Thank you all for prompt reply.
Baluncore,
The move profile is sinusoidal, this type of indexer is common in the manufacturing industry, it give a nice slow start/stop at the pitch, this system has two positions. Thanks for correcting my math.
Berkeman.
Risks in my business is prioritized to people, tooling, part. I am assuming the .86 represents from max velocity, since the profile is sinusoidal, ithink the velocity varies throughout the index cycle, at this point I assume at 90 deg intervals.
Tigerdawg.
The stop time is based on power disconnection from the motor driving the thing, the time to disable is the system response time. This includes the actuation of the stop signal, fieldbus (Ethernet) transport time, processor input update time, logic execution time, I/O faults within the system, output update time, and contactor opening time (power removal). Under normal stopping conditions the drive (VFD) supplies regenerative braking, when the dial is in dwell. Under the operator protection scenario, the contactor rules.
I am reasonably sure the calculations are correct, this is a common system, and the technology has been around for a long time. Braking is common, and works just like the brakes on your car, no damage unless you hit something.
All,
I am using worst case .86 seconds for stop time, but my intellectual curiosity always overpower me and I have to know more. Interestingly enough I find the response time of a contactor with an integral diode, is faster that one with an external diode. The diodes are used to 'snub' counter EMF. Does anyone have an explanation? Maybe some additional inductance, or slower field collapse?