Finding sending end voltage for 3-phase 11 kV line with reactive power

  • Thread starter Thread starter ads114
  • Start date Start date
  • Tags Tags
    Transmission
Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
1 reply · 2K views
ads114
Messages
11
Reaction score
0
hi there.

can anybody advise with this one please?

a short 3 phase 11kv line delivers a load of 4.1 mw,2.6 mvar lag if the series impedance of the line is (7.2 +j12.1 ) calculate the sending end voltage and load angle.

the thing which is confusing me is the 2.6mvar lag bit,i know i need to get a power factor from this to work things out, how do i change this into a power factor value ie 0-1?

any pointers appreciated.
 
Physics news on Phys.org
You have P=4 MW and Q = 2.6MVAR, so you can get S using the power triangle and then you can easily get the power factor, cosθ = P/S.