How to calculate needed inverter power?
  • Thread starter Thread starter Farkane
    Inverter Power
The discussion revolves around determining whether a specific inverter can adequately supply power to a load of approximately 10 kW. Participants explore the inverter's specifications, including its continuous and peak power ratings, and consider various factors affecting power requirements, such as load characteristics and power factor.
  • Farkane questions if a 10 kW load can be supported by an inverter rated for 10 kVA continuous power and 12.5 kVA for 30 minutes.
  • Bobbywhy suggests that more information is needed and provides links to UPS power requirement calculators.
  • Farkane clarifies that the inverter is used for auxiliary loads in a trolleybus system and seeks a method to prove its adequacy to directors.
  • One participant mentions the importance of considering the power factor of motors when calculating the apparent power needed, suggesting that losses could increase the required power above the inverter's rating.
  • Another participant emphasizes the need to know the maximum load that could occur and the significance of the inverter's short circuit capacity.
  • Farkane expresses a belief that the inverter's continuous power rating is the key factor and suggests that intermittent loads may not exceed the inverter's capacity.
  • A request is made for a formula to calculate inverter load power for better understanding.
Participants do not reach a consensus on whether the inverter is sufficient for the load. There are multiple viewpoints regarding the factors that should be considered, such as power factor, load characteristics, and the need for additional calculations.
Participants note the importance of understanding the specific characteristics of the loads and the inverter's operational limits, but do not resolve the mathematical or technical uncertainties presented.
Farkane
Hi all ,
I m rookie engineer and i just faced a big problem for me.There is a inverter which has ;
750V DC input voltage
3x400 V AC outpu voltage
12.5 kVA 30min power
And ı have appx 10kw loads. Is my inverter enough to feed that load?
Even if it can feed how can i prove that ?
Thanks in advanced
Farkane, Welcome to Physics Forums!
You have not given enough information to expect a useful response. Please try to put your requirements into one of these:
Here are a few Uninterruptible Power Supply (UPS) Power Requirement Calculators:
http://www.csgnetwork.com/upssizecalc.html
http://www.tripplite.com/en/products/selectors/ups/index.cfm
http://www.refurbups.com/UPS-Sizing-Calculator
If you do not get satisfactory answers, then do return here and post your specific questions and doubts.
Cheers,
Bobbywhy
I am working as a trolleybus maintenance engineer. So our auxiliary inveter has appx 10 kW loads when trolleybus is running and as you know trolleybus has 750V DC catener line. Aux inverter input voltage is 750V DC and output voltage is 3x400V AC.It has 10kVA continuous power.Inverter with its 3x400V AC feeding that 10kW load. My point is , how can i determined that inverter power is enough to feed how much load? I need something that prove to my directors.
Thanks
Farkane
I assume the inverter is feeding a motor? In that case the the motor is probably rated with a power factor (PF), cos phi. If the motor is rated 10 kW, that is 10kW mechanical output. Take into account the losses you get electrical active power of, let's say 11kW. And with a power factor of 0.8 you get apparent power of S=13.75kVA. That is higher than the nominal rating of your inverter. Take note that this is just some random numbers just to illustrate the point.
Maybe you don´t need full power when running on aux. power, or maybe just intermittent during acceleration. In such a case, the inverter might do the work. This can be controlled. Any how, the inverter needs to be secured with fuses and controls in order for it to operate inside its ratings.
How is the Trolleybus industry going?
You can assume that inverter is feeding auxiliary units like air compressors,steering pumps etc. There is already a motor inverter in the vehicle. According to this informations how can
i calculate inverter need power?
Btw trolley sector is pretty good. Sector is reliable and environmental so that most of the municipalities prefer trolley system instead of street tram. Also street trams are more expensive than trolley.
Ok, but the approach is the same. Air compressors and pumps are driven by electric motors. But the loading of these are probably more constant than traction motors.
In order to accurately dimension the inverter you need to know accurately the maximum load that can occur. As you have stated, the inverter can supply 10 kVA constantly, and 12.5 kVA for 30 min.
If this is a factory installation you probably can find the nominal rating of the appliances and circuit in the documentation.
Another important point is the short circuit capacity of the inverter. That is, it must be able to provide enough power to trip the circuit breaker during a fault.
As far as i understand my inverter continuous power is the significative factor. Also aux. equipments are working randomly they are not working continuously except steering pump. So that my 10kVa will be enough for my loads. What you think about my idea?
Can someone show me the formula of callculating inverter load power? I need some calculation than i can easily understand
  • · Replies 18 ·
  • · Replies 47 ·