When to Use Temperature or Pressure for R134-a Tables?

  • Thread starter Thread starter bagofmilk
  • Start date Start date
Click For Summary
SUMMARY

The discussion focuses on the use of R134-a tables for determining the state of refrigerant R-134a based on temperature and pressure. The participants clarify that both temperature and pressure are necessary to accurately set the state of the fluid, particularly in a refrigeration cycle where the compressor handles vapor. They emphasize using saturated vapor properties for calculations, especially at -24ºC and 100kPa, and confirm that mass flow rate can be calculated using the formula mdot = Flow Rate / Specific Volume at the vapor stage.

PREREQUISITES
  • Understanding of thermodynamic properties of refrigerants, specifically R-134a.
  • Familiarity with the use of saturation tables for refrigerants.
  • Knowledge of isentropic processes in refrigeration cycles.
  • Ability to perform unit analysis for mass flow rate calculations.
NEXT STEPS
  • Study the use of R-134a saturation tables for various temperatures and pressures.
  • Learn about isentropic processes and their significance in refrigeration systems.
  • Explore the concept of specific volume and its role in calculating mass flow rates.
  • Investigate the differences between vapor and liquid properties in refrigeration applications.
USEFUL FOR

Engineers, HVAC technicians, and students in thermodynamics who are involved in refrigeration system design and analysis will benefit from this discussion.

bagofmilk
Messages
3
Reaction score
0
R134-a Tables Use T or P??

Using the Saturated R134-a tables, I'm a little confused as to when I should look up values according to temperature or pressure.

In this particular problem:
Refrigerant-134a enters a compressor at 100kPa and -24ºC with a flow rate of 1.35 cfm and leaves at 800kPa and 60ºC. Determine the mass flow rate of R-134a and the power input to the compressor.

The equations I plan to use are: mdot = Q/v. And I think that to find power I can use
P = mdot * (u2 - u1)

The problem is that I don't know if I should look at the values according to T1=-24C or P1 = 100kPa (same for T2). Can anyone shed any light on this?
 
Engineering news on Phys.org


You need two properies to set the state of the fluid, so you need to use both temperature and pressure. In order to set the state, you have to find the intersection of two property lines that intersect somewhere in the T_S or P_V diagram; in your case for state (1) you can find the intersection of the T=-24 C line (or near to it) and 100 kPa line.

Once you've set the state, you would follow an isentropic line up to the higher pressure and this would give you State (2) (the intersection of an isentropic line through state (1) and the 800 kPa line). You have both temperature and pressure for state (2), which means you'll also be able to find the compressor's efficiency if state (2) is not isentropic w.r.t. state (1).
 


Mech_Engineer said:
You need two properies to set the state of the fluid, so you need to use both temperature and pressure. In order to set the state, you have to find the intersection of two property lines that intersect somewhere in the T_S or P_V diagram; in your case for state (1) you can find the intersection of the T=-24 C line (or near to it) and 100 kPa line.

Once you've set the state, you would follow an isentropic line up to the higher pressure and this would give you State (2) (the intersection of an isentropic line through state (1) and the 800 kPa line). You have both temperature and pressure for state (2), which means you'll also be able to find the compressor's efficiency if state (2) is not isentropic w.r.t. state (1).

I see what you mean when you say to find the intersection of T and P. It makes sense. But we are only given the tables. Would I have to interpolate the two values (vf @ T=-24C and vf @ P=100kPa)?

Also, when you say follow the isentropic line - would I use the liquid or vapor entropy value?
 


Ah, sorry I missed that you are using saturation tables. In the case of saturated fluid, the saturation state is technically the second property setting the state of your fluid. In a refrigeration system, the compressor compresses vapor rather than liquid (liquid would be a pump, and not a refrigeration cycle), so I would say you you need to look at saturated vapor properties.

In the case of R-134a, saturated vapor/liquid at -24 C is at 1.1160 bar (111.6 kPa) so you can really look up properties using either value, I'm guessing there was some rounding error in the problem statement because R-134a at -24 C and 100 kPa is not techically saturated fluid any more. I wouldn't bother interpolating, just use temperature.
 


Mech_Engineer said:
Ah, sorry I missed that you are using saturation tables. In the case of saturated fluid, the saturation state is technically the second property setting the state of your fluid. In a refrigeration system, the compressor compresses vapor rather than liquid (liquid would be a pump, and not a refrigeration cycle), so I would say you you need to look at saturated vapor properties.

In the case of R-134a, saturated vapor/liquid at -24 C is at 1.1160 bar (111.6 kPa) so you can really look up properties using either value, I'm guessing there was some rounding error in the problem statement because R-134a at -24 C and 100 kPa is not techically saturated fluid any more. I wouldn't bother interpolating, just use temperature.

Awesome! Thanks. Also, just to double check - I can find mdot by using:
mdot = Flow Rate / (Specific Volume-vapor stage 1), correct?
 


Correct, and you can see it in a units analysis:

Flow rate (SI): m^3/s
Specific Volume: m^3/kg

(Flow Rate) / (Specific Volume) = kg/s
 

Similar threads

Replies
1
Views
721
Replies
3
Views
2K
  • · Replies 8 ·
Replies
8
Views
5K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 20 ·
Replies
20
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
3
Views
4K
Replies
1
Views
1K