How can adjacent air be accounted for in fresh air exchanges for HVAC systems?

  • Thread starter Thread starter MacLaddy
  • Start date Start date
  • Tags Tags
    Air Hvac
AI Thread Summary
In evaluating fresh air exchanges for an HVAC system in a negative air pressure medical laboratory, the discussion highlights the need for a minimum of 6 air changes per hour (ACH), with 2 ACH from outside air, according to ASHRAE 170. The calculated total ACH is 28.5, but determining the fresh ACH is more complex, particularly when adjacent air is considered. It is noted that air can be deemed "fresh" if it hasn't been previously used for ventilation, and adjacent air may be usable for dilution if no contaminants are present in those areas. The conversation emphasizes that while ASHRAE standards specify outdoor air requirements, practical ventilation may yield a lower percentage of fresh air than theoretically calculated.
MacLaddy
Gold Member
Messages
290
Reaction score
11
TL;DR Summary
Investigating methods to calculate fresh air intake from adjacent spaces
Good morning folks. I have a question about fresh air in an HVAC system. The explanation I provide are a bit tedious, but the question is eventually asked towards the bottom.

I am evaluating a negative air pressure room for a small medical laboratory. Using ASHRAE 170, I know this room needs to have a minimum total of 6 air changes per hour (ACH), with 2 of those ACH coming from fresh outside air. The room air should also be exhausted directly to the outdoors and not returned to the system.

Using a calibrated air hood, we measured the following.

Supply: 165 CFM
Exhaust: -190 CFM
No Return.
Room Volume: 400 CF

Knowing this, I can easily calculate total air changes per hour.

##ACH = \frac{190 (ft^3/min) * 60 (min/hr)}{400 ft^3} = 28.5##

This easily meets the criteria for Total ACH. However, the fresh ACH is more difficult. We are going to attempt the Outside Air Percentage (OA) method.

## OA = \frac{MAT - RAT}{OAT - RAT} \times 100##

Where:

RAT = Return Air Temperature.

MAT = Mixed Air Temperature.

OAT = Outside Air Temperature.

Now my question. If we aren’t meeting requirements via the OA% method, is there a way to figure out how much fresh air is coming from the adjacent area? From the numbers, we can see there is a deficit of 165-190 = -25 CFM. This is approximately 3.75 ACH.

When is fresh air not considered fresh anymore? Is there a method to account for adjacent air at all, or is it typically ignored and considered just a positive or negative relationship?

Thanks,
Mac
 
Engineering news on Phys.org
MacLaddy said:
This easily meets the criteria for Total ACH. However, the fresh ACH is more difficult. We are going to attempt the Outside Air Percentage (OA) method.

## OA = \frac{MAT - RAT}{OAT - RAT} \times 100##
You're saying you don't have a direct reading of the outside air fraction at the air handling unit? That's a little surprising, but ok...
Now my question. If we aren’t meeting requirements via the OA% method, is there a way to figure out how much fresh air is coming from the adjacent area? From the numbers, we can see there is a deficit of 165-190 = -25 CFM. This is approximately 3.75 ACH.

When is fresh air not considered fresh anymore? Is there a method to account for adjacent air at all, or is it typically ignored and considered just a positive or negative relationship?
That's the million dollar question with ventilation. ASHRAE and its interpretations are not always completely clear, but the basic logic is that air is "fresh" if it can do what it's supposed to do and hasn't already been used for that purpose. In other words, if you are supplying fresh air (from outside) to one room at a code required rate, you can't then transfer it to another room and still call it "fresh", even if there was nobody in that room to contaminate it. But if you need the air for dilution of chemical contaminants in a lab, for example, and there's no lab in the adjacent corridor, then all of the air transferred from that corridor is usable for dilution of the chemicals in that lab.

AHRAE 170-2008 (the latest I have...), sect 7.1.1b says:
"The air change rates specified are for supply in positive pressure rooms and for exhaust in negative pressure rooms."

In other words, your lab is negative because it is protecting the adjacent rooms from what's going on inside, so the air transferred from those adjacent rooms is "fresh" for that purpose (otherwise, those rooms would be negative too). Applying this broadly to your problem, I'd say you are taking the analysis further than you need to: your room is 100% exhausted so for the purpose of your question all of that 28.5 ACH is OA/fresh/ventilation. Period, analysis finished.
 
  • Like
Likes Lnewqban, anorlunda and MacLaddy
russ_watters said:
You're saying you don't have a direct reading of the outside air fraction at the air handling unit? That's a little surprising, but ok...

No. It's an older system where multiple small heat pumps (2 to 5 Ton) are spread through the clinic and all supplied from one DOAS.

russ_watters said:
That's the million dollar question with ventilation. ASHRAE and its interpretations are not always completely clear, but the basic logic is that air is "fresh" if it can do what it's supposed to do and hasn't already been used for that purpose. In other words, if you are supplying fresh air (from outside) to one room at a code required rate, you can't then transfer it to another room and still call it "fresh", even if there was nobody in that room to contaminate it. But if you need the air for dilution of chemical contaminants in a lab, for example, and there's no lab in the adjacent corridor, then all of the air transferred from that corridor is usable for dilution of the chemicals in that lab.

AHRAE 170-2008 (the latest I have...), sect 7.1.1b says:
"The air change rates specified are for supply in positive pressure rooms and for exhaust in negative pressure rooms."

In other words, your lab is negative because it is protecting the adjacent rooms from what's going on inside, so the air transferred from those adjacent rooms is "fresh" for that purpose (otherwise, those rooms would be negative too). Applying this broadly to your problem, I'd say you are taking the analysis further than you need to: your room is 100% exhausted so for the purpose of your question all of that 28.5 ACH is OA/fresh/ventilation. Period, analysis finished.

That's a great way to view it and one that I logically agree with. One caveat I worry about is the ASHRAE Standard specifically says the lab requires 2 "Outside ACH." But yeah, for the adjoining space to stay positive it would require fresh air. Analysis Finished.

Thanks. That was very helpful.
Mac
 
  • Like
Likes anorlunda, berkeman and russ_watters
MacLaddy said:
... It's an older system where multiple small heat pumps (2 to 5 Ton) are spread through the clinic and all supplied from one DOAS.
For an existing system like that one, the minimum required volume of air that the dedicated outdoor unit supplies to all air handlers should have been calculated based on the ventilation rate procedure of ASHRAE 62.1.
That means that certain amount of outside air is fed to the whole building based on a theoretical need of multi-zones, but in no way each of those zones receives the volume of fresh air that "belongs" to it.

If the room you are evaluating is exhausted at 28 changes per hour, I would say that it is receiving the equivalent of 3 to 8 changes per hour of fresh air.
Practical ventilation is never less than 10% of the supplied air volume for dealing with sensible and latent loads of commercial buildings, for medical facilities is higher than that.

Copied from pages 8 and 14 of ASHRAE standard 170-2017, under Space ventilation-Hospital spaces and in reference to Table 7.1:
"7.1.a.6.i.i The minimum outdoor air change rate listed in this standard shall be interpreted as the ##V_{oz}## (zone outdoor airflow) for purposes of this calculation."

:cool:
 
  • Like
Likes berkeman
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly

Similar threads

Replies
2
Views
4K
Replies
2
Views
5K
Back
Top