How Do I Convert Voltage Readings to Pressure in mm H2O Using a Setra 264?
The discussion focuses on converting voltage readings from a Setra 264 pressure sensor to pressure measurements in mm H2O. The Setra 264 outputs a voltage signal ranging from 0 to 5 VDC, corresponding linearly to a pressure span of 0.1 inwc to 100 inwc. For example, 0 VDC represents 0 inwc, while 5 VDC indicates 100 inwc. Users should verify the specific span listed on the instrument's nameplate, as this will dictate the conversion calculations.
  • Understanding of voltage measurement and conversion
  • Familiarity with the Setra 264 pressure sensor specifications
  • Basic knowledge of pressure units, specifically inwc and mm H2O
  • Ability to perform linear interpolation calculations
  • Research the conversion formula from inwc to mm H2O
  • Learn about linear interpolation techniques for sensor output
  • Explore the Setra 264 user manual for detailed specifications
  • Investigate the implications of using differential pressure instruments for flow rate measurements
This discussion is beneficial for engineers, technicians, and anyone involved in pressure measurement and conversion, particularly those using the Setra 264 sensor in HVAC applications.
temaire
I'm using a http://www.setra.com/ProductDetails/264_HVAC.htm" to measure pressure differences in a water manometer. However, I am getting outputs in voltage using a voltmeter and want to know how to convert these voltages to pressure in mm H2O.
Your instrument will output a signal between 0 - 5 VDC.
The span may be between 0.1 inwc to 100 inwc. This should be listed on the nameplate.
The instrument will output the maximum span value at 5 VDC and linear values in between.
For example, suppose it is spanned to 100 inwc. The output will look like:
Instrument Output, Differential Pressure
0 VDC, 0 inwc
2.5 VDC, 50 inwc
5 VDC, 100 inwc
Sometimes, if a differential pressure instrument is used for flow rate, there will be a square root function included. Double check, but I did not see this.
I figured it out.
Thanks for the reply.
  • · Replies 26 ·
  • · Replies 16 ·