Air pressure difference between floor & ceiling

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
4 replies · 4K views
tinkeringone
Messages
15
Reaction score
0
Can't figure out how to get my digital manometers to read the pressure difference between the air near the floor vs. at the 8' high ceiling. It reads 0 IWC no matter how I do it. One of my instruments is a micromanometer (reads as low as .001 IWC pressure differential), and it reads 0 IWC there too.
I'm zeroing the meter at floor level, and have no hose on the "reference" port. And I gave a 9 foot manometer hose on the "signal" port with the meter at floor level and the open end of the hose a few feet from the ceiling.
I'm thinking that there be about a 0.108 IWC PD there with that 8' difference in height. Why am I getting 0? It isn't an air tight room, and no fans are on.
 
Physics news on Phys.org
russ_watters said:
Are you accounting for the air pressure in the manometer tube...?

I guess not, if the tube you're referring to is the hose going from the digital manometer to the ceiling. I assumed that pressure in the hose was the same as the air pressure at the ceiling where the open end of that hose is.
Never had to do that just measuring static pressure, i.e. in an air duct. But I guess that was at about the same height as the meter.
How would I account for the pressure in that hose?
 
tinkeringone said:
I assumed that pressure in the hose was the same as the air pressure at the ceiling where the open end of that hose is.

No. The air pressure in a vertical length of hose will vary with height, exactly the same way as the air pressure in the room.

If you position the hose vertically, seal the end, and then bring it down to floor level you should see a difference in reading. But correcting the reading to give you an accurate measurement would be complcated, especially if the hose is flexible.

The straightforward way to measure this is with an instrument that measures absolute pressure, not relative, and is sensitive enough to show the small pressure difference.
 
Thank you, AZ, as I too was unsuccessfully "measuring" height air dP in my room with a diff. manometer. Now I see why - so simple. I have tried just now, and exactly, as you imply, it is not possible with a flexible hose as a slightest deformation of its walls causes huge pressure fluctuations.