Relationship between static pressure and CFM

Click For Summary
The discussion centers on understanding the relationship between static pressure and airflow (CFM) in blower fans. Higher CFM does not inherently result in greater static pressure, as each fan has specific performance characteristics that can be analyzed using fan curves. To achieve a moderate suction of 150 to 200 CFM with around 1 inch of static pressure, one must consider the specific fan's capabilities. Resources like fan curves and manufacturer catalogs can help identify suitable fans for particular applications. Ultimately, selecting the right fan requires matching the desired airflow and static pressure to the fan's performance specifications.
dmehling
Messages
114
Reaction score
0
I am wanting to create a moderate amount of suction with a blower fan and I am trying to figure out the relationship between static pressure and airflow measured in CFM. Does higher CFM necessarily give you greater static pressure? I'm thinking I need between 150 to 200 CFM to get around 1 inch of static pressure, but that is a wild guess. When I search online for such a fan I find either a computer cooling fan which is not enough power or I get an industrial type blower fan that is way too powerful. I can't seem to find something in between.
 
Engineering news on Phys.org
Static pressure is pressure without motion (that's what the word "static" means). So there is no positive relationship between fan static pressure and flow rate, with two exceptions:

1. For a specific fan, each possible static pressure corresponds to a specific airflow. Ie, if you close a valve and increase the backpressure the fan has to overcome, the new cfm can be read from a fan curve by matching the new pressure to the curve.

2. In a situation where all of the static pressure is turned into velocity pressure - such as in a pressurized tank with an open valve, you can use Bernoulli's equation equating the two to find velocity from static pressure.

Without knowing the application, it is tough to help, but you can go online and find fan curves and see if they'll work for you. You'll notice on most that they show a static pressure for airflows all the way down to zero. Here's a catalog from a manufacturer I use a lot. Curves start on PDF page 20: http://www.lorencook.com/PDFs/Catalogs/AC.pdf
 
Last edited by a moderator:
https://newatlas.com/technology/abenics-versatile-active-ball-joint-gear/ They say this could be used as a shoulder joint for robots. Mind boggling! I'm amazed this has been done in real life. The model they show seems impractical to me. The ball spins in place but doesn't connect to anything. I guess what they would do would be attach a shaft to that ball, then restrict the motion so the drive gears don't contact the shaft. The ball would have two limited degrees of freedom then a...

Similar threads

  • · Replies 6 ·
Replies
6
Views
2K
Replies
6
Views
4K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 7 ·
Replies
7
Views
11K
  • · Replies 22 ·
Replies
22
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 11 ·
Replies
11
Views
7K
  • · Replies 11 ·
Replies
11
Views
3K