Thank you all very much, I will confirm primary side voltage to start with.
By the way, the compressor motors have soft start modules only, no frequency inverters, I guess it was value engineering at first sight. And yest TX was to mean a transformer.
Thanks again, will update you if indeed we...
Hello Asymptotic,
433V was what the transformer name plate stated as max output, I am new to the building, as part of the FM team; however the Schneider's load monitoring system indicates that the transformer gives out 446V on all three phases. Then the bus bar tap off unit on 9th floor is...
Hope you may help me to understand how detrimental to compressor motor would be if it operated at voltages exceeding the manufacturer's specified 400V by 12%? so 448V.
I have vendor engineers saying since it exceeds 10% they cannot safely run the plant and of course the voltage monitoring relay...