Pumped hydoelectric storage equation problem

  • Thread starter Thread starter Erik S
  • Start date Start date
  • Tags Tags
    Storage
Click For Summary

Discussion Overview

The discussion revolves around the efficiency calculations for a reversible hydraulic generator/pump station used in pumped hydroelectric storage. Participants explore the relationship between the power ratings of the pump and turbine, the efficiency of the system, and the implications of different flow rates and operational conditions.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant seeks to determine the percentage of bought energy that can be delivered back to the grid, expressing confusion over achieving high efficiency values.
  • Another participant suggests typical efficiencies for such systems range from 70-80% and questions why the pump's capacity is only 10% of the turbine's capacity.
  • Some participants propose that the low pump capacity may be due to the longer duration of pumping at low-cost power compared to shorter periods of high-demand turbine operation.
  • There are references to the use of Manning's equation for calculating flow rates, although some participants express uncertainty about the specifics of the pump's design.
  • One participant suggests that the efficiency calculation could be approached by comparing the net power output of the turbine and pump.
  • Several participants discuss the implications of using separate pumps and turbines for different flow rates and the potential efficiency of Archimedes screws in this context.
  • Concerns are raised about the efficiency of Archimedes screws at high vertical heights, with references to specific hydro plants as examples.

Areas of Agreement / Disagreement

Participants express differing views on the efficiency of the system and the relationship between pump and turbine capacities. There is no consensus on the optimal design or efficiency metrics, and the discussion remains unresolved regarding the best approach to calculate efficiency and the suitability of different turbine types.

Contextual Notes

Participants mention various assumptions related to flow rates, operational conditions, and the design of the pump and turbine system. There are unresolved questions about the specific characteristics of the system being discussed, including the potential use of Archimedes screws and the implications of height on efficiency.

Erik S
Messages
5
Reaction score
0
I am trying to figure out the efficiency of a reversible hydraulic generator/pump station that will generate electricity when the price is high, and pump water up into the reservouar with power from the grid when electricity is cheap.

I have calculated the following information for the pump and turbine:

Ppump= 10 MW
Qpump= 7.5 m^3/s

Pturbine= 96 MW
Qturbine= 72.5 m^3/s

How can I figure out what percentage of the bought energy can be delivered back to the net?
I am having trouble figuring out how to set up an equation I can use to solve this problem, No matter what I go I get really high effeciency like 99% which must be wrong.

Thanks in advance.
 
Engineering news on Phys.org
Typical efficiencies are 70-80% overall. Why is pumped capacity only 10% of turbine capacity?
 
The pump is rated at 10MW, the produced flow is calculated using Mannings equation with given Mannings constant.

This is because I don't have any information on the volumetric displacement/ rpm of the pump
 
Erik S said:
The pump is rated at 10MW, the produced flow is calculated using Mannings equation with given Mannings constant.

This is because I don't have any information on the volumetric displacement/ rpm of the pump
So this system has open-conduit flow? Can you post a sketch of your system?
 
You can easily just ratio all of those numbers against each other to find the efficiency.

...however, just by looking at them I can see that your 99% efficiency is about right. So your problem is in how you came up with those performance points.

By the way, this is engineering, not math. Moving thread...
 
insightful said:
Why is pumped capacity only 10% of turbine capacity?
Maybe because water is pumped for longer periods while some power is available at low cost, than the shorter periods of peak turbine flow that generate power when the demand and price are higher.

Erik S, You need to find the efficiency of the motor, pump, turbine and alternator.
The penstock will need to be designed to operate with the higher flow expected during turbine operation.
 
Baluncore said:
Maybe because water is pumped for longer periods while some power is available at low cost, than the shorter periods of peak turbine flow that generate power when the demand and price are higher.
Pumping and generating power are usually close:

https://en.wikipedia.org/wiki/Pumpe...ty#/media/File:Pumpspeicherkraftwerk_engl.png

For a 10:1 difference, you'd need a separate pump and turbine for high efficiency.
 
insightful said:
Pumping and generating power are usually close:
But not in this case.

insightful said:
For a 10:1 difference, you'd need a separate pump and turbine for high efficiency.
Erik S said:
I have calculated the following information for the pump and turbine:

Ppump= 10 MW
Qpump= 7.5 m^3/s

Pturbine= 96 MW
Qturbine= 72.5 m^3/s
As you can see, there is a separate pump and turbine for the different flow rates.
 
insightful said:
Pumping and generating power are usually close:
Where does that fact come from ? Do you have a reference ?
 
  • #10
Erik S said:
I am trying to figure out the efficiency of a reversible hydraulic generator/pump station that will generate electricity when the price is high, and pump water up into the reservouar with power from the grid when electricity is cheap.

I have calculated the following information for the pump and turbine:

Ppump= 10 MW
Qpump= 7.5 m^3/s

Pturbine= 96 MW
Qturbine= 72.5 m^3/s

How can I figure out what percentage of the bought energy can be delivered back to the net?
I am having trouble figuring out how to set up an equation I can use to solve this problem, No matter what I go I get really high effeciency like 99% which must be wrong.

Thanks in advance.

Easy, Net Work rate =Net Powerhydroplant= Pturbine-Ppump
If you are interested with Hydro Plant Efficiency = Net Powerhydroplant/Pturbine

Efficiency means what you get from the total effort you exert or gain over capital.
I hope this helps.
 
  • #12
Baluncore said:
Where does that fact come from ? Do you have a reference ?

Re: Pump versus generate powers.

Insightful didn't say always, he said usually.

It is simply that the number of hours in the day for high-peak power and low-peak power are similar. That alone means you want pumping power and generating power to be of similar magnitude.

It also has to do with the cost of power transmission. Transmission capacity is unnecessarily expensive for high power flows (plus or minus direction) for short periods of time. Both plus and minus flows are typically spread over several hours.
 
  • #14
insightful said:
I'm wondering if this system might be using Archimedian screws:

Sure, but remember that the energy stored is proportional to the quantity of water pumped, and the vertical height difference. You might need 200 meters of height to make it worth the trouble. I question the efficiency of a Archemedes Screw at that height.

Consider an example: The Blenheim-Gilboa Pumped Hydro Plant, has 19 million cubic meters of water storage, at 348 meters vertical head, to make 1134 MW electric.
 
  • #15
anorlunda said:
Sure, but remember that the energy stored is proportional to the quantity of water pumped, and the vertical height difference.
Cannot an Archimedes screw be very efficient at low head and high volume for both pumping and generating?

(Edit: Admittedly, this system would require a huge surface area reservoir.)
 
Last edited:
  • #16
anorlunda said:
Sure, but remember that the energy stored is proportional to the quantity of water pumped, and the vertical height difference. You might need 200 meters of height to make it worth the trouble. I question the efficiency of a Archemedes Screw at that height.

Consider an example: The Blenheim-Gilboa Pumped Hydro Plant, has 19 million cubic meters of water storage, at 348 meters vertical head, to make 1134 MW electric.

Archimedes Screw is ideally applicable to Low Head, High flow reservoirs. For high heads and high flow reservoir, ideal is the impulse and mix flow type of turbine. 200 m is very high elevation indeed.
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 10 ·
Replies
10
Views
3K
Replies
14
Views
3K
Replies
18
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K
Replies
2
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K
Replies
14
Views
2K
Replies
1
Views
2K