Choosing the Right 3-Way Valve for Dual Water Source Control

  • Thread starter Thread starter jawbreak
  • Start date Start date
  • Tags Tags
    Application Valve
Click For Summary
SUMMARY

The discussion centers on selecting the appropriate 3-way valve for controlling two water sources feeding into a single reservoir. The recommended solution is to use two 8111K45 Brass Three-Way Solenoid Valves with Side Port NC, 1/4" NPT Female, .09 Cv Factor, and Viton Seat from McMaster, which are suitable for applications requiring flow in both directions. A universal valve is necessary when pressure can be applied to either port, ensuring no leakage occurs. The conversation also highlights the cost-effectiveness of using two Normally Open (NO) valves instead of a single 3-way valve.

PREREQUISITES
  • Understanding of Direct-Acting Solenoid Valves
  • Familiarity with valve configurations (Normally Open, Normally Closed, Universal)
  • Knowledge of pressure dynamics in fluid systems
  • Basic electrical wiring for solenoid operation
NEXT STEPS
  • Research the specifications and applications of Asco Brass Solenoid Valves
  • Learn about the differences between Normally Open and Normally Closed valves
  • Explore the installation and wiring of solenoid valves in dual-source systems
  • Investigate the impact of pressure differentials on valve performance
USEFUL FOR

This discussion is beneficial for engineers, technicians, and hobbyists involved in fluid control systems, particularly those working with solenoid valves in dual-source applications.

jawbreak
Messages
4
Reaction score
0
I was wondering anyone could help me figure out the type of valve I need.

The application is I have two sources of water going into the same reservoir and I want to be able to switch between the two.

I am currently looking at Direct-Acting Solenoid Valves 3 way

Now I am noticing some say universal and wondering if this is the type I need? What does it mean by universal? I want the water to be able to flow in either direction. In and out.

Any suggestions and help is greatly appreciated thanks.
 
Engineering news on Phys.org
A manufacture and part number would help us.
 
Cant figure out a way to bookmark this site but if you go to

http://www.mcmaster.com/

And catalog page 417 its at the top
Brass Three-Way Solenoid Valves

Looking at the diagram I'm not sure if it can do what I want if or if that's what the universal type is for.This is what I want:

<---->|...|
...|...|<----->
<---->|...|

(periods/dots are just for proper alignment)

config 1:

<---->|...|
...| \_|<----->
<---->|...|

config 2:

<---->|...|
...| _|<----->
<---->|/..|

One of two sources can be selected and it can flow in both directions.

Thanks again, hope diagrams make sense
 
Last edited:
These are generally low pressure valves made by Asco for example. A lot of these valves are "unbalanced" which means that pressure has a tendency to push the valve open. Thus, they can start leaking (internally) at a pressure below the normal operating pressure.

A universal valve (per Asco) is a valve that can seal off internally at full rated pressure in all directions such that it doesn't matter if the port is pressurized not (ie: it doesn't matter if the port is an IN or an OUT port). The cost for having this feature is generally higher solenoid power for any given Cv, thought that's not always the case since many times the solenoid is oversized anyway.

Other valves, such as 'Normally Open' or 'Normally Closed' have specific IN and OUT ports, and pressure in the opposite direction will cause the valve to leak. If you have a common, low pressure port that you're flowing to, you can probably use a NO or NC valve.

Edit: I see our posts overlapped. From the last post you seem to indicate that you could have higher pressure on the common port which means you'll need a universal one.
 
config 1:

----->|...|
...|\_|---->
----->|...|...\
......|
......|
......|
<-----|...|.../
...|\_|<---
<-----|...|

config 2:
----->|...|
...| _|---->
----->|/..|...\
......|
......|
......|
<-----|...|.../
...| _|<---
<-----|/..|


Heres the final looking application

Two solenoids are connected by a tube where there are two different inputs and output reservoirs. The two solenoids will be wired to together to switch at the same time.

So it seems if I got two of the 3way universal it would work?

Also if I wanted to use a NO or NC could I? Since the second solenoid has one input and two outputs does this matter?

Thanks again, I am extremely grateful.
 
From looking at your post #5, it looks like you only have flow in one direction (ie: pressure is always highest on the same side of your valve). If that's the case an NO or NC valve is fine. If the dP is low enough, it may still work just fine. If you need to operate the valve such that it blocks flow regardless of which port is pressurized, you need the universal one. Hope that helps.

oh... and welcome to the board :smile:
 
Thanks Q_Goest, you've been a great help!

Looks like I'm going to go with two of the

8111K45
Brass Three-Way Solenoid Valve with Side Port NC, 1/4" NPT Female, .09 Cv Factor, Viton Seat

from mcmaster, the ones on top of page 417.

Thanks for the nice welcome :)
 
Asco makes some of the same solenoid valves. As a matter of fact, I wouldn't be surprised if the ones from McMaster weren't from Asco.
 
think about this
just use two valves
both n.o. valves
this way you can open one or the other or both at the same time
the two smiple valve cost less than a 3-way
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 16 ·
Replies
16
Views
3K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 11 ·
Replies
11
Views
3K
Replies
5
Views
8K
Replies
1
Views
914