Heat transfer between water tank and pipe system

  1. Nov 27, 2016 #1
    Hello All,
    I have a question for heat exchange calculation and hope someone can help. I would like to recover the "cooling energy" from a ice melting pool for air-conditioning for a small office. I plan to install three fan coil units with 800CFM for the office with closed loop water pipe to circulate water from fan coil units to the cooling coil immersed in the ice melting water tank and then back to fan coil units. Hence, heat from the office will transfer to the ice melting water.
    Ice melting tank effective size : 4m x 2.2m x 1m(H)
    Ice melting water temperature : 3 ~ 5*C as measured
    Cooling coil : OD : 9.52mm OD; Length : 32.4m ; Material : copper
    Fan coil unit : each cooling capacity 7.92kW (assume water in at 7*C and leave at 12.5*C)
    What is the water circulating flow rate for the above system ?
    How long will the ice water support for the system (as the water temperature will rise up) ? Ice will be refilled for every 2 to 3 hours and cannot support air-conditioning at 7*C.
    Any assumption can be made. I only need rough estimation for reference. I have a normal air-conditioning system for the office as backup. This project is for environmental education purpose. Thanks !!
     
  2. jcsd
  3. Dec 3, 2016 #2
    Thanks for the thread! This is an automated courtesy bump. Sorry you aren't generating responses at the moment. Do you have any further information, come to any new conclusions or is it possible to reword the post? The more details the better.
     
  4. Dec 13, 2016 #3
    Anyone can help ?
     
  5. Dec 14, 2016 #4

    BvU

    User Avatar
    Science Advisor
    Homework Helper
    Gold Member

    Hello Leo, :welcome:

    It is a bit unclear how we can help here. Are you asking simple things, like
    with as a naive answer$$ {dQ\over dt} = \rho \,c_p \, \Delta T\, F_v \quad \Rightarrow \quad F_v = { 7.92\; kJ/s \over 1000 \; kg/m^3 \ 4.2 \;kJ/(kg\cdot \mathstrut^\circ\! C) \ 5.5 ^\circ \!C} \ \ ? $$So some 1.2 m3/h per coil.

    Similarly for the melting rate of ice:
    $$

    {dM\over dt} = {dQ\over dt} \Delta H_f \quad \Rightarrow \quad T = \rho \ V \ \Delta H_f {dQ\over dt} = {593\; kg/m^3 \ 8.8 \;m^3 \ 334\; kJ/kg \over 7.92\; kJ/s}$$or some 20 hours if all three are at full capacity (and the ice tank is perfectly isolated :rolleyes: (*) )

    (## \; 593\; kg/m^3\ ## is the density of dry crushed ice)


    But there are some things in your account I can't follow: ice in contact with water should yield a temperature of ##0 \; ^\circ \!C\ ##, so how come you measure 3 - 5 ? And use 7 degrees for the coil input ?

    How did you determine the length of your cooling coil ? Isn't it a design parameter to be established ? You have ##\displaystyle {dQ\over dt} = U\; A\; \Delta T## with ##A## the contact area and ##U## the over-all heat transfer coefficient (which you probably don't know yet).
     
  6. Dec 14, 2016 #5
    Thanks for your reply. Sorry for confusion in my question. I would like to determine the water circulation rate inside the pipe system. That is critical to determine the water temperature entering and leaving the ice melting pool, as well as entering and leaving fan coil units. If water circulation rate is too fast, there will be no sufficient time for heat transfer to the ice melting pool. If it is too slow, the fan coil unit will not have sufficient water flow to remove heat from the office. How can I determine a suitable water circulation rate ?

    I measured the water temperature at the ice melting pool by infrared temperature measurement sensor and the reading is 3~5 degree. Is it not suitable for the measurement? On the other hand, the pool has hot water supply for ice melting. I am not sure any hot water mixed in the pool before my measurement.

    Regarding the cooling coil length, I will use an abandoned 1600 CFM fan coil unit's coil and the measured length is 32.4m.

    I don't know the U-value of the cooling coil in the ice melting pool, any ball-part figure can be used ?

    Thank you very much.

    Best Regards

    Leo
     
  7. Jan 3, 2017 #6
    Hello, anyone can help ? Thanks.
     
  8. Jan 4, 2017 #7

    russ_watters

    User Avatar

    Staff: Mentor

    Since you specified an inlet and outlet temperature and power, that leads directly to only one possible water circulation rate, as calculated by @BvU
    It is a bit surprising, but I suppose it is possible in a dynamic situation.
    Since this is real-world, that makes life easier. You can calculate it based on the actual testing you've done, but I don't think I would bother. With a 3-5C melting pool temperature and 7C supply to the FCU, I'd say your main problem is too small of a tank and/or not enough ice. Ice storage can be a useful solution to some HVAC problems, but as you are finding out, you need a lot of ice. In the USA, we have a unit of refrigeration called a "ton", which refers to the melting of a US ton (900 kg) of ice in 24 hours. Each of your FCUs has a capacity of 2 tons.
     