Hi-Rise Plumbing: Is It Risky & Unsanitary?

  • Thread starter Thread starter DaveC426913
  • Start date Start date
Click For Summary

Discussion Overview

The discussion revolves around the plumbing system in a high-rise building, specifically addressing concerns about the sanitary conditions of floor drains in relation to toilet waste. Participants explore the mechanics of plumbing traps, potential code violations, and the implications of sound observations related to water flow in the drainage system.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Conceptual clarification

Main Points Raised

  • One participant expresses concern about the proximity of solid waste to the bathroom floor drain, questioning the sanitary implications of such a setup.
  • Another participant suggests that the drain should be protected by a trap, implying that this would mitigate health risks.
  • Some participants argue that it may be a code violation for toilets to drain into a pipe that is open to the bathroom, raising concerns about air displacement and potential exposure to sewer gases.
  • Discussion includes the mechanics of floor drains, with mentions of trap primers that help maintain water levels in traps to prevent odors and gases from entering the bathroom.
  • Some participants share experiences of hearing water gushing down the drain, with differing opinions on whether this indicates proper function or potential issues with the trap.
  • One participant notes that high-rise plumbing systems often include horizontal sections to manage the kinetic energy of waste, suggesting a design consideration to prevent blockages.
  • There are humorous exchanges about the lengths one might go to investigate the plumbing issue, including the idea of conducting an experiment to observe the drain's function.
  • A participant shares a detailed observation of the sounds produced by the drain during toilet flushing, concluding that the system appears to be functioning correctly based on their findings.

Areas of Agreement / Disagreement

Participants express a mix of agreement and disagreement regarding the functionality and safety of the plumbing system. While some believe the system is functioning as intended, others raise concerns about potential code violations and sanitary risks. No consensus is reached on the overall safety of the plumbing setup.

Contextual Notes

Participants reference various plumbing codes and mechanisms, but there is uncertainty about specific regulations and the exact nature of the plumbing setup in the building. Discussions about the effectiveness of traps and the potential for sewer gases highlight the complexity of the plumbing system.

DaveC426913
Gold Member
2025 Award
Messages
24,318
Reaction score
8,509
I work on the 24th floor. In the loo, I noticed a standard 4" drain in the floor about 6 feet from the toilets. When the toilets flush, you can clearly hear water gushing down the drain. I'll bet if I shone a light down there, I'd be able to see it dropping down the vertical. i.e I suspect it come out at a straight T-joint, a foot below the drain.

Is this not risky - but more to-the-point - highly unsanitary? I mean, if there's solid waste flowing and sloshing just a foot below that grill - even in normal operation - isn't that spewing bacteria-laden particles into the bathroom proper?
 
Engineering news on Phys.org
Shine a flashlight into the drain; I'd be shocked if it wasn't protected by a trap.
 
  • Like
Likes   Reactions: CWatters
russ_watters said:
I'd be shocked if it wasn't protected by a trap.
Like this:

http://www.americanplumbingflorida.com/wp-content/uploads/2016/09/p-trap-plumbing.jpg

p-trap-plumbing.jpg
 

Attachments

  • p-trap-plumbing.jpg
    p-trap-plumbing.jpg
    16.2 KB · Views: 1,710
He said toilets, not sinks!
Sounds like a code violation to have the toilets drain into a pipe that is open to the loo. As 'it' goes down the air is displaced up into the room through the floor drain. Bad situation!
 
AZFIREBALL said:
He said toilets, not sinks!
Sounds like a code violation to have the toilets drain into a pipe that is open to the loo. As 'it' goes down the air is displaced up into the room through the floor drain. Bad situation!
No, please re-read the diagram. It says drain or sink. Floor drains will generally have p-traps too, I believe. I'm more familiar with electrical codes and not plumbing codes, but I'll try to find a code section to post...
 
Properly built floor drains have water traps and ultimately they will connect to the same soil drain or stack as the toilets are connected to. How close they connect will determine how easily you can hear the toilets washing past them.

The floor drains get water for their traps from trap primers which drip water into them periodically. If you ever look at a urinal or toilet flush valve and see a small 3/8" water line mysteriously running from them into the wall, that is one way the trap primers get their water. Every time you flush one of them you send a little spurt of water to a floor drain.

These systems are notoriously fragile and often go bad allowing traps to dry out. A dry trap would definitely be noisier than a full one. It would also allow sewer gases to pass through to that room. Custodians typically catch on to this and will allow some mop water to go down the drain every night, but not all of them know about it.

Ultimately your toilets, sinks, urinals, water fountains, showers, floor drains, vents etc ad nauseum all are connected and if there's ever a clog then sewage could back up to the first lowest drain above the blockage. Could be a floor drain, could be a shower. Fun stuff.
 
Last edited by a moderator:
  • Like
Likes   Reactions: Klystron, russ_watters, jedishrfu and 2 others
There are also concentric traps that can be serviced from above. Also used for wet room shower drains.
 
  • Like
Likes   Reactions: russ_watters
there's another part of the system in houses, the plumbing vent in the roof can get clogged with leaves and debris and cause issues with flushing. I imagine high rises have something similar that must be kept open to the air.

https://m.wikihow.com/Vent-Plumbing
 
DaveC426913 said:
When the toilets flush, you can clearly hear water gushing down the drain.
I've seen that too where i worked. Indeed i could look in and see water run by. But never any solids and it never smelled..
Had i seen solids i'd have known somebody took a shortcut and abused the concept of "wet vent"

upload_2018-10-18_13-9-48.png

In that image the toilet is vented through the vertical lavatory drain line..

but i think (dont know for sure) it was one of those automatically primed drains instead, as previous post mentioned. . See this short video:


Armed with those basics you can observe further and figure it out...
I love learning 'tricks of the trade' through studying everyday experiences. .old jim
 

Attachments

  • upload_2018-10-18_13-9-48.png
    upload_2018-10-18_13-9-48.png
    34.7 KB · Views: 716
  • #10
russ_watters said:
Shine a flashlight into the drain; I'd be shocked if it wasn't protected by a trap.
What makes me think it's draining directly is that I can hear it clearly. The high-pitched sloshes that you hear directly from water, rather than the lower-pitched, muffled sounds filtered through a trap.

I doubt I wold hear such sounds coming from my shower drain at home, since it will be blocked by the water in the S-trap.

I'm loathe to get on my knees and look into a drain with a flashlight in the middle of a busy office washroom...
 
Last edited:
  • #11
berkeman said:

berkeman said:
No, please re-read the diagram. It says drain or sink. Floor drains will generally have p-traps too, I believe. I'm more familiar with electrical codes and not plumbing codes, but I'll try to find a code section to post...

I'm familair with P-traps and S-traps. But the water-filled trap should muffle the otherwise very clear sounds of gushing water.

As in your diagram,. I should be hearing sounds coming from everywhere except directly out of the drain.
 
  • #12
DaveC426913 said:
I'm familair with P-traps and S-traps. But the water-filled trap should muffle the otherwise very clear sounds of gushing water.

Yes, unless the water in the trap evaporated away. See #6
 
Last edited:
  • Like
Likes   Reactions: russ_watters
  • #13
Another fun fact, just slightly off-topic.
In high-rise buildings the drains have a short horizontal section every few floors. Without that feature, by the time the solids get to the bottom they have enough kinetic energy to blast right thru the pipe bend that goes out to the city sewer.

p.s. Sounds like a problem that was learned the hard way!
 
  • Like
Likes   Reactions: Klystron and berkeman
  • #14
If it's a top access trap perhaps someone forgot to put the insides back in.
 
  • #15
Sounds like the trap is dry or not present. Feel free to dump some water down there. A gallon would be more than enough to fill a 3 or 4 inch trap. Shine a light down it afterward, if you see a pool of water you are good to go. If you just see a bend in the pipe then there's no trap and you should ask facilities to fix that.
 
  • Like
Likes   Reactions: russ_watters and anorlunda
  • #16
I can't believe I'm actually considering doing this in the name of science.

Grabbing a flashlight and a bucket and getting down on my hands & knees in the stall of a bathroom on the 24th floor of the office building where I work.

Is this one of those moments where, after it's ruined your life by going viral, you look back and think to yourself "...sure picked an unlucky day to wear the latex gimp suit to work..."
 
  • #17
DaveC426913 said:
I can't believe I'm actually considering doing this in the name of science.

Maybe wait for casual Friday.

Let us know the results of your experiment.
 
  • #18
DaveC426913 said:
sure picked an unlucky day to wear the latex gimp suit to work..."

Make a show of it. Get a thrift store tuxedo and top hat , gloves and a watering can decorated with stick on flowers. .
 
  • Like
Likes   Reactions: Tom.G, DaveC426913 and Bystander
  • #19
OK, as a first round of study, I examined the duration and timing of the water noises. I recorded it so as to minimize estimation error.

This is a chart of the sounds.
toilet flush.png


The kabloosh lasts five seconds, and then there is a full three second gap of silence before the tinkling sound in the drain.
The sound from the drain starts quite abruptly and then ends quite abruptly 5 seconds later (i.e. as if controlled).

This to me, indicates the tinkle is either actively or passively injected into the drain after the flushing is completed. Likely the mechanism that keeps the trap primed with water.

Looking down into the drain, I can see water about a foot down - surely the water in the trap. It jostles during flushing but there is no flow to be seen.
The tinkling, on the other hand, is quite apparent. It comes from higher up, about 6 inches below the grill, and is only maybe 250mL, if that.

I would say this drain is not only working correctly, but is designed to actively prevent evaporation of the trap water.

I am satisfied with my results.

When will my grant money arrive?
 

Attachments

  • toilet flush.png
    toilet flush.png
    4.2 KB · Views: 584
  • Like
Likes   Reactions: russ_watters, Tom.G and jim hardy
  • #20
DaveC426913 said:
OK, as a first round of study...

Looking down into the drain...
Did you wear a janitor's jumpsuit for Halloween?
 
  • #21
russ_watters said:
Did you wear a janitor's jumpsuit for Halloween?
This is the first year in decades that I did not wear a 'ween costume to a job.
Something about this place... :frown:
 