| Aug12-11, 03:47 AM | #1 |
|
|
neutral wire and earth
why during the the distribution of electricity to houses neutral wire is connected to earth wire?
|
| Aug12-11, 05:20 AM | #2 |
|
|
That would be illegal in UK. In the US the power feed neutral is connected to a supply transformer primary, not to earth. The local house neutral from the transformer secondary is earthed at the distribution board because the US practise needs is split phase and needs a stable cente zero. |
| Aug12-11, 06:59 AM | #3 |
|
|
In the US, the center tap (neutral) of the transformer (secondary) supplying your house is connected to a large conductor with a spike on the end that is driven into the ground. One of the two connections on the primary of this transformer (the "return") is also connected to this very same spike in the ground at the utility pole.
This neutral from the center tapped secondary is also connected to your service entrance (distribution board) at your house. Here again, it is also connected to a spike that is driven into the ground next to your house. This is also the place where the "equipment grounding conductor" is connected with the neutral and the spike and driven into the ground. Terminology is important here. What I just called the "equipment grounding conductor" is the technical term for this bare copper (or sometimes green insulated) wire in the US. This is more commonly referred to as "ground" or "the ground wire". From what I understand, this is called the "earth wire" in the UK. These conversations always seem to get confused because of the different terminologies we use on opposite sides of the pond. :-) |
| Aug12-11, 09:39 AM | #4 |
|
|
neutral wire and earth |
| Aug12-11, 09:43 AM | #5 |
|
|
|
| Aug12-11, 09:50 AM | #6 |
|
|
I will leave you and Evil Bunny to have a long discussion about US practice.
I repeat: In the UK the neutral is not connected to ground. Do not try the very unsafe experiment of grabbing hold of the line (it is not called live; both are actually 'live'). Whether you get a shock or not depends upon many factors, but not upon whether the neutral is earthed. go well |
| Aug12-11, 10:31 AM | #7 |
|
|
|
| Aug12-11, 10:46 AM | #8 |
|
|
|
| Aug12-11, 10:58 AM | #9 |
|
|
|
| Aug12-11, 11:43 AM | #10 |
|
|
With a totally floating ac system with two conductors it is possible to touch either conductor safely, because the other conductor would instantly assume the supply potential wrt Earth. A lot of equipment supplies are floating (connected to the mains via an isolating transformer) - and it is a very safe system -EXCEPT when one side becomes grounded and this is not detected and then someone else happens to touch the other leg (assuming that they are safe). Any large network will have resistive paths to earth and so you can never be sure that it totally floats - so you may as well tie one side to near-earth and then you know where you are. In a three phase system, this is more obvious, I think. If the loading of a three phase system is equal on all three legs then very little (zero) current will actually flow in the neutral wire. |
| Aug12-11, 11:45 AM | #11 |
|
|
|
| Aug12-11, 12:25 PM | #12 |
|
|
There are many circumstances where a fault will not be detected. Only when there is enough current to blow a fuse will the mere grounding of the neutral "detect" a fault. (And that would never reveal a neutral-earth connection fault) The only way to detect a fault reliably is to use a residual current circuit breaker and that would work with or without a grounded neutral and it will spot a fault on either leg. Problem is that RCCBs are active devices and not actually fail-safe.
|
| Aug12-11, 12:54 PM | #13 |
|
|
- Almost forgot, I don't think I have ever seen a GFCI fail to open during a fault. It is more likely that they trip unnecessarily. |
| Aug12-11, 01:10 PM | #14 |
|
|
Let's get a few things straight.
Single phase electrical feeds to a property are normally controlled by a single pole switch, which is in the line circuit. So the line can be 'live' or disconnnected. The neutral is permanantly 'live' with this system. Now suppose someone was working on the wiring and had switched off the switch ie disconnected the line. And further suppose that a line- neutral cross fault occurred upline. The neutral would aquire the line voltage, a potentially lethal situation to anyone working on the wiring. If, however the neutral was earthed a fault current would flow, causing disconnection and resulting in safety. A further caveat. Birds can sit on transmission lines because they can fly up there and are small enough not to touch anything else at the same time. It is pure folly for a human, standing on the ground, to attempt to emulate this. |
| Aug12-11, 04:01 PM | #15 |
|
|
|
| Aug12-11, 04:17 PM | #16 |
|
|
![]() What disagreement? What is better? |
| Aug13-11, 03:10 AM | #17 |
|
|
@averagesupernova
RCCB is spelled out in the para you have quoted. I could ask what your acronym stands for, too. Someone mentioned single pole switching. This is always a source of danger. Also, in a balanced system, fusing and switching can be problematical. Do you use double or single leg switching? Only one fuse will blow but this does not ensure isolation in a balanced system. Neutral fusing in a one sided system is even more deadly. |
| New Reply |
| Thread Tools | |
Similar Threads for: neutral wire and earth
|
||||
| Thread | Forum | Replies | ||
| Noise in the neutral wire | Electrical Engineering | 25 | ||
| Question about the neutral wire in an electrical system... | Classical Physics | 4 | ||
| Neutral wire? | Electrical Engineering | 1 | ||
| Wire Reverse between Life and Neutral | Electrical Engineering | 30 | ||
| Neutral Wire | General Physics | 16 | ||