Relationship between static pressure and CFM

AI Thread Summary
The discussion centers on understanding the relationship between static pressure and airflow (CFM) in blower fans. Higher CFM does not inherently result in greater static pressure, as each fan has specific performance characteristics that can be analyzed using fan curves. To achieve a moderate suction of 150 to 200 CFM with around 1 inch of static pressure, one must consider the specific fan's capabilities. Resources like fan curves and manufacturer catalogs can help identify suitable fans for particular applications. Ultimately, selecting the right fan requires matching the desired airflow and static pressure to the fan's performance specifications.
dmehling
Messages
114
Reaction score
0
I am wanting to create a moderate amount of suction with a blower fan and I am trying to figure out the relationship between static pressure and airflow measured in CFM. Does higher CFM necessarily give you greater static pressure? I'm thinking I need between 150 to 200 CFM to get around 1 inch of static pressure, but that is a wild guess. When I search online for such a fan I find either a computer cooling fan which is not enough power or I get an industrial type blower fan that is way too powerful. I can't seem to find something in between.
 
Engineering news on Phys.org
Static pressure is pressure without motion (that's what the word "static" means). So there is no positive relationship between fan static pressure and flow rate, with two exceptions:

1. For a specific fan, each possible static pressure corresponds to a specific airflow. Ie, if you close a valve and increase the backpressure the fan has to overcome, the new cfm can be read from a fan curve by matching the new pressure to the curve.

2. In a situation where all of the static pressure is turned into velocity pressure - such as in a pressurized tank with an open valve, you can use Bernoulli's equation equating the two to find velocity from static pressure.

Without knowing the application, it is tough to help, but you can go online and find fan curves and see if they'll work for you. You'll notice on most that they show a static pressure for airflows all the way down to zero. Here's a catalog from a manufacturer I use a lot. Curves start on PDF page 20: http://www.lorencook.com/PDFs/Catalogs/AC.pdf
 
Last edited by a moderator:
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
After over 25 years of engineering, designing and analyzing bolted joints, I just learned this little fact. According to ASME B1.2, Gages and Gaging for Unified Inch Screw Threads: "The no-go gage should not pass over more than three complete turns when inserted into the internal thread of the product. " 3 turns seems like way to much. I have some really critical nuts that are of standard geometry (5/8"-11 UNC 3B) and have about 4.5 threads when you account for the chamfers on either...