I1/I2 = N2/N1Φmax = Bmax * AcSingle Phase Transformer Calculations

  • Thread starter Thread starter oxon88
  • Start date Start date
  • Tags Tags
    Phase Transformer
Click For Summary

Discussion Overview

The discussion revolves around calculations related to a single-phase transformer, including determining the number of secondary turns, primary and secondary currents, maximum flux, and the cross-sectional area of the core. Participants explore various equations and concepts related to transformer operation, including voltage, current, magnetic flux, and flux density.

Discussion Character

  • Homework-related
  • Technical explanation
  • Exploratory
  • Debate/contested

Main Points Raised

  • Participants calculate the number of secondary turns using the transformer turns ratio formula, arriving at 50 turns.
  • There are attempts to calculate primary and secondary currents based on the transformer's power rating, with some participants suggesting different methods and values.
  • Discussion on the meaning of the transformer's rating of 120 kVA, with some participants asserting it indicates maximum output power.
  • Participants explore the relationship between magnetic flux and transformer voltage, discussing relevant equations such as Φ = B.A.cosθ and the universal EMF equation E = 4.44 x f x N x a x B.
  • There is a debate about the significance of the 4.44 factor in transformer equations, with some participants seeking clarification on its derivation and application.
  • Some participants express confusion regarding the relationship between maximum flux and flux density, leading to further exploration of equations and concepts.
  • Participants discuss the implications of their calculations, including the physical dimensions of the transformer core based on their results.

Areas of Agreement / Disagreement

Participants generally agree on the calculations for the number of turns and the interpretation of the transformer's power rating. However, there are multiple competing views regarding the calculations for current and the application of the 4.44 factor, indicating that the discussion remains unresolved on these points.

Contextual Notes

Some participants express uncertainty about the equations used for calculating magnetic flux and its relationship to voltage and turns, highlighting potential gaps in their understanding. There is also mention of unit conversions and the need for careful consideration of dimensions in calculations.

Who May Find This Useful

This discussion may be useful for students and practitioners interested in electrical engineering, specifically those studying transformers and their operational principles.

oxon88
Messages
176
Reaction score
1

Homework Statement



A single phase transformer has the following rating: 120 kVA, 2000 V/100 V, 60 Hz with 1000 primary turns.

Determine:

a) the secondary turns
b) the rated primary and secondary currents
c) the maximum flux
d) given a maximum flux density of 0.25 T, the cross sectional area of the core.

Homework Equations



V2/V1 = N2/N1
 
Physics news on Phys.org
trying to work out the answer for part a

N2 = N1*V2 / V1


= (1000 * 100) / 2000


N2= 50 turns


Is this correct?
 
oxon88 said:
trying to work out the answer for part a

N2 = N1*V2 / V1


= (1000 * 100) / 2000


N2= 50 turns

1000 turns : 50 turns ≡ 2000V : 100V ✔[/size][/color]
 
Thanks, can you offer any advice on solving part b?

Im stuck trying to work out the current in either N1 or N2

once i have one of these values I guess i can use V2/V1 = N2/N1 = I2/I1
 
ok here is an attempt at b

I1=120000/2000 = 60A

I2 = 60/0.05 = 1200A
how does this look?
 
Last edited:
What does it mean when it says a single phase transformer has the following rating: 120 kVA?
 
120kVA is the maximum power the transformer can output. its a measure of volt-amps.

so... 120kVA / 100v = 1200A on the secondary?
 
oxon88 said:
120kVA is the maximum power the transformer can output. its a measure of volt-amps.
Close enough. :smile:
so... 120kVA / 100v = 1200A on the secondary?
Yes. And the same idea applies to the primary, too.
 
I'm a bit stuck with part c. Any advice on this one?
 
  • #10
oxon88 said:
I'm a bit stuck with part c. Any advice on this one?
What equations do you know that involve magnetic flux?
 
  • #11
Would this be appropriate to use?

Magnetic Flux = B.A.cosθ
 
  • #12
oxon88 said:
Would this be appropriate to use?

Magnetic Flux = B.A.cosθ
Φ=B.A.cosθ is a good equation to memorize, and we'll need that for part (d) which relates flux to flux density and area.

For part (c) we need an equation relating flux, voltage and number of turns for a transformer.
 
  • #13
ok I see. Would this be more appropriate?

Φ = V × T / N

Φ = Flux (weber)
V = Voltage
T = Time
N = No. of turns
 
Last edited:
  • #14
In an operating transformer the flux is constantly changing, and in a sinusoidal manner. It's the changing flux linking the secondary that induces the secondary voltage. :smile:
E1 = N1 . ΔΦ/Δt
You're getting close. It's based on that, but others have done all the necessary fiddle-factoring and you've almost certainly been presented with the final equation in lectures or textbook reading.

Hint: there's a 4.44 factor in it.
 
Last edited:
  • #15
right then I think I may have got it...

Vp = 4.44 * f * Np * Φmax2000 = 4.44 * 60 * 1000 * Φmax

2000 = 266400 * Φmax2000 / 266400 = ΦmaxΦmax = 7.51 mWb
 
  • #16
Φmax = 7.51 mWb ✔ [/size] [/color]
:smile:
 
  • #17
Great thanks for you help and advice. Its making more sense now. Last part to go...

Φ = B * A * cosθ

would θ = 0 ?



7.51x10-3 = 0.25 * A * cos(0)

7.51x10-3 / 0.25 = A

A = 0.03003mm2
 
  • #19
oxon88 said:
Great thanks for you help and advice. Its making more sense now. Last part to go...

Φ = B * A * cosθ

would θ = 0 ?
EDIT: Oops. Misread the Greek. :-p
Yes, windings are perpendicular to the core.
7.51x10-3 = 0.25 * A * cos(0)

7.51x10-3 / 0.25 = A

A = 0.03003mm2
Check those units.
 
  • #20
would it be m2? (standard SI base unit)
 
  • #21
oxon88 said:
would it be m2? (standard SI base unit)
It should be.

0.03 m² sounds better. 120kVA would be a heavy industrial transformer. If the core were to have a circular cross-section it would be 20cm. diameter, without the windings, so I guess that sounds in the ballpark.

So, you have the transformer equations all connected up now?
i0om5.gif
 
  • #22
so that would mean if the core was circular, the diameter would be roughly 19.5cm? That is huge.

yes its all a lot clearer now. thank you for your help and time.
 
  • #23
Hi could somebody expand on 4.44 factor if you don't mind.
 
  • #24
hmmm

I'm guessing that the equation used to find the max flux is the universal EMF equation :-

E = 4.44 x f x N x a x B

where
E = rms voltage of winding
f = frequency
N= number of turns
a = cross=-sectional area of core
B = peak flux density

Just wondering how we can actually use this to find 'B' as we don't know what 'a' is either? It looks like it was just left-out. Surely this would give a wrong answer then??

I've reached this question too, and my notes have no mention of this universal equation so I'm struggling a bit to work it out..

Could anyone please explain why it's been left out and yet the answer is still right..
 
  • #25
braceman said:
I'm guessing that the equation used to find the max flux is the universal EMF equation :-

E = 4.44 x f x N x a x B

where
E = rms voltage of winding
f = frequency
N= number of turns
a = cross=-sectional area of core
B = peak flux density

Just wondering how we can actually use this to find 'B' as we don't know what 'a' is either?
If you are asked to find maximum flux, then you are to find flux, Φ[/size], not flux density, B. https://www.physicsforums.com/showpost.php?p=3871394
 
  • #26
bugger

thanks for the reply Nascent,

yeah, I misread it to read just flux and not flux density like it was.

Going back and trying to find the equation just for flux now...
 
  • #27
I'm getting this for d)

Bm = 0.25T
Φm = Bm*A
Or , A = Φm/Bm
= 0.0075/0.25 m2
= (0.0075/0.25)*10000 cm2
= 300 cm2

Thoughts
 
  • #28
NascentOxygen said:
:smile:

Hi NascentOxygen,

I understand this is an old thread but just wondering if you clarify one thing. Would I be correct in saying the 4.44 figure comes from 2π/√2=4.44, and that the √2 is there for the fact it is single phase? I was doing some reading and found this online, why has the RMS value been used on this rather than the max since the question asks for maximum flux?

Thanks,
Jason

https://www.electronics-tutorials.ws/transformer/trans6.gif
 
  • #29
Jason-Li said:
Would I be correct in saying the 4.44 figure comes from 2π/√2=4.44, and that the √2 is there for the fact it is single phase?

I would say you're exactly right.
for sine waves
ω = 2πf
and √2 is the ratio of peak to rms

upload_2018-12-23_20-3-23.png


Hats off to you for digging into understand the equations.
It's a lot easier than trying to remember them, isn't it ?
4.44 is slide rule accuracy.
With today's calculators you can postpone rounding off until the last step.
Sometimes textbook authors arrange their example problems so that pi's and √'s cancel out , and angles have convenient cosines.
That's when a little bit of such 'procrastination' just might pay off .

old jim
.
 

Attachments

  • upload_2018-12-23_20-3-23.png
    upload_2018-12-23_20-3-23.png
    3 KB · Views: 747
  • Like
Likes   Reactions: Jason-Li and gneill
  • #30
jim hardy said:
I would say you're exactly right.
for sine waves
ω = 2πf
and √2 is the ratio of peak to rms

View attachment 236282

Hats off to you for digging into understand the equations.
It's a lot easier than trying to remember them, isn't it ?
4.44 is slide rule accuracy.
With today's calculators you can postpone rounding off until the last step.
Sometimes textbook authors arrange their example problems so that pi's and √'s cancel out , and angles have convenient cosines.
That's when a little bit of such 'procrastination' just might pay off .

old jim
.
Yeah precisely the reason I don't just copy people who have done the question previous, I want to understand it so I can apply it more easily in future! Thanks for confirming that with the good explanation and picture also.

An old Jim is a wise Jim !
 
  • Like
Likes   Reactions: jim hardy

Similar threads

Replies
1
Views
2K
  • · Replies 11 ·
Replies
11
Views
28K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
1
Views
4K
  • · Replies 6 ·
Replies
6
Views
4K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K