Recent content by quark

  1. Q

    Boiling water using electric current

    I hope you will not use the turbine for producing electric power:frown:
  2. Q

    How Does Temperature Change in a Sealed Room with a Broken Cooling System?

    The equipment rating should be in btu/hr rather than btu. Use the formula Q = 1.1xcfmxdT. As you have no air circulation, after adding up all the heatloads in the room and getting the total heat input in btu/hr, divide the room volume by 60. This gives you the temperature rise per minute.
  3. Q

    Websites/books for 'Engineering Mechanics'.

    Timoshenko and Young
  4. Q

    Can 25 PSI Methane Flow Through a 3/8 Pipe Meet a 392,000 BTU/hr Demand?

    First get the mass flowrate of methane. If you know the calorific value in btu/lb (better NCV or LHV), then total heat flowrate/LHV gives you mass flowrate of methane in lb/hr. That is the mass flowrate you require at any pressure. For piping calculation, if you can get an equation that directly...
  5. Q

    Effect on flow after sudden expansion

    There are two non practical assumptions here. One is that there is no pump in the system. Second one is that pressure in the header remains constant. I don't have issues (if mods forgive me) as long as this is a homework problem. Otherwise, better description of the system may yield better...
  6. Q

    Help with pressure differences-sponge and wood

    Incase of sponge, the area that experiences the force is more and that is why pressure is less. Press the sponge to such an extent that it will not deform and then your pressure reading should be same with that of hard surface.
  7. Q

    Compressor Power Equation | Factors & Link

    The site seems to be down at the moment but there are online calculators for recips and centrifs at www.processassociates.com To to process tools section.
  8. Q

    Understand Evaporator Terms & Choose Right Compressor

    The fluid power consumed by a compressor can be calculated by mass flowrate of refrigerant times the enthalpy difference. The enthalpy of super heated gas is more than saturated gas so power consumption will be less. However, there are limitations to the extent of superheat and you can get those...
  9. Q

    Calculating cubic ft/ min and PSI

    Yes, provided listed cfm is acfm at 175 psig Yes. The above equation I wrote considers isothermal condition i.e PV = constant. When you are decreasing the pressure in a pressure reducing valve, the temperature change in the fluid is not significant (at least for the sake of...
  10. Q

    Calculating cubic ft/ min and PSI

    I would like to expand Q_Goest's comment a bit. When you speak of PD devices, either mass flowrate or volume flowrate at standard conditions (i.e scfm) remains constant irrespective of discharge pressure, keeping suction pressure constant, but actual volumetric flowrate (i.e acfm) changes...
  11. Q

    X Watts to run = x Watts of heat?

    I am not saying that ASHRAE specifies this method for chiller room ventilation. However, I mean they don't deal with the situations on a case to case basis. The heat load from the equipment is categorized into 3 parts. 1. Machine in and driver out, 2.Machine out and driver in and 3...
  12. Q

    Finding the Angle of Lap, Tight Side Tension, & Belts for a Pulley Belt Drive

    Nice link Fred. I have belt selection books from 2 manufacturers but this online reference is handy.
  13. Q

    Find the Perfect Drain Size for Your Cylindrical Tank | Flow Physics Assistance

    That is a funny tank, in practice. (16 m height / 2m dia.) Is it horizontal or vertical? Just go to the link below and do some trials and error. http://www.efunda.com/formulae/fluids/draining_tank.cfm#calc Consider 3 bar as 30 meters head approximately. 60% liquid adds about 9 meters and...
  14. Q

    X Watts to run = x Watts of heat?

    I have seen this question coming up many times in many forums. We are all right that total energy shouldn't be considered as heat load when calculating heat load of a controlled space. For example, if we place a water cooled chiller along with motor in a controlled space, as per ASHRAE...