Grounding the secondary side of a transformer affects current flow and circuit protection. In the case of an earth fault, grounding at L2 results in equal voltage across the secondary windings, preventing current flow. Conversely, grounding at L1 can allow current to bypass protective measures, potentially starting a motor without blowing a fuse. The discussion highlights the importance of proper relay placement to avoid undetected faults that could lead to overload conditions. Understanding these grounding scenarios is crucial for safe electrical system design.
wv123456789
Messages
1
Reaction score
0
TL;DR Summary
Grounding of secondary side of transformer
Hello,

I am a mech engineer teaching myself electrical engineering so please forgive my ignorance. Could someone explain to me how the coil stays open when grounded in the figure 2-12b.

With my limited understanding I can see that in 2-13a the if the side of the circuit on the left of the coil contacted ground (earth fault) then because of grounding at L2 both sides of the secondary windings would be at the same voltage so no current. In 2-13b grounding at L1 means that because of the Earth fault ground is now hot, current would pass through grounding at L1, bypassing the stop and into the coil? Is that correct?

many thanks,

will

1660805387097.png
 
Engineering news on Phys.org
Welcome to PF.
In (a), grounding any point between L1 and the motor, would blow the fuse.
In (b), grounding any point between L1 and the motor, could start the motor without blowing the fuse.
 
Figure 2-13A is not ideal either. Overload relay labeled OL should not be in the low side. A fault to ground between M and OL can exist for years without anyone realizing it until one day due to an overload condition on the motor causes the overload relay to trip and it has been bypassed due to an undetected fault between M and OL.
 
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top