Harmonics in power calculations
This discussion focuses on interpreting data from a 3-phase electronic meter, specifically regarding power calculations involving harmonics. The user, Sparky, successfully calculated watts, VA, and VAR from loaded conditions but encountered discrepancies in no-load conditions. The significant increase in harmonics VA and harmonic power factor (pf) during no-load conditions suggests that these harmonic values are crucial for accurate power calculations. The conversation highlights the importance of understanding harmonic contributions in power quality assessments.
  • Understanding of 3-phase power systems
  • Knowledge of power factor and its implications
  • Familiarity with harmonic analysis in electrical systems
  • Proficiency in using electronic power meters
  • Learn how to calculate total harmonic distortion (THD) and its impact on power quality
  • Study the role of harmonic VA and harmonic power factor in power calculations
  • Explore methods for balancing inductive and capacitive loads in 3-phase systems
  • Investigate the use of power triangle diagrams in analyzing power relationships
Electrical engineers, power quality analysts, and technicians working with 3-phase systems who need to optimize power calculations and understand the effects of harmonics on system performance.
Sparky_
Greetings,
I’m looking at the output of an electronic 3-phase meter.
I have 2 “snapshots” from the meter.
In one snapshot I can make sense of most of the data presented.
The output gives me Va, Vb, Vc, Ia, Ib, Ic, and their angles, a single power factor, watts, VA, and VAR.
When I built my power triangle I almost agree with the outputted VA, watts, and VAR. I am within a little on some and right on it on other numbers.
For this snapshot – there was “load” - current in all 3 phases is around 1.1A.
The meter also provides “Harmonics VA and Harmonic pf” I did not use these 2 numbers in my power triangle.
My next snapshot was without load.
I am given the exact same data – current is around 0.1 in all 3 phases.
I cannot get any where close to the power triangle – meaning using the same procedure above – (Vrms)(Irms) – VA, VA(cos()) = watts and so on. I do not get the outputted watts, VA and VAR. The outputted powers are quite a bit higher.
One thing that stands out is that in this snapshot (no load) my harmonics VA and harmonics pf are quite a bit larger than the loaded snapshot.
With load: harmonics VA = 25.7 and harmonics pf = 0.069.
With no load: harmonics VA = 493.965 and harmonics pf = 0.30.
Here is all of the data for the no load:
Va = 113.336, Ia = 0.087: Ia lags Va by 15.86 degrees
Vb = 112.676, Ib = 0.136: Ib leads Vb by 21 degrees
Vc = 113.512, Ic = 0.158, Ic lags Vc by 10 degrees
Watts = 710.078
VArms = 1644.563
VAtd = 1568.625
VAR = 1398.719
Pf = 0.432
Harmonics VA = 493.965
Harmonics pf = 0.3
Can you show me how to get the (above) watts, VA rms, and VAR from the provided currents and voltages?
How do I use the provided harmonic data in power calculations?
Thanks
Sparky
keep in mind what you have involved in the load, a sure mix of inductors and capacitors which can balance you pf. why your b phase is capacitive without load i am not sure, but it is to be expected inductive. remember your power is coming from a transformer, an inductive coil.
Watts = 710.078
VArms = 1644.563
VAtd = 1568.625
VAR = 1398.719
Pf = 0.432
is this data the data your meter provided?
Hey Sparkey
yes that is data straight from the meter. Again in the first snapshot - I could reproduce the Watts, VA, and VAR (which were provided from the meter) by using the provided currents and voltages and their angles.
In this snapshot the same calculation method does not work and I noticed that my harmonic VA and pf harmonics stand out when compared to the first snapshot. I did not use these 2 pieces in my first calculations and my gut says they are needed here. I just don't know how to use these two numbers nor what they are telling me.
Thanks
-Sparky
  • · Replies 41 ·
  • · Replies 55 ·
9K
10K
  • · Replies 61 ·
32K