Sizing the Supply and return tanks for chilled water system

 
Share Thread Thread Tools
Nov23-11, 01:53 PM   #1
 

Sizing the Supply and return tanks for chilled water system


Well i am currently working as a project engineer for utilities at my factory .This is my first installation of chilled water system.So would be requiring some help in sizing the Chilled water supply and return tanks.I am attaching the picture along so that the system is easily understandable.
Attached Thumbnails
CHILLED WATER FLOW DIAGRAM.jpg  
 
PhysOrg.com
PhysOrg
science news on PhysOrg.com

>> Front-row seats to climate change
>> Attacking MRSA with metals from antibacterial clays
>> New formula invented for microscope viewing, substitutes for federally controlled drug
Nov23-11, 02:09 PM   #2
 
Recognitions:
Gold Membership Gold Member
I have done a lot of heat and mass balance studies for mills, but none of them have been based on such a bare-bones snapshot.

If you want to size your system, you need to need (at a minimum) to identify the seasonal high and low temps of the input water (then over-design by a margin), identify the capacity of your plant to cool the input water to suitable temperatures (with margins, of course), and identify the expected exit temperatures (again with margins) and see if you can size a system that might meet these requirements.

It would also be a really good idea to talk to senior engineers/management, etc to see if there are any plant expansions or process modifications over the horizon that might tip your project into unworkable/uneconomic territory. In an industrial environment, the bean-counters can ruin your career pretty quickly, even if you gave them conservative parameters initially and they changed the rules after the fact or during implementation.

Good luck.
 
Nov23-11, 02:40 PM   #3
 
Well sorry for the bare diagram because i jsut wanted to make it simple.I tried to size it but have few issues .Let em first define my systems parameters.

Water in Chilled water tank is at temperature of 5-6 C
Temperature of Water in Return Tank is aroudn 18 C in Summer and around 14-15 C in winter

Chilled water generated is at 1228 m3/h i.e. 307m3/h by each chiller.

System requirement of chilled water is 856m3/h

I designed the Forward tank(140m3/h) with 10 minutes of buffer time that is the case if chillers go on shutdown due to power failure we would have 10 minutes to get system back online.



I calculated that all the time 131 m3 of water is inside the lines.


Now my concern is the Return Tank .How do i size it and on what basis.SHoudl i jsut keep it 140m3/h or need to size it and on what basis .
 
New Reply
Thread Tools


Similar Threads for: Sizing the Supply and return tanks for chilled water system
Thread Forum Replies
water supply system Engineering Systems & Design 7
Piping stress Analysis for Cooling Water Circuit (Supply/Return) Engineering Systems & Design 2
HVAC - Chilled Water System General Engineering 4
design of a water supply system Engineering Systems & Design 1
Design water supply system Engineering Systems & Design 11