GDo not overcompensate the motor inductance with capacitors as, when you turn it off, the two will become a resonant self-excited...
-
GGuineafowl replied to the thread VFD for powering a car lift.I’ve ordered three ##450V, 30\mu F## capacitors, having approached the calculation differently and got the same answer: At ##400V, 11A...
-
GGuineafowl replied to the thread VFD for powering a car lift.Thanks, I’ll get some EP grease. The only problem is, the lubricator is an oil reservoir, 11, and a tight-fitting felt wick, 9, which...
-
GThe heating could be induced by the thread profiles of screws and nuts not perfectly matching, as when new. If that is the case...
-
GGuineafowl replied to the thread VFD for powering a car lift.The screw is on the right, and turns the other screw via two 90deg gearboxes and a driveshaft under the lift area. The lift nut is no...
-
GGuineafowl replied to the thread VFD for powering a car lift.Ok, so a cosphi of 0.65 gives an angle of 49.5 degrees: $$Z=36.4\Omega <49.5° = 23.6 +j27.7\Omega$$ $$C=\frac 1 {2\pi f 27.7} = 115...
-
GI don't know the details of the VFD that you're considering, but: Reducing the output frequency would be (approximately) the torque...
-
GMeasure the positive reactance of the motor at operating frequency. Then provide negative reactance to cancel most of that.
-
GGuineafowl replied to the thread VFD for powering a car lift.VFD manual should be linked in the first post. Yes, I thought lifting the car slower might reduce the loading of the system. Or, running...
-
GGuineafowl replied to the thread VFD for powering a car lift.As a first attempt, looking at the motor plate (connected in star): $$Z=\frac V I = \frac {400} {11} = 36.4\Omega$$ Find capacitor with...
-
GGuineafowl replied to the thread VFD for powering a car lift.1. Done - it has automatic screw lubricators which have been cleaned out and topped up. 2. Yes, certainly something to try. I assume 3...
-
GGuineafowl replied to the thread VFD for powering a car lift.This one is a 3ph 400V in and out model. Can’t be changed. Cheap enough for a punt on this problem; if no go, I can use it for something...
-
GPower supply to the 7.5kW rotary is 1ph, 240Vac. Supply voltage drop at full load is within 5%. The rotary outputs (roughly) 415Vac 3ph...
-
GGuineafowl replied to the thread High School Straightforward integration….I’ve also seen it written: $$\int fg’ \,dx = fg - \int f’g \,dx$$ Maybe you could preface with ‘f and g are functions of x’ and save...