Heat transfer between water tank and pipe system

Click For Summary

Discussion Overview

The discussion revolves around the heat transfer calculations for a cooling system utilizing an ice melting pool to provide air-conditioning for an office. Participants explore the water circulation rate needed for the system, the melting rate of ice, and the implications of various design parameters such as cooling coil length and temperature measurements.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant inquires about the water circulation flow rate needed for the system, providing initial calculations based on power and temperature differences.
  • Another participant questions the measured water temperature of 3-5°C, suggesting that ice in contact with water should yield a temperature of 0°C.
  • There is a discussion on the cooling coil length, with a participant noting that it should be a design parameter and questioning how it was determined.
  • Concerns are raised about the water circulation rate being too fast or too slow, affecting heat transfer efficiency and cooling capacity.
  • One participant suggests that the size of the ice tank may be inadequate for the cooling needs, referencing a standard refrigeration metric (ton) to illustrate the ice melting capacity required.
  • Participants express uncertainty about the U-value of the cooling coil and whether a rough estimate could be used for calculations.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the appropriate water circulation rate, the implications of the measured water temperature, or the adequacy of the ice tank size. Multiple competing views and uncertainties remain throughout the discussion.

Contextual Notes

Limitations include the lack of clarity on the U-value of the cooling coil, assumptions regarding the isolation of the ice tank, and the potential influence of hot water mixing in the ice melting pool prior to measurement.

Leo Lee
Messages
4
Reaction score
0
Hello All,
I have a question for heat exchange calculation and hope someone can help. I would like to recover the "cooling energy" from a ice melting pool for air-conditioning for a small office. I plan to install three fan coil units with 800CFM for the office with closed loop water pipe to circulate water from fan coil units to the cooling coil immersed in the ice melting water tank and then back to fan coil units. Hence, heat from the office will transfer to the ice melting water.
Ice melting tank effective size : 4m x 2.2m x 1m(H)
Ice melting water temperature : 3 ~ 5*C as measured
Cooling coil : OD : 9.52mm OD; Length : 32.4m ; Material : copper
Fan coil unit : each cooling capacity 7.92kW (assume water in at 7*C and leave at 12.5*C)
What is the water circulating flow rate for the above system ?
How long will the ice water support for the system (as the water temperature will rise up) ? Ice will be refilled for every 2 to 3 hours and cannot support air-conditioning at 7*C.
Any assumption can be made. I only need rough estimation for reference. I have a normal air-conditioning system for the office as backup. This project is for environmental education purpose. Thanks !
 
Anyone can help ?
 
Hello Leo, :welcome:

It is a bit unclear how we can help here. Are you asking simple things, like
Leo Lee said:
What is the water circulating flow rate for the above system ?
with as a naive answer$$ {dQ\over dt} = \rho \,c_p \, \Delta T\, F_v \quad \Rightarrow \quad F_v = { 7.92\; kJ/s \over 1000 \; kg/m^3 \ 4.2 \;kJ/(kg\cdot \mathstrut^\circ\! C) \ 5.5 ^\circ \!C} \ \ ? $$So some 1.2 m3/h per coil.

Similarly for the melting rate of ice:
Leo Lee said:
How long will the ice water support the system
$$

{dM\over dt} = {dQ\over dt} \Delta H_f \quad \Rightarrow \quad T = \rho \ V \ \Delta H_f {dQ\over dt} = {593\; kg/m^3 \ 8.8 \;m^3 \ 334\; kJ/kg \over 7.92\; kJ/s}$$or some 20 hours if all three are at full capacity (and the ice tank is perfectly isolated :rolleyes: (*) )

(## \; 593\; kg/m^3\ ## is the density of dry crushed ice)But there are some things in your account I can't follow: ice in contact with water should yield a temperature of ##0 \; ^\circ \!C\ ##, so how come you measure 3 - 5 ? And use 7 degrees for the coil input ?

How did you determine the length of your cooling coil ? Isn't it a design parameter to be established ? You have ##\displaystyle {dQ\over dt} = U\; A\; \Delta T## with ##A## the contact area and ##U## the over-all heat transfer coefficient (which you probably don't know yet).
 
BvU said:
Hello Leo, :welcome:

It is a bit unclear how we can help here. Are you asking simple things, like
with as a naive answer$$ {dQ\over dt} = \rho \,c_p \, \Delta T\, F_v \quad \Rightarrow \quad F_v = { 7.92\; kJ/s \over 1000 \; kg/m^3 \ 4.2 \;kJ/(kg\cdot \mathstrut^\circ\! C) \ 5.5 ^\circ \!C} \ \ ? $$So some 1.2 m3/h per coil.

Similarly for the melting rate of ice:
$$

{dM\over dt} = {dQ\over dt} \Delta H_f \quad \Rightarrow \quad T = \rho \ V \ \Delta H_f {dQ\over dt} = {593\; kg/m^3 \ 8.8 \;m^3 \ 334\; kJ/kg \over 7.92\; kJ/s}$$or some 20 hours if all three are at full capacity (and the ice tank is perfectly isolated :rolleyes: (*) )

(## \; 593\; kg/m^3\ ## is the density of dry crushed ice)But there are some things in your account I can't follow: ice in contact with water should yield a temperature of ##0 \; ^\circ \!C\ ##, so how come you measure 3 - 5 ? And use 7 degrees for the coil input ?

How did you determine the length of your cooling coil ? Isn't it a design parameter to be established ? You have ##\displaystyle {dQ\over dt} = U\; A\; \Delta T## with ##A## the contact area and ##U## the over-all heat transfer coefficient (which you probably don't know yet).

Thanks for your reply. Sorry for confusion in my question. I would like to determine the water circulation rate inside the pipe system. That is critical to determine the water temperature entering and leaving the ice melting pool, as well as entering and leaving fan coil units. If water circulation rate is too fast, there will be no sufficient time for heat transfer to the ice melting pool. If it is too slow, the fan coil unit will not have sufficient water flow to remove heat from the office. How can I determine a suitable water circulation rate ?

I measured the water temperature at the ice melting pool by infrared temperature measurement sensor and the reading is 3~5 degree. Is it not suitable for the measurement? On the other hand, the pool has hot water supply for ice melting. I am not sure any hot water mixed in the pool before my measurement.

Regarding the cooling coil length, I will use an abandoned 1600 CFM fan coil unit's coil and the measured length is 32.4m.

I don't know the U-value of the cooling coil in the ice melting pool, any ball-part figure can be used ?

Thank you very much.

Best Regards

Leo
 
Hello, anyone can help ? Thanks.
 
Leo Lee said:
Thanks for your reply. Sorry for confusion in my question. I would like to determine the water circulation rate inside the pipe system. That is critical to determine the water temperature entering and leaving the ice melting pool, as well as entering and leaving fan coil units. If water circulation rate is too fast, there will be no sufficient time for heat transfer to the ice melting pool. If it is too slow, the fan coil unit will not have sufficient water flow to remove heat from the office. How can I determine a suitable water circulation rate ?
Since you specified an inlet and outlet temperature and power, that leads directly to only one possible water circulation rate, as calculated by @BvU
I measured the water temperature at the ice melting pool by infrared temperature measurement sensor and the reading is 3~5 degree. Is it not suitable for the measurement?
It is a bit surprising, but I suppose it is possible in a dynamic situation.
Regarding the cooling coil length, I will use an abandoned 1600 CFM fan coil unit's coil and the measured length is 32.4m.

I don't know the U-value of the cooling coil in the ice melting pool, any ball-part figure can be used ?
Since this is real-world, that makes life easier. You can calculate it based on the actual testing you've done, but I don't think I would bother. With a 3-5C melting pool temperature and 7C supply to the FCU, I'd say your main problem is too small of a tank and/or not enough ice. Ice storage can be a useful solution to some HVAC problems, but as you are finding out, you need a lot of ice. In the USA, we have a unit of refrigeration called a "ton", which refers to the melting of a US ton (900 kg) of ice in 24 hours. Each of your FCUs has a capacity of 2 tons.
 
  • Like
Likes   Reactions: Vedward

Similar threads

  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 2 ·
Replies
2
Views
3K
Replies
3
Views
3K
  • · Replies 5 ·
Replies
5
Views
9K
Replies
1
Views
3K
Replies
5
Views
2K
Replies
7
Views
2K
Replies
7
Views
2K
Replies
1
Views
1K
Replies
25
Views
4K