In summary, the conversation discusses an existing industrial problem with a chiller system and two separate water circulation loops made of different materials. The issue is whether or not to remove the plate heat exchanger (PHE) and send the water directly from the chiller storage to the plant, which could result in contamination from the mild steel and copper pipes. The conversation also includes questions about the significance of the contamination, the availability of filters to avoid spreading contaminants, and the potential solution of replacing the mild steel pipe with stainless steel. Overall, the experts advise against removing the PHE due to the potential decrease in efficiency and introduction of contaminants.
  • #1
pradeepbarola
7
0
Hi

Its an existing industrial problem. There is a chiller system and two separate Water Circulation loops are there for water flow.

First: Piping of the Chiller ( Made of Copper), then Mild Steel Piping upto the storage vessel and the to plate heat exchanger (PHE).

Second:

Water Circulation loop ( made of SS 316 L) in the plant which passes through PHE for heat exchange.

Check the attached images

The water in the above two loops two not come in direct contact with each other.

Both the loops have water circulating through them. Now I want to remove the PHE system and send the water directly from chiller storage to plant. The issues of using it are.

1. Contamination from Mild Steel and Copper pipe will spread in the whole plant.

Now I want to know:

Q1. Will the contamination will be really significant if I bypass the PHE. FYI the plant chilled water is used in the Vessel Jacket for Heat Exchange only. So its the issue of life of Jacket and will there be a considerable impact on it.

Q2. Are the any filters available to avoid spreading of Contaminates beyond a certain point.

Q3. Will replacing the Mild Steel Pipe by SS solve the issue. And is so will copper be a remaining issue.

Looking forward for an early reply

Thanks in Advance.
 

Attachments

  • exisitng copy.jpg
    exisitng copy.jpg
    18.6 KB · Views: 700
  • proposed copy.jpg
    proposed copy.jpg
    17.6 KB · Views: 528
Engineering news on Phys.org
  • #2
pradeepbarola said:
Contamination from Mild Steel and Copper pipe will spread in the whole plant.

Now I want to know:

Q1. Will the contamination will be really significant if I bypass the PHE.

Greetings.
I'm pretty sure that I can't help you at all, but I would like to clarify something. Are you referring to metallic contamination from the pipes themselves, or contaminants that happen to be in the pipes?
 
  • #3
Does your chiller only use water? There's no glycol mixture or similar?
What kind of chiller is it: Air-cooled, water-cooled, evaporative?
Depending on your answer to that question, where does make up water to the chiller come from (if applicable)?
Has the water in the process loop been treated at all (softened/filtered/etc)?

We don't know the age of your system, so who knows what kind of contaminents are in your piping...

Also, you won't see the 7.5-8.5 C from an input temp of 12-14 at the current operating duty. The output temp from the chiller is determined by the input temp of the water. If you put water at 14C in, you'll get water at around 11-12C out, if the system is left as it is.
 
  • #4
@Danger: I can say particulate matter from the mild steel pipings,
@King: Only water is used, its a Air Cooled chiller system, the system is 4-5 years old
just to clarify 7.5-8.5, 10-11 is the chiller loop inlet and outlet temp. respectively, and 12-14, 10-11 are the inlet and outlet resp. for process loop.

Even if the pipes are having contaminates , the water can be replaced before installing new piping.
 
  • #5
My first assumption was correct—I can't be of assistance to you. Sorry about that. Best wishes for a resolution.
 
  • #6
OP, I understood where the temps were being indicated. My point was that the chiller can only cool the water a certain delta-T for whatever flow you've got. Getting rid of the heat exchanger means the chiller inlet temperature is higher (since it's direct from the process) and therefore the outlet temperature will be higher unless you increase the flow, probably, significantly.

As for your concern about contamination...there is no way to get around it if you wish to use the chiller you've got. I don't know your contamination limits, nor an I familiar with what, and how much, contaminents are released from copper tubing and steel pipe, so I can't comment on that. But if they are that worried about it, you have to keep the heat exchanger.

Removing it will:
--Make your process less efficient by driving temperatures up (increasing BTU requirement for chiller)
--Introduce contaminants (even if you buy all stainless piping, you'll still have copper in the chiller. I'm pretty sure no chiller uses SS tubing).

Is the water in the process loop (not the chiller loop) treated?
 

What is chiller water loop contamination?

Chiller water loop contamination refers to the presence of impurities or foreign substances in the closed loop system that circulates chilled water through a building's HVAC system. These impurities can include dirt, debris, bacteria, algae, and other contaminants that can negatively affect the performance and efficiency of the chiller system.

What are some common causes of chiller water loop contamination?

The most common causes of chiller water loop contamination include inadequate maintenance and cleaning of the system, lack of filtration or improper filtration, poor water quality, and the presence of stagnant water or dead legs in the system. Additionally, external factors such as construction or nearby pollution sources can also contribute to contamination.

What are the consequences of chiller water loop contamination?

Chiller water loop contamination can lead to a variety of negative consequences, including reduced chiller efficiency, decreased heat transfer, increased energy consumption, corrosion and damage to system components, and potential health risks for building occupants. It can also result in costly repairs and downtime for the chiller system.

How can chiller water loop contamination be prevented?

Preventative maintenance is key to preventing chiller water loop contamination. This includes regular cleaning and flushing of the system, proper filtration, and testing and treating the water for impurities. It is also important to address any external factors that may contribute to contamination. Regular monitoring and early detection can also help prevent contamination from becoming a larger issue.

What are some methods for treating chiller water loop contamination?

If chiller water loop contamination is detected, there are several methods for treating it. These can include chemical treatments such as biocides or scale inhibitors, physical cleaning methods like flushing or filtration, and mechanical solutions such as UV disinfection or ozone treatment. The best treatment method will depend on the type and severity of the contamination, as well as the specific needs of the chiller system.

Similar threads

Replies
17
Views
2K
  • Mechanical Engineering
Replies
7
Views
3K
  • Mechanical Engineering
Replies
5
Views
2K
  • General Engineering
Replies
4
Views
6K
  • General Engineering
Replies
13
Views
13K
  • Mechanical Engineering
Replies
1
Views
2K
Replies
16
Views
2K
  • Mechanical Engineering
Replies
3
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
9
Views
6K
Replies
4
Views
5K
Back
Top