduced energy loss in wires. Participants explore theoretical implications, practical examples, and the nuances of voltage drop versus supplied voltage.
  • Some participants assert that raising voltage allows for a reduction in current to maintain the same power, thereby decreasing power loss due to the I²R effect.
  • Others clarify that the resistance in a wire is generally fixed unless additional wire is purchased, and that the voltage drop along the wire is distinct from the voltage supplied to the system.
  • A participant provides a practical example involving power loss calculations at different voltage levels, illustrating how higher voltage results in lower current and reduced energy loss.
  • There is a discussion about the distinction between voltage drop and the voltage supplied, with some participants questioning the application of Ohm's law in different contexts.
  • One participant emphasizes that while the voltage drop across a wire is indeed IR, the supplied voltage can be independent of the drop, affecting power delivery.
Participants express differing views on the implications of voltage, current, and resistance, particularly regarding the definitions and roles of voltage drop versus supplied voltage. The discussion remains unresolved with multiple competing perspectives on these concepts.
Participants note the importance of context when discussing voltage and resistance, highlighting that different equations apply to different scenarios, and that assumptions about resistance being constant may not hold in all cases.
This discussion may be of interest to individuals studying electrical engineering, physics, or anyone involved in practical applications of electrical systems, particularly those concerned with energy efficiency and power loss in wiring.
DeepSeeded
If you raise the voltage you must raise either the current or the resistance since V = IR.
So how does a wire with higher voltage and lower current have less resistance?
It should have more resistance to make up for the lower current.
If you raise the voltage you can reduce the current to give the same power since P=IV
Higher voltage and lower current is less power lost to I2R
If you lower the Resistance the voltage will go DOWN, not up, the R in your equation is only a component of V, not of the current.
The R is generally fixed - unless you want to buy more wire.
The V in your equation is the voltage DROP along the wire, the V in my equation is the voltage on the wire (ie relative to ground)
Everybody must have reached the same page in the book because this is coming up a lot
https://www.physicsforums.com/showthread.php?t=287174
Ok so let's assume that R is a constant and make it 1. Now we have Power = IV and V = I, so power = II and we can increase I or I, what's the difference?
Be careful about which V, there is V=the voltage you are running the system at, and V = the voltage drop along the wire.
eg. Suppose you need to supply 1MW (enough for a city block) and have a 1 ohm wire.
At V=4Kv (a typical trash can size pole transformer) current from I=P/V = 250A
Vdrop= I R = 250V so you get 3.75Kv out at the other end and waste I2R = 62KW as heat.
At V=25Kv (typical sub station) I = 1,000,000/25,000 = 40A, so you only lose V=IR=40volts, and only 1.6KW is wasted (about a tea-kettle)
At 1MV only 1Watt would be wasted - however running million volt cables is difficult since they have to be kept a long way from the ground to prevent arcing and the switching gear is expensive.
So Vdrop = IR, not V = IR?
Otherwise they couldn't increase V to 1MV without increasing I
Correct, the voltage in a wire you can make as anything you like using transformers (and so change the current) the voltage drop along the wire is what causes the problems, this depends only on the current and resistance.
So the Voltage in a wire between two specified points is not IR? I seem to remember this being the case in an LRC circuit when taking the integral over the closed loop.
Just to make sure it is said succinctly: P=IV describes the power lost by a resistive load, with V being the drop across the load. The voltage of power lines is not a voltage drop, it is a voltage supplied. It isn't where the loss comes from. Different equations for different situations.
Yes the voltage difference between two points on a wire is IR, but it doesn't matter what the voltage is (above ground). If you put one amp through a one ohm wire with one end at 1V then the voltage drop is 1V and the other end is at zero. If you put one end of the wire at 1000V there is the same 1V drop and the other end is at 999V.
But the power you can deliver down the wire is the voltage above ground (ie the 1000V) times the current. And you want to maximize power while minimizing current.
Ok, got it thanks.
  • · Replies 19 ·
  • · Replies 57 ·
15K
9K
  • · Replies 22 ·