Power network short circuit current calc
This discussion centers on calculating short circuit currents in a power network involving two parallel generators and delta-wye transformers. The user modeled a fault scenario using power network software and sought to verify results through manual calculations. Key insights reveal that many textbooks ignore source and line impedance on the 33kV side, attributing fault current limitations solely to the 33kV/690V transformer and bus bar impedances. The user references IEC60909, which incorporates source impedance in short circuit calculations, prompting questions about impedance visibility from the 690V side.
  • Understanding of power network configurations, specifically delta-wye transformer setups.
  • Familiarity with short circuit current calculations and asymmetrical fault analysis.
  • Knowledge of IEC60909 standards for short circuit calculations.
  • Experience with power network simulation software for modeling fault conditions.
  • Study the principles of short circuit analysis as outlined in IEC60909.
  • Learn about the impact of source impedance on fault current calculations.
  • Explore advanced power network simulation tools for accurate modeling.
  • Investigate the differences between symmetrical and asymmetrical fault current calculations.
Electrical engineers, power system analysts, and professionals involved in power protection and fault analysis will benefit from this discussion.
lavalin
I have a power network, two parallel generators which feed 2 parallel delta-wye transformers with a bus tie inbetween, from 690V to 33kV. These two transformers feed a bus which a whole bunch of 33kV/690V DELTA-WYE transformers hang off for distribution.
There was a fault the other day at the bus which is fed from one of these 33kV/690V step down transformers which I modeled in some power network software to determine the peak value of asymmetrical fault current.
I decided to try and compute it by hand (something I have not done in a very long time) just to confirm the result of the simulation. I looked at some textbooks and I noticed all of them ignore source and line impedance (33kV side) before the 33kV/690V distribution transformer and state the current is limitted purely by the 33kV/690V impedance + the bus bar (which it feeds) impedance.
I am no specialist in power protection but I have my own theories why the source impedance can be ignored. Can anyone shed some light on why the textbooks do it?
I also found IEC60909 which does not neglect source impedance when performing a short circuit calc. It is quite confusing as to the way they do it. They seem to reference the impedance on the 33kV side of the transformer to 690V. Can anyone explain how the impedance on the 33kV side is seen from the 690V side?
Solved it, thanks.