| Jan29-13, 07:35 AM | #18 |
|
|
conflict in AC electricity |
| Jan29-13, 07:36 AM | #19 |
|
|
Otherwise I could say the voltage of the live is 10000 V and the voltage of the neutral is 99760 V, giving a p.d. of 240 V. That is possible if it was a floating power supply. |
| Jan29-13, 07:45 AM | #20 |
|
|
If you did this with the neutral, it would - all else being equal - be okay. But now suppose there was a break in the neutral wire between the plug and the power supply. The neutral wire would jump up to 240 V and you've now got a live chassis. Not good! There are other reasons as well, to do with the way circuit breakers are set up to detect faults. |
| Jan29-13, 07:55 AM | #21 |
|
|
|
| Jan29-13, 07:57 AM | #22 |
|
|
|
| Jan29-13, 07:58 AM | #23 |
|
|
I see you expert folks are carefully ignoring the questions to your theories in my post#13.
In particular what is the potential of the neutral terminal of a portable generator with respect to earth? Finally would someone post the section of the Wiring Regulations that apparantly requires UK neutrals to be earthed? I have previously posted at PF the Wiring Regulations section that prohibits this. |
| Jan29-13, 08:25 AM | #24 |
|
|
There's much more 'chat' than actual figures on this when I do a Google search (Dozens of forums for electrical installers etc.- anecdotes, mainly). I did find out that temporary generator installations can get away with 25V N-E but the max one should expect in a permanent installation is only 3 or 4V. This is just due to a realistic value for the neutral cable (all the way from the transformer) and a typical maximum load.
@Studiot Your measured value of 30V would give me some concern. Where do you measure this - on the input to your consumer distribution unit or on a socket. Also, with what sort of load? If you get that with no domestic load then you should ring your supplier and they should send someone out to see you, I reckon. (Keep your wellie boots on when you're in the shower!) Why isn't this thread in the EE section, I wonder? |
| Jan29-13, 08:30 AM | #25 |
|
|
http://www.ussu.co.uk/ClubsSocieties...430%202011.pdf It's entirely irrelevant as everyone else is discussing mains supplies. In the US I think the connection is in the house, which is why the discussion was getting confused. But this is all irrelevant to the original post. The 30 V between your neutral and earth could be due to a whole host of reasons - the most obvious being impedance of the wires. Seems strangely high to me, but I'm not a sparky. |
| Jan29-13, 08:37 AM | #26 |
|
|
@Studiot
You're in for a major re-wire of your house, I expect. No time for more postings on PF. You'll be out earning overtime to pay for it all. ![]() Where ignorance is bliss, 'tis folly to be wise. |
| Jan29-13, 09:28 AM | #27 |
|
|
I have the Board's certificate of satisfactory test for my own wiring, thank you for your concern.
Any competent electrician would know that the 30 volts would not be maintained if I tried to draw significant current to earth. I am far more concerned with the hazardous practices suggested by others here, or by the suggestion that portable generators are somehow different or are not covered by the wiring regulations. Of course they are. Much of the world's supplies are from such generators. Portable includes multi megawatt devices towed behind an HGV tractor. Reading th OP's posts I suspect he is from 'the subcontinent' where the wiring system is based on older British practice - that of providing both earthed and non earthed AC supplies. I repeat my comment to him that the earth should not carry current in normal operation - it is a safety conductor. No one has offered a reason for earthing the neutral. So here is why the americans do and we do not. Here is the reason for american practice The consumer neutral is the centre point of a split phase transformer. By itself, it is floating. It is earthed to provide a stable reference for both phases whose differential return currents would otherwise unbalance it. In the US the consumer's neutral does not carry any other consumer's return current. Excellent sound practice. But wholly inapplicable to British practice since the British consumers neutral does not stem from a consumers transformer, but from a local substation where the combined return current from the entire phase arrives. This phase services many consumers. |
| Jan29-13, 09:40 AM | #28 |
|
|
Single transformer for many customers: the cheapest option in dense housing.
|
| Jan29-13, 10:53 AM | #29 |
|
|
|
| Jan29-13, 11:00 AM | #30 |
|
|
|
| Jan29-13, 02:12 PM | #31 |
|
Mentor
|
If the neutral and ground are tied together at the substation, the neutral will have approximately zero potential art the ground, everywhere. As it pertains to the OP's question, I don't see why it matters where they are connected, only that they are. |
| Jan29-13, 02:52 PM | #32 |
|
|
First who said the neutral and ground are tied together at the substation? I didn't. In the US, a pair of transmission wires, single phase no earth (the company feed) are brought to the company side of the consumer supply transformer (actually owned by the company I believe but I'm not sure about that). That is the primary. The consumer is supplied from a centre tapped secondary on this transformer. The centre tap is earthed locally. The two halves of the 'split phase' are used to supply the consumer 120 outlets and the whole secondary used to supply any 240 heavy demand installations. As far as possible the split phases are balanced but in any event their current draw does not affect the current through the primary circuit terminals, only its magnitude. The other point of this is that the consumer is electrically isolated from other consumers and cannot unbalance their supplies, since the consumer is in the secondary and the feed supply in the primary. In British practice, on the other hand, imagine the effect of multiple grounding one of the two main conductors of a phase. All the phase current would be routed directly to local ground, leaving serious unbalance in the (neutral) return conductor. The British consumer is not electrically isolated from his neighbour and what he does affects the neighbours supply. |
| Jan29-13, 02:57 PM | #33 |
|
Mentor
|
That's all fine, but what does that have to do with the OP's question? To be more precise: if you stand in a bathtub full of water and grab a neutral wire in London, should you expect a shock?
|
| Jan29-13, 03:06 PM | #34 |
|
|
|
| New Reply |
Similar discussions for: conflict in AC electricity
|
||||
| Thread | Forum | Replies | ||
| What is a context conflict? | Calculus & Beyond Homework | 12 | ||
| QM conflict with relativity | Quantum Physics | 2 | ||
| Resolving conflict | Current Events | 0 | ||
| GR and QM conflict | Special & General Relativity | 0 | ||
| solution conflict! | Calculus & Beyond Homework | 3 | ||