Im am trying to figureout how to calculate savings using a VFD -
Variable Frequincy(Speed) Drive

Direct energy savings easy

I am trying to Calculate the savings in AIR FLOW/+/Air temp-differerance

Not exausting 75'F air outside at say 10,000 CFM - And not bringing in 30'F Air in the winter at the same CFM's

I am not looking for a direct answer I am am looking for equations/examples? such as. Cost to heat 1 CF of Air per Degree F , Without going into too much detail I can use some assumptions (efficency of heating sorce etc.)
 
Physics news on Phys.org
I figured it all out :smile:


Basically assume 10,000 CFM Fan

Values
Total CFM 10,000

Tatal CF - Day 14,400,000

1 CF air = 0.075 lbs 1,080,000

To heat 1 lbs air = 0.24
BTU's per Degree ferinhight A) 259,200

Delta T (Temp Change) B) 50

BTU's Per day A*B 12,960,000

1000 BTU = 1 Cubic foot gas 12,960

1 cubic metre = 0.0283 cubic foot 366.77

Cost Per cubic metre of gas $0.50

Air cost per day for
10,000 CFM fan Using Gas $183.38


BOOH YEAH
 
That looks pretty good, yeah. The difficulty is in getting more precise - you need weather data to know what the actual delta-T is on an hourly basis. I use a piece of software called Binmaker: http://www.interenergysoftware.com/binM/pro/BMPAbout.htm
 
Luckily your calculations make more sense than your grammar. Yes though, your calcs look decent.
 
Well I am sorry MINGER that my grammar is not up to par with yours :frown: - Actually I could care less :-p

But thank you for the reply's

And if I wanted to be really specific I am pritty sure I would also need to take into account the moisture/humidity , the efficiency of the heating sorce , Envelope of the building , Solar heat ...

Thanks for that info on that BIN program all take a look at it.