Grounding of secondary side transformer

Click For Summary
SUMMARY

The discussion focuses on the grounding of the secondary side transformer, specifically analyzing the implications of grounding at different points in the circuit as illustrated in figures 2-12b and 2-13. It is established that grounding at L2 results in both sides of the secondary windings being at the same voltage, preventing current flow. Conversely, grounding at L1 can lead to current passing through the coil, potentially starting the motor without blowing the fuse. Additionally, it is noted that placing the overload relay (OL) on the low side is not ideal, as it may allow undetected faults to persist until an overload condition occurs.

PREREQUISITES
  • Understanding of electrical circuit diagrams, particularly transformer configurations.
  • Knowledge of grounding principles in electrical engineering.
  • Familiarity with overload relay functions and their placement in circuits.
  • Basic concepts of fault conditions and their impact on circuit operation.
NEXT STEPS
  • Research the implications of grounding in transformer circuits, focusing on secondary side configurations.
  • Study the role and placement of overload relays in electrical systems to prevent undetected faults.
  • Learn about fault detection methods in electrical circuits to enhance safety and reliability.
  • Explore the effects of different grounding techniques on circuit performance and safety.
USEFUL FOR

Electrical engineers, mechanical engineers transitioning to electrical concepts, and professionals involved in circuit design and safety assessments will benefit from this discussion.

wv123456789
Messages
1
Reaction score
0
TL;DR
Grounding of secondary side of transformer
Hello,

I am a mech engineer teaching myself electrical engineering so please forgive my ignorance. Could someone explain to me how the coil stays open when grounded in the figure 2-12b.

With my limited understanding I can see that in 2-13a the if the side of the circuit on the left of the coil contacted ground (earth fault) then because of grounding at L2 both sides of the secondary windings would be at the same voltage so no current. In 2-13b grounding at L1 means that because of the Earth fault ground is now hot, current would pass through grounding at L1, bypassing the stop and into the coil? Is that correct?

many thanks,

will

1660805387097.png
 
Engineering news on Phys.org
Welcome to PF.
In (a), grounding any point between L1 and the motor, would blow the fuse.
In (b), grounding any point between L1 and the motor, could start the motor without blowing the fuse.
 
Figure 2-13A is not ideal either. Overload relay labeled OL should not be in the low side. A fault to ground between M and OL can exist for years without anyone realizing it until one day due to an overload condition on the motor causes the overload relay to trip and it has been bypassed due to an undetected fault between M and OL.
 
  • Like
Likes   Reactions: Baluncore

Similar threads

Replies
6
Views
4K
  • · Replies 13 ·
Replies
13
Views
4K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 5 ·
Replies
5
Views
5K
  • · Replies 7 ·
Replies
7
Views
2K
Replies
7
Views
12K
  • · Replies 3 ·
Replies
3
Views
4K
  • · Replies 7 ·
Replies
7
Views
5K
  • · Replies 5 ·
Replies
5
Views
5K