How long can I heat up a container?

  • Thread starter Thread starter mechwill
  • Start date Start date
  • Tags Tags
    Container Heat
Click For Summary

Discussion Overview

The discussion revolves around how long it takes to heat a cabin using a 1000 Watt air heater, specifically from an ambient temperature of 12 ºC to a desired room temperature of 21 ºC. Participants explore the calculations involved, including the effects of insulation and air density on heating time.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant proposes using the equation Q = m Cp delta T to calculate the mass flow rate and heating time, but expresses concern about the lack of consideration for insulation and infiltration.
  • Another participant questions the assumption of constant air density during heating and suggests that heat rising may lead to inefficient heating of the room.
  • A suggestion is made to use a ceiling fan to circulate warm air more effectively.
  • Some participants argue that the heater's size is adequate if used efficiently and recommend using a thermostat to manage the heater's duty cycle.
  • There is a discussion about the cost of electricity based on the heater's power consumption and the duration of use.
  • Participants mention the importance of estimating heat loss through various building components to maintain the desired temperature.
  • One participant provides specific values for air density and specific heat capacity, suggesting that these can be used for more accurate calculations.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the best approach to calculate heating time, with multiple competing views on the importance of insulation, air density, and heater efficiency remaining unresolved.

Contextual Notes

Participants highlight limitations in their calculations, including assumptions about air density changes with temperature and the need to account for heat loss through building materials.

mechwill
Messages
5
Reaction score
0
hi guys,

I have a little cabin in my backyard. Recently, i have dug out a 1000 Watt air heater and installed in the cabin.

I like to find out how long i need to run the heater to warm up to the room temperature of 21 ºC from the ambient of 12 ºC. Either the heater needs to be bigger or let it run longer to heat up the room

I initially start the calculation with this equation Q = m Cp delta T. Re-arrange the equation and it becomes m = Q / (Cp * delta T). Once i have find the mass flow rate, i know the volume of the room and the density of the air. I can calculate the time right?

However, one of my main concern is about the insulation and the infiltration which changes the time to heat up the room right? but that equation does not state any U value or R value. so... did i do something wrong or use the wrong equation?

Thanks
 
Engineering news on Phys.org
Welcome, Mechwill.
Not being educated, I would take this to be a trial-and-error problem. While formulae are a great idea, they don't always reflect reality. I see a couple of problems. One is that you claim to know the density of the air. Have you accounted for the fact that it will change as a function of the temperature rising? Secondly, and to me more importantly, is that since heat rises you will be filling up the top of the room with warm air first, which is of no use to you. While I recommend that you wait for someone knowledgeable to respond, my first thought is that you might increase your efficiency by installing a ceiling fan to blow the warm air back down.
 
Danger said:
Welcome, Mechwill.
Not being educated, I would take this to be a trial-and-error problem. While formulae are a great idea, they don't always reflect reality. I see a couple of problems. One is that you claim to know the density of the air. Have you accounted for the fact that it will change as a function of the temperature rising? Secondly, and to me more importantly, is that since heat rises you will be filling up the top of the room with warm air first, which is of no use to you. While I recommend that you wait for someone knowledgeable to respond, my first thought is that you might increase your efficiency by installing a ceiling fan to blow the warm air back down.


I haven't considered that option until you've mentioned it. That way you will circulate the hot and cold air in the room.

The reason why i am asking this is because that i want to know how much electricity i am paying to have that heater running. Maybe if i know the time to heat up the room, i can size down the heater and add a fan on top of it to save some money.

Thanks for the suggestion
 
There's no need to down-size the heater, especially since you already have one that you don't have to pay for. Just lower the duty cycle so it doesn't run more than necessary. That's what thermostats are for. It should have one built in, but if it doesn't you can nab one for 5 or 10 bucks at a hardware store. It won't use any more energy than a smaller unit running more frequently.
You could always supplement it with a good old-fashioned potbelly stove or build a nice little fireplace.
 
Your heater is conveniently sized to use 1 kwhr per hr.
You therefore can find out very quickly how much you pay to run your heater, simply multiply your electric $ cost/kw hr shown on your electric bill by the number of hours the heater runs.
Separately, depending on where you live and the size of your cabin, a 1000w heater is unlikely to provide much in the way of space heat. If it has a fan built in. it may be enough for a warm spot near your workbench.
 
etudiant said:
a 1000w heater is unlikely to provide much in the way of space heat. If it has a fan built in. it may be enough for a warm spot near your workbench.

That's more a function of the insulation than anything else. If it's very efficient, 1KW should be fine. (I suppose that I should qualify my comments by pointing out that I'm Canadian. Once our outdoor temperature hits anything over 5°, we're out on the lawn in our T-shirts slugging beer and ogling the neighbourhood girls in their bikinis...)
 
You know the volume of air in the box, and the density won't change all that much from 12 C to 21 C, so you know the mass of the air in the box (to the accuracy you'd need). At 10 C air is more dense than at 20 C, so use that. It's 1.247 (kg/m3)

You know the specific heat capacity of the air in the box, since it's pretty much the same at those temps (at typical room conditions, Cp=1.012)

Your delta T is obviously just 21 C - 12 C (or more correctly 294.15 K - 285.15 K) = 9 degrees C.

This gives you an estimate of the heat requirement requirement. Since you know your power in wattage, you just take the heat requirement and divide by your power available and you'll get how long it will take to heat up. Then multiply that by your electricity costs.

Then, of course, you'll need to do some estimation on how much it energy it will take to maintain that temperature.
 
Travis_King said:
You know the volume of air in the box, and the density won't change all that much from 12 C to 21 C, so you know the mass of the air in the box (to the accuracy you'd need). At 10 C air is more dense than at 20 C, so use that. It's 1.247 (kg/m3)

You know the specific heat capacity of the air in the box, since it's pretty much the same at those temps (at typical room conditions, Cp=1.012)

Your delta T is obviously just 21 C - 12 C (or more correctly 294.15 K - 285.15 K) = 9 degrees C.

This gives you an estimate of the heat requirement requirement. Since you know your power in wattage, you just take the heat requirement and divide by your power available and you'll get how long it will take to heat up. Then multiply that by your electricity costs.

Then, of course, you'll need to do some estimation on how much it energy it will take to maintain that temperature.

I think in order to maintain at the same level of temperature. Heat loss of the building needs to be performed. The calculation starts off with calculating the heat loss through the walls, roof, floor, windows, door, infiltration. The total amount of the heat that is loss from the room is known. Since I have 1 kW heater, which is essentially the heat source, the net heat is known. Finally, I can use the equation that you suggest to estimate the amount of time that is required to heat up the room.

Not sure if i am missing any step here. Thanks for the clarification and the step by step explanation
 
Danger said:
That's more a function of the insulation than anything else. If it's very efficient, 1KW should be fine. (I suppose that I should qualify my comments by pointing out that I'm Canadian. Once our outdoor temperature hits anything over 5°, we're out on the lawn in our T-shirts slugging beer and ogling the neighbourhood girls in their bikinis...)

Now i see what you do with your spare time. haha
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
Replies
9
Views
3K
Replies
14
Views
2K
Replies
5
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 16 ·
Replies
16
Views
5K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 12 ·
Replies
12
Views
3K
  • · Replies 9 ·
Replies
9
Views
5K
Replies
9
Views
4K