Force on conductors during a short circuit fault

In summary, a short circuit fault occurs when a conductor or part of a circuit comes into contact with another conductor, creating a low resistance path for current flow. This results in a large amount of current flowing through the conductors, causing them to experience a significant force. The magnitude of this force is determined by the amount of current, the length of the conductors, and the distance between them. If the force is too great, it can lead to damage or destruction of the conductors, as well as potential hazards such as fires or explosions. Therefore, it is important to properly design and protect electrical systems to prevent short circuit faults and minimize the force on conductors.
  • #1
Ntip
53
5
TL;DR Summary
How do I relate fault current to the force on two conductors?
If I have two parallel bars serving as a DC bus with a capacitor across the output and there is a short fault event, I know the peak current is limited by V/X. The instantaneous current would be a function of the time RLC time constant. How do I relate this to the force on the conductors due to this transient?
 
Engineering news on Phys.org
  • #2
Welcome to PF.

Where is the short fault ? At the capacitor, somewhere along the transmission line, or at the generator.
The current will be limited by fault protection.
The peak force will occur at peak current.
 
  • #3
If the fault was at the capacitor, I would expect that to produce the highest current since the resistance and inductance is minimized. If it occurred at the generator I would expect di/dt to be the minimum since the inductance would be highest. The peak would also be the lowest since the resistance would be the highest. Is this line of thinking correct?

I'm interested in knowing how to calculate the peak force but I'm not sure how to do this.

Regardless of if the peak is limited by resistance or protection I'm still interested in knowing how it varies with time time in general. I know this isn't realistic for an actual design, but I'm just trying to understand it right now. If there is no protection, my thought is that the current should look sinusoidal. It would increase as a sinusoid with a resonant frequency of f=1/(2pi*sqrt(LC)). The peak would be limited by I=V/R.

The current would initially be DC. As the short happens the current increases so there is a time varying current. That would also induce a time varying magnetic field so I figured I could use maxwells equations but I'm not sure how or if that is even correct. Am I on the right path here or is there something else that I'm not considering? Again, I'm not really considered with the generator in this case. I'm only trying to get the theory where the capacitor is across the bus and the bus is shorted at any point along the bus.
 
  • #4
Short circuit calculations can be simple or very complicated. There are software packages for the complicated ones.

I searched "short circuit calculation" and I found a wealth of sources, and tutorials for both simple and complicated cases. One of them said this:

https://electrical-engineering-portal.com/short-circuit-calculations
When a fault occurs, capacitor…
A capacitor in an AC system charges and discharges in a controlled manner every half cycle, based on the sinusoidal driving voltage and system impedances. When a fault occurs, the system voltage is suddenly changed and the capacitor discharges at a rapid rate, with a high discharge current. The current is greatest if the fault occurs when the capacitor is charged to the maximum at a voltage peak. Only the impedance between the capacitor and the fault limits the discharge current.

The current will “ring down” based on circuit resistance and reactance. The resistance provides damping and the interaction between the system reactance and capacitor determines the frequency of the oscillating current.
 
  • #5
anorlunda,

Thanks for the link. That's good to see my It would work pretty much as described. I've found stuff on how to calculate the short circuit current, but not so much the force generated during the short circuit event. Software is one way to calculate the force.

The Lorentz force seems like it may be helpful here since that's what I would use to show wires attracting or repelling. Since the magnetic field is time varying I'm not sure if I also need one or more of maxwells equations. It is a DC bus so there would be some e-field between conductors. That would also fit in with maxwells equations.

Basically, everything seems coupled and I'm trying to figure out how to tackle this.
 
  • #6
Just as a worst case first approximation:

Since any inductance will slow the discharge, and hence the peak current, try calculating the Lorentz force using the peak current accounting for only the resistance of the busbars and the ESR (Equivalent Series Resistance) of the capacitor.

If the assembly withstands that, you have a starting point to decide on a safety factor you are comfortable with. Since this seems to be a pulse operation, include the possibility of mechanical fatigue in the mounting.

Cheers,
Tom
 
  • #7
If the short circuit is between the conductors then the currents will flow in opposite directions so the conductors will be pushed apart. The DC situation is the simple computation case. Obviously, the direction of the force is the same with AC, although it is then pulsed.

There is another thread on this subject;
https://www.physicsforums.com/threa...ce-from-fault-current-on-overhead-wire.895215

Code for the computation on transmission lines is here.
https://github.com/powerdistributio...blob/master/calculators/conductor_slapping.md
 
Last edited:
  • #8
Tom.G said:
Just as a worst case first approximation:

Since any inductance will slow the discharge, and hence the peak current, try calculating the Lorentz force using the peak current accounting for only the resistance of the busbars and the ESR (Equivalent Series Resistance) of the capacitor.

A larger inductance will slow the discharge but what if the protection never enabled for some reason and the current was able to reach the peak just in a longer time compared to a much smaller inductance. Since the peak is still relatively the same would the peak force be the same? If it's dependent on di/dt then it should be higher right? That's part of why I'm trying to determine how to build in the time varying portion of this.

To calculate the Lorentz force, F=q(E + v x B), I need the B field. I'm not sure which one of maxwells equations to use to get that. Is E the E-field between the conductors during normal operation found by E=V/d? Charge q would be the electron charge so is v then the peak current? I kind of doubt but that's where I'm lost and why I have these questions. Thanks for your help.
 
  • #9
Baluncore said:
If the short circuit is between the conductors then the currents will flow in opposite directions so the conductors will be pushed apart. The DC situation is the simple computation case. Obviously, the direction of the force is the same with AC, although it is then pulsed.

Thanks for that reference. I'll read it and see if I can relate it here.

If the fault is not cleared, shouldn't the DC fault be the same as an AC fault in this case? You would basically have an LC tank so there would be some resonant frequency with some damping due to the bus and ESR of the caps. I figured the current would then continue to ring down at the resonant frequency until the fault was cleared, something burnt up, or all energy was dissipated.

I'm still not sure what equations to use here to even calculate the peak force in this case. As I mentioned above, to do F=q(E + v x B) don't I need to find the Bfield from one of maxwell's equations? And what E and v do I use? This is a new area to me but I just sort of remember these equations from physics classes a long time ago.
 
  • #10
Ntip said:
A larger inductance will slow the discharge but what if the protection never enabled for some reason and the current was able to reach the peak just in a longer time compared to a much smaller inductance.
With inductance included, the peak will be smaller than for the purely resistive case because the capacitor will be partly discharged while rising to the peak.

Try these videos:




(above found with:
https://www.google.comsearch?&q=magnetic+force+between+two+parallel+conductors)
 

1. What is a short circuit fault?

A short circuit fault is a type of electrical fault that occurs when there is a low resistance connection between two conductors in an electrical circuit. This results in a sudden surge of electrical current, which can cause damage to the circuit and potentially lead to a fire.

2. How does a short circuit fault affect conductors?

A short circuit fault can cause a significant increase in the amount of current flowing through the conductors. This increase in current can generate a large amount of heat, which can damage the conductors and potentially cause them to melt or catch fire.

3. What factors can contribute to a short circuit fault?

There are several factors that can contribute to a short circuit fault, including faulty wiring, damaged insulation, overloaded circuits, and faulty electrical equipment. It is important to regularly inspect and maintain electrical systems to prevent these issues from occurring.

4. How does the force on conductors change during a short circuit fault?

During a short circuit fault, the force on conductors increases due to the sudden surge of electrical current. This force is caused by the magnetic field that is generated by the current and can be strong enough to physically move the conductors or cause them to vibrate.

5. How can short circuit faults be prevented?

Short circuit faults can be prevented by ensuring that electrical systems are properly designed and installed, using high-quality materials and equipment, and regularly inspecting and maintaining the system. It is also important to follow safety protocols and avoid overloading circuits to reduce the risk of short circuit faults.

Similar threads

  • Electrical Engineering
Replies
15
Views
1K
  • Electrical Engineering
Replies
8
Views
1K
  • Electrical Engineering
Replies
4
Views
3K
  • Electrical Engineering
Replies
17
Views
2K
Replies
27
Views
458
  • Electrical Engineering
2
Replies
38
Views
5K
Replies
4
Views
6K
Replies
6
Views
3K
Replies
10
Views
1K
Replies
20
Views
2K
Back
Top