How to find total Kw Usage of an A/C Unit PLEASE HELP

  • Thread starter Thread starter PowerMan8989
  • Start date Start date
  • Tags Tags
    Unit
AI Thread Summary
To determine the total kW usage of a 10-ton rooftop A/C unit with model # TCD120C40AAB, the system power is 12.83 kW, while the total kW is 13.83 kW. The discussion emphasizes the importance of calculating energy usage in kWh rather than kW. It suggests that accurate projections of energy savings from switching to a "cool roof" require complex computer simulations rather than simple calculations. The impact of the roof color on building temperature is highlighted, indicating that a white roof could reduce the frequency of A/C operation, leading to energy savings. Overall, the focus is on understanding the relationship between roof type and A/C efficiency rather than just temperature output data.
PowerMan8989
Messages
2
Reaction score
0
i am trying to find the total kw usage of a 10 ton rooftop unit. Its model # is TCD120C40AAB. Its EER value is 9.2. Nominal CFM is 4000. Gross Cooling Capacity is 125,000. System Power is 12.83 kw.

I am trying to figure out how much kw i will be saving by getting a "cool roof" instead of a typical black roof. The white roof will have R-20 insulation as the black roof only had R-6.

When i look at the Product Gross Cooling Capacity Performance Data Sheet, i can search what the MBH is going to be at different ambient temperatures. This way i can see what the kw usage is at 165 degree Fahrenheit and the kw usage at 115 degree Fahrenheit and determine how much i would save by implementing a white roof. I just cannot figure out how to calculate the kw usage of my unit at different temperatures as a projection.

PLEASE HELPP!
 
Engineering news on Phys.org
Welcome to PF!

First, we need to discuss units. You asked for "total kW". The total kW of this unit is 13.83 kW. What you probably really meant was total energy usage. Energy is measured in kWh, not kW.

Now, the question you are asking can't be answered with a simple thumb rule or equation. It needs to be calculated with a computer simulation of the annual air conditioning required by the building.

Also, the temperature vs output data for the AC unit isn't critical here. Even if the AC unit is on the roof, it won't experience a condenser inlet temperature of 165F now and 115 later. But what will happen is the black roof will make the building heat up less than it does now, making the AC unit run less often, and that's where most of the savings comes from.
 
Last edited:
So its better to have a black roof or white roof, and do you mean that the white roof will make the building heat up less?
 
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...
I need some assistance with calculating hp requirements for moving a load. - The 4000lb load is resting on ball bearing rails so friction is effectively zero and will be covered by my added power contingencies. Load: 4000lbs Distance to travel: 10 meters. Time to Travel: 7.5 seconds Need to accelerate the load from a stop to a nominal speed then decelerate coming to a stop. My power delivery method will be a gearmotor driving a gear rack. - I suspect the pinion gear to be about 3-4in in...